Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Power off UPS after graceful server shutdown
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2612:56 AM. Last Modified: 2024-03-1902:41 AM
Power off UPS after graceful server shutdown
I inherited a server rack (5 chassis) with a Smart 3000 UPS:
Model:
Smart-UPS 3000 RM
Serial Number:
OS1006160019
Firmware Revision:
666.6.D
Manufacture Date:
11/19/09
The servers are running:
PowerChute Network Shutdown Version: 4.3.0
Build Number: 7951
Operating System: Microsoft Windows Server 2019 Standard (10.0.17763 N/A Build 17763)
Java Version: OpenJDK 64-Bit Server VM (11.0.1+13)
One server is configured to do an emergency backup prior to shutting down and then do a UPS Shutdown (Shutdown Settings --> UPS Shutdown --> Turn Off the UPS / no command to run --> Duration left at 30 seconds.
I've tested and the UPS power down is not working. There are several configuration settings in the NMC of the UPS, but the language is proprietary and the terms are not defined (ergo, I can't figure it out) and I can't find any documentation describing this scenario.
Question: How do I configure the UPS to power down after the servers are shut down?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2612:56 AM. Last Modified: 2024-03-1902:41 AM
Hi,
Did the UPS/NMC record it received the shutdown command from PCNS? Also, how many PCNS clients are registered with the NMC? With older version of the NMC it would wait for all PCNS client to signal they were powering off prior to shutting the UPS down.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2612:56 AM. Last Modified: 2024-03-1902:41 AM
Hi,
Did the UPS/NMC record it received the shutdown command from PCNS? Also, how many PCNS clients are registered with the NMC? With older version of the NMC it would wait for all PCNS client to signal they were powering off prior to shutting the UPS down.