Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

PowerChute 4.1 starts vCenter server before last host is going down

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: PowerChute 4.1 starts vCenter server before last host is going down
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-26 03:05 AM

0 Likes
6
545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-26 03:05 AM

PowerChute 4.1 starts vCenter server before last host is going down

This question was originally posted by Pavel on APC forums on 8/4/2016


Hello all,

We decided to use last version of PCNS 4.1 in our company for shutdown VMs, hosts and UPS after switching on battery. So before using it in production we run some tests. In our test environment we can`t shutdown the UPS.

Test environment:
2 ESXi hosts in HA cluster (ESXi 5.5 Update 3b build: 3248547)
1 UPS - Symmetra RM6000 with NMC - AP9619
vCenter Server 5.5 Update 3b (build: 3252642) running on VM (OS: Windows Server 2008 R2)
PowerChute Network Shutdown 4.1 deployed on cluster as VMware Virtual Appliance. PowerChute is configured to shutdown after getting UPS event "Manual Bypass" with delay 30 seconds.

Before switching UPS to Manual Bypass two VMs (vCenter server and PowerChute) are located on second host and there are tied to second host by DRS rules.

After switching UPS to Manual Bypass all going well, all VMs gracefully shutdown except VC and PowerChute, first host switches to maintenance mode and shutdown, then vCenter server shutdowns and after some time first host gets command to shutdown, but before it powered off PowerChute starts vCenter server. After some seconds second host goes down.

We performed test twice and both times vCenter server starts before second hosts goes down.

This is a normal behavior of the procedure of shutdown? We need to start vCenter server only after start up the hosts. How to achieve this?

Time period in log files of shutdown process is 08/04/2016 11:07:54 - 08/04/2016 11:37:48

Thanks in advance!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • appliance
  • esxi
  • firmware
  • pcns
  • PowerChute
  • shutdown
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-26 03:06 AM

0 Likes
0
545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-26 03:06 AM

This reply was originally posted by Bill on APC forums on 8/15/2016


Hi,

Sorry for the delay in my response. I have been on holiday. 

I think the issue is due to the locking mechanism in VirtualizationFileStore.properties and a mismatch in the Hostname/FQDN between vCenter Server and what's configured locally on the ESXi hosts.

05-08-16 08:22:00,337 DEBUG Thread-32 com.apcc.m11.components.WebServer.util.virtualization.VMWareUtils - getHostUsingIPOrDNSName - Host IP: esxru0321cl001.mycompany.com
05-08-16 08:22:00,367 DEBUG Thread-32 com.apcc.m11.components.WebServer.util.virtualization.VMWareUtils - Found [1] hostSystemEntites
05-08-16 08:22:00,370 DEBUG Thread-32 com.apcc.m11.components.WebServer.util.virtualization.VMWareUtils - Found hostSystem esxru0321cl001

05-08-16 08:22:02,189 DEBUG Thread-32 com.apcc.m11.components.WebServer.util.virtualization.VMWareUtils - getHostUsingIPOrDNSName - Host IP: esxru0321cl002.mycompany.com
05-08-16 08:22:02,224 DEBUG Thread-32 com.apcc.m11.components.WebServer.util.virtualization.VMWareUtils - Found [1] hostSystemEntites
05-08-16 08:22:02,226 DEBUG Thread-32 com.apcc.m11.components.WebServer.util.virtualization.VMWareUtils - Found hostSystem esxru0321cl002

While vCenter Server is online the host lock will be added to VirtualizationFileStore.properties as:

esxru0321cl001.mycompany.com
esxru0321cl002.mycompany.com


After VCSA goes offline and PCNS connects directly to the host, the ESXi host name is returned as esxru0321cl001, and esxru0321cl002 instead of esxru0321cl001.mycompany.com, esxru0321cl002.mycompany.com - so the locks get removed and PCNS incorrectly attempts to start the VCSA VM.
-
The Solution to this is to update the Hostname on each of the ESXi hosts to make sure that it uses the FQDN. Using vSphere Client go to Configuration - DNS and Routing - check that Name and Domain are correct. Also in MOB browser check that FindByIP and FindByDNSName return the FQDN. See Kbase FA241346 for assistance with MOB. 

See Answer In Context

Reply
Share
Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-26 03:05 AM

0 Likes
0
545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-26 03:05 AM

This reply was originally posted by Bill on APC forums on 8/4/2016


Hi,

I think increasing the value below in the pcnsconfig.ini file would prevent the issue from occurring. It seems to be taking awhile for the ESXi host to shut down.

[HostConfigSettings]
delay_after_exit_maintenance_mode = 30

Try increasing the number to 60 or 90 for example.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-26 03:05 AM

0 Likes
0
545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-26 03:05 AM

This reply was originally posted by Pavel on APC forums on 8/4/2016


Thanks Bill for the quick answer!

I will test shutdown process with new value of option delay_after_exit_maintenance_mode tomorrow and post the results. 

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-26 03:05 AM

0 Likes
0
545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-26 03:05 AM

This reply was originally posted by Pavel on APC forums on 8/5/2016


Hi,

I performed three shutdown tests with options below:
1) delay_after_exit_maintenance_mode = 60
2) delay_after_exit_maintenance_mode = 90
3) delay_after_exit_maintenance_mode = 30 and delay_after_vcsa_powered_on_and_connected = 60

and I have the same issue with starting of vCenter server before last host is powered off.

I attached log files for three tests:
1) 1_error.log, 1_EventLog.txt, 1_pcnsconfig.ini (Time period of shutdown process: 08/05/2016 08:18:12 - 08/05/2016 08:24:18)
2) 2_error.log, 2_EventLog.txt, 2_pcnsconfig.ini (Time period of shutdown process: 08/05/2016 11:14:47 - 08/05/2016 11:20:25)
3) 3_error.log, 3_EventLog.txt, 3_pcnsconfig.ini (Time period of shutdown process: 08/05/2016 14:46:56 - 08/05/2016 14:52:30)

Do you have any suggestions for solve this issue?

Thanks!

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-26 03:06 AM

0 Likes
0
545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-26 03:06 AM

This reply was originally posted by Pavel on APC forums on 8/11/2016


Up!

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-26 03:06 AM

0 Likes
0
546
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-26 03:06 AM

This reply was originally posted by Bill on APC forums on 8/15/2016


Hi,

Sorry for the delay in my response. I have been on holiday. 

I think the issue is due to the locking mechanism in VirtualizationFileStore.properties and a mismatch in the Hostname/FQDN between vCenter Server and what's configured locally on the ESXi hosts.

05-08-16 08:22:00,337 DEBUG Thread-32 com.apcc.m11.components.WebServer.util.virtualization.VMWareUtils - getHostUsingIPOrDNSName - Host IP: esxru0321cl001.mycompany.com
05-08-16 08:22:00,367 DEBUG Thread-32 com.apcc.m11.components.WebServer.util.virtualization.VMWareUtils - Found [1] hostSystemEntites
05-08-16 08:22:00,370 DEBUG Thread-32 com.apcc.m11.components.WebServer.util.virtualization.VMWareUtils - Found hostSystem esxru0321cl001

05-08-16 08:22:02,189 DEBUG Thread-32 com.apcc.m11.components.WebServer.util.virtualization.VMWareUtils - getHostUsingIPOrDNSName - Host IP: esxru0321cl002.mycompany.com
05-08-16 08:22:02,224 DEBUG Thread-32 com.apcc.m11.components.WebServer.util.virtualization.VMWareUtils - Found [1] hostSystemEntites
05-08-16 08:22:02,226 DEBUG Thread-32 com.apcc.m11.components.WebServer.util.virtualization.VMWareUtils - Found hostSystem esxru0321cl002

While vCenter Server is online the host lock will be added to VirtualizationFileStore.properties as:

esxru0321cl001.mycompany.com
esxru0321cl002.mycompany.com


After VCSA goes offline and PCNS connects directly to the host, the ESXi host name is returned as esxru0321cl001, and esxru0321cl002 instead of esxru0321cl001.mycompany.com, esxru0321cl002.mycompany.com - so the locks get removed and PCNS incorrectly attempts to start the VCSA VM.
-
The Solution to this is to update the Hostname on each of the ESXi hosts to make sure that it uses the FQDN. Using vSphere Client go to Configuration - DNS and Routing - check that Name and Domain are correct. Also in MOB browser check that FindByIP and FindByDNSName return the FQDN. See Kbase FA241346 for assistance with MOB. 

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-26 03:06 AM

0 Likes
0
545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-26 03:06 AM

This reply was originally posted by Pavel on APC forums on 8/17/2016


Hi,

After filling Domain name in all hosts of HA cluster the issue is no longer appear. I was checked this twice with shutdown the UPS on production environment. Before that Domain name was missing on all hosts.

Thank you Bill for your help!

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc