I inherited a server rack (5 chassis) with a Smart 3000 UPS:
| Model: | Smart-UPS 3000 RM |
| Serial Number: | OS1006160019 |
| Firmware Revision: | 666.6.D |
| Manufacture Date: | 11/19/09 |
The servers are running:
PowerChute Network Shutdown Version: 4.3.0
I've tested and the UPS power down is not working. There are several configuration settings in the NMC of the UPS, but the language is proprietary and the terms are not defined (ergo, I can't figure it out) and I can't find any documentation describing this scenario.
Question: How do I configure the UPS to power down after the servers are shut down?
thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 12:56 AM . Last Modified: 2024-03-19 02:41 AM
Hi,
Did the UPS/NMC record it received the shutdown command from PCNS? Also, how many PCNS clients are registered with the NMC? With older version of the NMC it would wait for all PCNS client to signal they were powering off prior to shutting the UPS down.
The process should be
Q%2BBDvm0147NiGVTffs4sgQ%3D%3D.png
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 12:56 AM . Last Modified: 2024-03-19 02:41 AM
Hi,
Did the UPS/NMC record it received the shutdown command from PCNS? Also, how many PCNS clients are registered with the NMC? With older version of the NMC it would wait for all PCNS client to signal they were powering off prior to shutting the UPS down.
The process should be
Q%2BBDvm0147NiGVTffs4sgQ%3D%3D.png
Link copied. Please paste this link to share this article on your social media post.