Hello everyone, had a quick question about overloading a Back-UPS Pro 1500.
The unit has a capacity of 865 watts / 1500VA. At max usage, it'll run 4min.
Is it safe to double it's capacity (2x 3560 V2 switches at 870 watts each)?
What would the run time be, 2min? 1min?
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:20 AM . Last Modified: 2024-03-11 02:41 AM
i don't think this will work. you'll overload the UPS and it will give you a loud constant tone and I am pretty sure it won't output power anyway in this state.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:20 AM . Last Modified: 2024-03-11 02:41 AM
i don't think this will work. you'll overload the UPS and it will give you a loud constant tone and I am pretty sure it won't output power anyway in this state.