Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

PCNS 4.2 - Command File usage question

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS 4.2 - Command File usage question
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:53 AM . Last Modified: ‎2024-03-11 12:21 AM

0 Likes
3
824
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:53 AM . Last Modified: ‎2024-03-11 12:21 AM

PCNS 4.2 - Command File usage question

I am setting up PCNS 4.2 to shutdown my VMware vSphere 6.0 environment.  I have a single UPS / AP9630 NMC / with a Dell VRTX chassis with 2 hosts running 5 VM's.  I have setup for the shutting down of the VM's and then the Host using the VMware User Guide and feel I have that correctly configured, but after those were shutdown I wanted to use PCNS 4.2 lastly, to run a command via SSH to send a shutdown command via command-line to the VRTX chassis itself.  My thinking was I could use the command file to send the shutdown command via PUTTY after the VM's and host have been shutdown.

Could someone link me documentation on this?  Has anyone had success in implementing this?

Any input/suggestions are appreciated!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:54 AM . Last Modified: ‎2024-03-11 12:21 AM

0 Likes
0
821
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:54 AM . Last Modified: ‎2024-03-11 12:21 AM

Hi,

Is PCNS installed on a VM or standalone Windows system? If not on a VM and if you are configured for vCenter Server then PCNS will run a command file after the hosts have powered down. If PCNS is installed on a VM then it will run the command file prior to the hosts powering down. In that scenario you would need the command file to include a delay to allow the hosts to complete the power down prior to the chassis.

As an example this Windows shutdown command has a delay of 60 seconds shutdown /s /f /m \\server ip /c "PowerChute has initiated a system shutdown" /t 60

As fare as writing the command file, I suggest you check Dell documentation or check the Dell Community. https://www.dell.com/community/

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:54 AM . Last Modified: ‎2024-03-11 12:20 AM

0 Likes
0
821
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:54 AM . Last Modified: ‎2024-03-11 12:20 AM

Hi,

Normally you would have the system that is running PCNS connected to the same UPS. Since you do not you should select the outlet group that the host/s are plugged into. If you have each host plugged into a different outlet group then you can pick either one. The reason that PCNS asks is later on you are given the option to turn off outlet group, turn off UPS, or do not turn off UPS. If you select turn off outlet group the group you selected as the one powering PCNS will be command down and the others will not. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:54 AM . Last Modified: ‎2024-03-11 12:21 AM

0 Likes
0
822
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:54 AM . Last Modified: ‎2024-03-11 12:21 AM

Hi,

Is PCNS installed on a VM or standalone Windows system? If not on a VM and if you are configured for vCenter Server then PCNS will run a command file after the hosts have powered down. If PCNS is installed on a VM then it will run the command file prior to the hosts powering down. In that scenario you would need the command file to include a delay to allow the hosts to complete the power down prior to the chassis.

As an example this Windows shutdown command has a delay of 60 seconds shutdown /s /f /m \\server ip /c "PowerChute has initiated a system shutdown" /t 60

As fare as writing the command file, I suggest you check Dell documentation or check the Dell Community. https://www.dell.com/community/

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:54 AM . Last Modified: ‎2024-03-11 12:21 AM

0 Likes
0
821
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:54 AM . Last Modified: ‎2024-03-11 12:21 AM

Thanks for the response Bill!  I have another question regarding the setting on the UPS configuration page for "Select the Outlet Group powering the server with PowerChute Network Shutdown installed".  I currently have the PCNS 4.2 installed on a Windows 10 Professional workstation and it is not plugged into the same UPS I have my servers on.

Is this OK?  Do I need to have the computer running PCNS 4.2 plugged into the same UPS?  What should I put for this setting?

Thanks,

Jeff

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:54 AM . Last Modified: ‎2024-03-11 12:20 AM

0 Likes
0
822
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:54 AM . Last Modified: ‎2024-03-11 12:20 AM

Hi,

Normally you would have the system that is running PCNS connected to the same UPS. Since you do not you should select the outlet group that the host/s are plugged into. If you have each host plugged into a different outlet group then you can pick either one. The reason that PCNS asks is later on you are given the option to turn off outlet group, turn off UPS, or do not turn off UPS. If you select turn off outlet group the group you selected as the one powering PCNS will be command down and the others will not. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of