Ask our Experts
Didn't find what you are looking for? Ask our experts!
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-26 12:56 AM . Last Modified: 2024-03-19 02:41 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 12:56 AM . Last Modified: 2024-03-19 02:41 AM
I inherited a server rack (5 chassis) with a Smart 3000 UPS:
| Model: | Smart-UPS 3000 RM |
| Serial Number: | OS1006160019 |
| Firmware Revision: | 666.6.D |
| Manufacture Date: | 11/19/09 |
The servers are running:
PowerChute Network Shutdown Version: 4.3.0
I've tested and the UPS power down is not working. There are several configuration settings in the NMC of the UPS, but the language is proprietary and the terms are not defined (ergo, I can't figure it out) and I can't find any documentation describing this scenario.
Question: How do I configure the UPS to power down after the servers are shut down?
thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 12:56 AM . Last Modified: 2024-03-19 02:41 AM
Hi,
Did the UPS/NMC record it received the shutdown command from PCNS? Also, how many PCNS clients are registered with the NMC? With older version of the NMC it would wait for all PCNS client to signal they were powering off prior to shutting the UPS down.
The process should be
Q%2BBDvm0147NiGVTffs4sgQ%3D%3D.png
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 12:56 AM . Last Modified: 2024-03-19 02:41 AM
Hi,
Did the UPS/NMC record it received the shutdown command from PCNS? Also, how many PCNS clients are registered with the NMC? With older version of the NMC it would wait for all PCNS client to signal they were powering off prior to shutting the UPS down.
The process should be
Q%2BBDvm0147NiGVTffs4sgQ%3D%3D.png
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.