Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

PCNS - Servers shutdown but did not restart when power was restored

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS - Servers shutdown but did not restart when power was restored
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 04:04 AM . Last Modified: ‎2024-03-05 10:28 PM

0 Likes
5
1288
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:04 AM . Last Modified: ‎2024-03-05 10:28 PM

PCNS - Servers shutdown but did not restart when power was restored

On the APC itself the setting to restart when power is restored is checked. I know this applies to the APC unit but I assumed it would cascade down to the clients. On our most recent power issue the servers did gracefully shutdown, but did not restart when the power was restored. Is there some configuration that needs to be set to make this step occur?

Thanks for any help

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:04 AM . Last Modified: ‎2024-03-05 10:28 PM

0 Likes
0
1288
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:04 AM . Last Modified: ‎2024-03-05 10:28 PM

PowerChute is just like any other software application that runs on the OS. When the computer is off the software cannot run and it does not have any setting that would edit / configure the BIOs. On the UPS side depending on the model you have you can configure either UPS or outlet group delays for power to be restored. That could be the cause but if power is being restored to the UPS or outlet group then the issue would be the BIOs.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:04 AM . Last Modified: ‎2024-03-05 10:28 PM

0 Likes
0
1288
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:04 AM . Last Modified: ‎2024-03-05 10:28 PM

There are typically three options for the BIOs power settings.

Stay Off : keeps the power off until the power button is pressed.
Last State: Resume whatever state the PC was in before the failure. If  it was off it will stay off, if it was on it will power back up.
Always On: Regardless if the PC was off or not, resume
power back up after a power failure.


Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:04 AM . Last Modified: ‎2024-03-05 10:28 PM

0 Likes
0
1288
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:04 AM . Last Modified: ‎2024-03-05 10:28 PM

On the APC itself the setting to restart when power is restored is checked. I know this applies to the APC unit but I assumed it would cascade down to the clients. On our most recent power issue the servers did gracefully shutdown, but did not restart when the power was restored. Is there some configuration that needs to be set to make this step occur?

Thanks for any help

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:04 AM . Last Modified: ‎2024-03-05 10:28 PM

0 Likes
0
1288
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:04 AM . Last Modified: ‎2024-03-05 10:28 PM

You need to configure the BIOs to restart the system when power is restored. Kbase FA159550 discusses the issue http://www.apc.com/support/index?page=content&country=US〈=en&id=FA159550

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:04 AM . Last Modified: ‎2024-03-05 10:28 PM

0 Likes
0
1288
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:04 AM . Last Modified: ‎2024-03-05 10:28 PM

prior to installing powerchute when power was lost to the servers and they did not shutdown gracefully, they DID reboot automatically when power was restored. This would seem to indicate that the bios is set to reboot when power is restored and thus I felt the FAQ linked above was not the issue. Is there any other configuration within the PowerChute software either at the client or the APC itself that needs to be configured for the reboot to occur?

Thanks


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:04 AM . Last Modified: ‎2024-03-05 10:28 PM

0 Likes
0
1289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:04 AM . Last Modified: ‎2024-03-05 10:28 PM

PowerChute is just like any other software application that runs on the OS. When the computer is off the software cannot run and it does not have any setting that would edit / configure the BIOs. On the UPS side depending on the model you have you can configure either UPS or outlet group delays for power to be restored. That could be the cause but if power is being restored to the UPS or outlet group then the issue would be the BIOs.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore