PCNS and VirtualCenter on one VM - not working? ESXi Hosts not shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS and VirtualCenter on one VM - not working? ESXi Hosts not shutdown
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

0 Likes
5
1931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

PCNS and VirtualCenter on one VM - not working? ESXi Hosts not shutdown

Dear forum,

we have the following scenario:

3 ESXi Hosts
2 USVs (Smart UPS X 3000)
UPS Configuration: Advanced
Virtual Center on VM (running on one of the 3 hosts) - Windows 2008 Server R2
PCNS 4.1 installed on the same server that runs VirtualCenter
Host managed by Virtual Center

Now we came across the following problem - On Battery Event:

as PCNS is running on the Virtual Center (which is a VM), the VirtualCenter is shutdown as the last Virtual Machine.

We thought that PCNS would maybe send the shutdown command to the ESXi hosts before shutting down the Virtual Center

but apparently it does not? And therefore, the ESXi Hosts will never shutdown? Is this correct?

Would the only solution to this problem be to have PCNS installed on a physical machine? Or is there another solution available?

Any help is appreciated! Thanks.


Log file:
11.10.2015 10:39:21 Maintenance Mode Task cancelled on Host ESX1 as VCSA VM is shutting down.
11.10.2015 10:39:20 Shutting down vCenter Server VM vCenter.
11.10.2015 10:38:18 Shutting down VMs on Host ESX21
11.10.2015 10:38:18 Starting Maintenance Mode Task on Host ESX1.
11.10.2015 10:38:18 Shutting down VMs on Host ESX3.
11.10.2015 10:38:17 Starting Maintenance Mode Task on Host ESX3
11.10.2015 10:38:13 Altbau: Shutdown sequence started on Hosts ESX3, ESX2, ESX1 in response to UPS critical event: On Battery.
11.10.2015 10:38:13 Altbau: UPS critical event: On Battery.
11.10.2015 10:38:03 Altbau: UPS's have switched to battery power.
11.10.2015 10:38:03 Altbau: UPS XXX.XXX.XXX.001 is running on battery power.
11.10.2015 10:37:59Altbau: UPS XXX.XXX.XXX.002  is running on battery power.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • esxi
  • PowerChute
  • shutdown
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

0 Likes
0
1931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

Hi,

The configuration you are using is not supported for the reason you mentioned. PCNS will shutdown vCenter and the VM it is running on which causes PCNS to be shutdown. Supported configurations can be found in Application Note 180 and the User's Guide. Your options are to install PCNS on a stand-alone Windows Server, or install the PCNS Appliance VM. Both of those options are listed in Application Note 180. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

0 Likes
0
1932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

Hi,

The configuration you are using is not supported for the reason you mentioned. PCNS will shutdown vCenter and the VM it is running on which causes PCNS to be shutdown. Supported configurations can be found in Application Note 180 and the User's Guide. Your options are to install PCNS on a stand-alone Windows Server, or install the PCNS Appliance VM. Both of those options are listed in Application Note 180. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

0 Likes
0
1931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

Dear Bill, 

thanks for your fast reply. 

Is it only possible to install PCNS on a stand-alone Windows Server or would it be possible for our scenario to have PCNS installed on a stand-alone Linux server?

Best wishes, 

Steff

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

0 Likes
0
1931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

Hi,

The options are stand-alone Windows, PCNS VM Appliance, PCNS installed on VMware VMA. We do not offer a stand-alone Linux option. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

0 Likes
0
1931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

Thanks, that made it very clear now. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

0 Likes
0
1931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

Hi,

On 11/25/2015 5:19 AM, ste said:

If I install Powerchute on vMA - in the Powerchute Setup - can I choose  "Host managed by VirtualCenter Server" ?

Yes. You should select Host Managed by vCenter Server. 

On 11/25/2015 5:19 AM, ste said:

In case of Shutdown it then will shutdown all VMs (except vMA & Virtual Center) and in the end shuts down the 3 ESXi(s)?

Application note 180 explains this shutdown process on page 4. Basically the process is VMs / vApps are powered down, vCenter is powered down, then the hosts are powered down. The host PCNS is running on is powered down last. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore