PCNS 4.3 not registering on NMC

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS 4.3 not registering on NMC
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:47 AM . Last Modified: ‎2024-03-08 04:05 AM

0 Likes
6
2972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:47 AM . Last Modified: ‎2024-03-08 04:05 AM

PCNS 4.3 not registering on NMC

Hello,

I am trying to install PCNS 4.3 and register with the UPS. The UPS and computer are both using static IP's and I can ping the UPS as well as login with the Web interface but I can't regist ther client. It says "Cannot connect to http://(UPS Static IP)".

We used this exact same process on our other UPS'es of the same model but something about the new Firmware or Software on this more recently manufactured UPS isn't allowing it to connect the same way.

We bought 10 UPS'es over the course of about 6 months. The first had a manufacture date of 12/18 and the most recent one, manufactured after 10/19 are all having this problem.

Any help would be appreciated.

Thank you!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • pcns_3
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:47 AM . Last Modified: ‎2024-03-08 04:05 AM

0 Likes
0
2972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:47 AM . Last Modified: ‎2024-03-08 04:05 AM

Hi,

 If the AP9630, AP9631, AP9635, AP9537SUM is running firmware 6.8.X verify that HTTP and or HTTPS has been enable. To enable HTTP and or HTTPS open the NMC web interface and go to Configuration - Network - Web - Access. Also, verify that HTTP and or HTTPS protocol has been enable for PowerChute. To verify HTTP and or HTTPS protocol has been enable for PowerChute open the NMC web interface and go to Configuration - Shutdown. You will find the PowerChute Communication Protocol at the bottom of the page. 
 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:05 AM

0 Likes
0
2972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:05 AM

Hi,

Open the NMC web page and go to Configuration - Shutdown. Just above where you selected http you will see user name this will be the user name and authentication phrase. The user name must match the user name assigned to PCNS and the authentication phrase must also match.

i207YMryyM7G0AsGlrF99g%3D%3D.pngi207YMryyM7G0AsGlrF99g%3D%3D.png

The default authentication phrase is admin user phrase. If you change the authentication phrase on the NMC you must also change it in PCNS. Open the PCNS web interface and go to Communication Settings - Administrator Authentication Phrase. 

BZKW3HbZ0Nt1re4%2BPlIicQ%3D%3D.pngBZKW3HbZ0Nt1re4%2BPlIicQ%3D%3D.png The authentication phrase must be at least 15, but no more than 32 characters. You must use ASCII characters A-Z, a-z, 0-9.

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:04 AM

0 Likes
0
2972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:04 AM

Hi,

The authentication phrase should be entered in the box just below the user name as shown in the screenshot .

NSMrEz3qj1NesoDV9DkxeA%3D%3D.pngNSMrEz3qj1NesoDV9DkxeA%3D%3D.png

With the release of firmware 6.8 there is no default user name or authentication phrase save on the NMC for communications with PCNS. You must enter the user name and authentication phrase PCNS will use. PCNS 4.x ships with the authentication phrase admin user phrase pre-configured. If you would like to use that phrase with firmware 6.8 you need to enter it. Prior to firmware 6.8 the PCNS authentication phrase was pre-configured on the NMC. 

When you open the NMC web interface and go to Configuration - Shutdown you should see the box to enter the authentication phrase. If you do not see the box check to be sure you are logging in as an administrator or device user. If you are logged in as an admin or device user and the option is not available, I suggest resetting the NMC and starting over. 

To reset the NMC go to Control - Network - Reset/Reboot. Select Reset All and click except TCP/IP. Once applied you will need to reboot the NMC from the same page. Once the NMC reboots you will need to reconfigure all settings you have made as the reset switched the NMC to factory defaults. 

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:47 AM . Last Modified: ‎2024-03-08 04:05 AM

0 Likes
0
2973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:47 AM . Last Modified: ‎2024-03-08 04:05 AM

Hi,

 If the AP9630, AP9631, AP9635, AP9537SUM is running firmware 6.8.X verify that HTTP and or HTTPS has been enable. To enable HTTP and or HTTPS open the NMC web interface and go to Configuration - Network - Web - Access. Also, verify that HTTP and or HTTPS protocol has been enable for PowerChute. To verify HTTP and or HTTPS protocol has been enable for PowerChute open the NMC web interface and go to Configuration - Shutdown. You will find the PowerChute Communication Protocol at the bottom of the page. 
 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:05 AM

0 Likes
0
2972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:05 AM

I had HTTP enabled under Configuration - Network - Web – Access but when I went to Configuration – Shutdown to enable HTTP for PCNS I get the error below.

I am assuming this mean I have to create a new Authentication Phrase before I can enable HTTP/HTTPS for PCNS.

Where can I create a new authentication phrase?

 

4qJBDLABYkWoe21aMUD0Nw%3D%3D.png4qJBDLABYkWoe21aMUD0Nw%3D%3D.png

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:05 AM

0 Likes
0
2973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:05 AM

Hi,

Open the NMC web page and go to Configuration - Shutdown. Just above where you selected http you will see user name this will be the user name and authentication phrase. The user name must match the user name assigned to PCNS and the authentication phrase must also match.

i207YMryyM7G0AsGlrF99g%3D%3D.pngi207YMryyM7G0AsGlrF99g%3D%3D.png

The default authentication phrase is admin user phrase. If you change the authentication phrase on the NMC you must also change it in PCNS. Open the PCNS web interface and go to Communication Settings - Administrator Authentication Phrase. 

BZKW3HbZ0Nt1re4%2BPlIicQ%3D%3D.pngBZKW3HbZ0Nt1re4%2BPlIicQ%3D%3D.png The authentication phrase must be at least 15, but no more than 32 characters. You must use ASCII characters A-Z, a-z, 0-9.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:04 AM

0 Likes
0
2972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:04 AM

The User Name in Configuration - Shutdown is the same that I am trying to login with but neither the HTTP or HTTPS box is checked there and it apparently won't let me check it without changing the Authentication Phrase. I found the place in PCNS to change it, as shown in your screenshot, but where is it in NMC?

I would rather not change it, but it seems NMC is forcing this in the new version.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:04 AM

0 Likes
0
2973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:04 AM

Hi,

The authentication phrase should be entered in the box just below the user name as shown in the screenshot .

NSMrEz3qj1NesoDV9DkxeA%3D%3D.pngNSMrEz3qj1NesoDV9DkxeA%3D%3D.png

With the release of firmware 6.8 there is no default user name or authentication phrase save on the NMC for communications with PCNS. You must enter the user name and authentication phrase PCNS will use. PCNS 4.x ships with the authentication phrase admin user phrase pre-configured. If you would like to use that phrase with firmware 6.8 you need to enter it. Prior to firmware 6.8 the PCNS authentication phrase was pre-configured on the NMC. 

When you open the NMC web interface and go to Configuration - Shutdown you should see the box to enter the authentication phrase. If you do not see the box check to be sure you are logging in as an administrator or device user. If you are logged in as an admin or device user and the option is not available, I suggest resetting the NMC and starting over. 

To reset the NMC go to Control - Network - Reset/Reboot. Select Reset All and click except TCP/IP. Once applied you will need to reboot the NMC from the same page. Once the NMC reboots you will need to reconfigure all settings you have made as the reset switched the NMC to factory defaults. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:04 AM

0 Likes
0
2972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:04 AM

I was able to get this working after setting the new passphrase on the Configuration - Shutdown. My problem before was not following the passphrase requirements. properly.

Thank you!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.