Power Factor Correction Fault - Dual power supplies downstream

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Power Factor Correction Fault - Dual power supplies downstream
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Argh_apc
Argh_apc
Cadet

Posted: ‎2021-06-28 11:22 AM . Last Modified: ‎2024-03-15 05:42 AM

0 Likes
2
1811
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:22 AM . Last Modified: ‎2024-03-15 05:42 AM

Power Factor Correction Fault - Dual power supplies downstream

Can APC comment on the issue of dual power supplies of a network switch, both downstream of the UPS?

I read an inquiry, "Do any of the attached loads have dual power inputs? If so, are they both connected to the UPS?  "

In this thread:

https://community.se.com/t5/APC-UPS-Data-Center-Enterprise/bd-p/datacenter-forum 

 

In my case this is a SURTD3000XLT with brand new batteries, and three network switches attached drawing 3.9 Amps. As you can see, however, something went wrong:

06/18/2020 10:23:02 Device UPS: In bypass in response to an internal hardware fault.
06/18/2020 10:23:02 Device UPS: A power factor correction fault exists.
06/18/2020 09:48:57 Device UPS: Runtime Calibration passed.

Despite this, the data log (at bottom) shows vbat and %cap increasing gradually until 11:29 AM, and now dropping again gradually. 

The primary switch has twin 1100-watt power supplies, with a Y-power cable, so both supplies are connected to the UPS.  This switch isn't drawing 1100 watts, but after reading that question, I wondered if both being on the UPS could be relevant.

%Cap is third column from right

vbat is second column from right

 06/18/2020   12:39:10   206.88   209.42   208.63   3.88   36.43   27.04   59.98   83.92   207.28   +76.55 
 06/18/2020   12:29:10   206.89   208.33   207.45   3.91   36.53   27.10   60.01   84.48   207.59   +76.55 
 06/18/2020   12:19:10   206.84   208.77   207.75   3.91   36.55   27.13   59.98   84.97   207.69   +76.55 
 06/18/2020   12:09:10   207.44   209.52   208.75   3.91   36.52   27.20   59.99   85.55   207.84   +77.00 
 06/18/2020   11:59:10   207.77   209.25   208.67   3.88   36.48   27.15   60.02   86.09   208.34   +77.00 
 06/18/2020   11:49:10   207.55   208.98   208.86   3.88   36.53   27.18   59.98   86.79   208.38   +77.00 
 06/18/2020   11:39:10   207.81   209.19   208.30   3.88   36.48   27.04   59.98   87.46   208.84   +77.00 
 06/18/2020   11:29:10   207.89   209.50   208.55   3.88   36.52   27.04   60.00   88.17   209.09   +77.00 
 06/18/2020   11:19:10   207.91   209.47   208.89   3.91   36.66   27.27   59.98   85.11   209.31   +77.68 
 06/18/2020   11:09:10   208.05   209.58   208.66   3.91   36.63   27.24   60.02   78.44   209.84   +77.68 
 06/18/2020   10:59:10   208.02   210.00   209.33   3.88   36.46   27.13   60.01   71.78   209.97   +77.00 
 06/18/2020   10:49:10   208.66   209.70   209.30   3.88   36.46   27.16   59.98   65.11   210.47   +77.68 
 06/18/2020   10:39:10   208.73   209.94   209.22   3.88   36.37   27.10   59.98   58.44   211.19   +78.58 
 06/18/2020   10:29:10   208.33   210.09   209.41   3.91   36.80   27.37   59.98   51.78   212.69   +80.60 
 06/18/2020   10:19:10   208.13   209.58   207.95   3.91   36.60   27.28   60.02   45.11   222.88   +81.28 
 06/18/2020   10:09:10   207.66   209.30   208.02   3.91   36.69   27.26   59.98   38.44   219.22   +81.28 
 06/18/2020   09:59:10   207.84   209.86   207.92   3.91   36.77   27.27   59.95   31.78   215.56   +79.25 
 06/18/2020   09:49:10   208.36   211.16   207.84   3.94   37.02   27.38   60.02   25.11   202.59   +78.58 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:22 AM . Last Modified: ‎2024-03-15 05:41 AM

0 Likes
0
1807
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:22 AM . Last Modified: ‎2024-03-15 05:41 AM

Hi Jay - 

Sometimes you may see issues if you have dual power supplies where one power supply is being fed by a UPS and the other power supply is fed by a different source (either another UPS or utility power). For best performance both power supplies should be fed by the same UPS, which it sounds like you are already doing. With some power supplies and different inputs you can see unnecessary stress on the UPS when they switch from supply "A" to supply "B". This is highly dependent on the power conditions being experienced at the install site.

In your situation if both power supplies are being fed by the same UPS, this does not apply. For your unit I would recommend contacting your local tech support team to troubleshoot.

 

Thanks

Liam

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Argh_apc
Argh_apc
Cadet

Posted: ‎2021-06-28 11:22 AM . Last Modified: ‎2024-03-15 05:42 AM

0 Likes
0
1808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:22 AM . Last Modified: ‎2024-03-15 05:42 AM

APC People, can you please refer me somewhere for more info on the issue with redundant power supplies on a single 3000VA unit?  Thank you.  

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:22 AM . Last Modified: ‎2024-03-15 05:41 AM

0 Likes
0
1808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:22 AM . Last Modified: ‎2024-03-15 05:41 AM

Hi Jay - 

Sometimes you may see issues if you have dual power supplies where one power supply is being fed by a UPS and the other power supply is fed by a different source (either another UPS or utility power). For best performance both power supplies should be fed by the same UPS, which it sounds like you are already doing. With some power supplies and different inputs you can see unnecessary stress on the UPS when they switch from supply "A" to supply "B". This is highly dependent on the power conditions being experienced at the install site.

In your situation if both power supplies are being fed by the same UPS, this does not apply. For your unit I would recommend contacting your local tech support team to troubleshoot.

 

Thanks

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login