We were handed down a BladeCenter for our lab. Anyone know what type of plug I need for an IBM BladeCenter 8677HC1 with 4 power supplies? The electrician needs know so he can install the circuit.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 10:20 PM . Last Modified: 2024-03-19 03:39 AM
We were handed down a BladeCenter for our lab. Anyone know what type of plug I need for an IBM BladeCenter 8677HC1 with 4 power supplies? The electrician needs know so he can install the circuit.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 10:20 PM . Last Modified: 2024-03-19 03:40 AM
Thanks for the thorough response!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 10:20 PM . Last Modified: 2024-03-19 03:39 AM
You betcha. I didn't answer all of your question though. The equipment uses a C19 plug, but the electrician won't put in a C19 mating circuit. He'll install a NEMA circuit.
I don't know how heavily you are populating these blade chassis, but you can't go wrong if you tell the electrician to put in a 50 amp 3-phase circuit 208V/3/60 Hubbell receptacle.
Buy an AP7898 (APC Rack PDU,Metered,ZeroU,12.5kW,208V,(30)C13,(6)C19;10' Cord)
Plug the AP7898 into the wall, and plug the blade chassis into the rack power strip using APC AP9877 (Pwr Cord, 16A, 100-230V, C19 to C20)
The matching connector to this plug is a CS8364C (i.e., if you're running an overhead whip to it)
Matching receptacle is a CS8369 (i.e., if you're terminating into a wall receptacle or outlet box when coming from under the raised floor into the rack).
Page 46 has the Plug/Connector/Receptacle matrix.
http://www.hubbellcatalog.com/wiring/catalogpages/section-b.pdf
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 10:20 PM . Last Modified: 2024-03-19 03:39 AM
We were handed down a BladeCenter for our lab. Anyone know what type of plug I need for an IBM BladeCenter 8677HC1 with 4 power supplies? The electrician needs know so he can install the circuit.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.