Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-29 05:28 AM . Last Modified: 2024-03-13 12:55 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:28 AM . Last Modified: 2024-03-13 12:55 AM
UPS SMX2200HV & PowerChute Business Edition 9.1.1 Build 604
Initial Settings - Shutdown Settings - Power Fail Config - set to "begin shutdown procedure after the UPS as been on battery for" 300secs.
Outlet Sequence - "Time for other apps to shut down" 30secs plus "Time for os to shut down" 180secs, "Total time for outlet Group 1 to shutdown" 210secs.
My question: if the inlet mains power to UPS goes off, does Outlet Group 1 shut down 210secs later, or 510secs later?
Thanks
Chris
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:28 AM . Last Modified: 2024-03-13 12:55 AM
Hi,
The UPS will run on battery for 300 seconds and then begin the shutdown process if AC is not restored. So, 300 second delay on battery, 30 second delay for application shutdown, then 180 second delay for OS shutdown. Total before outlet group powers off = 510 seconds.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:28 AM . Last Modified: 2024-03-13 12:55 AM
Hi,
The UPS will run on battery for 300 seconds and then begin the shutdown process if AC is not restored. So, 300 second delay on battery, 30 second delay for application shutdown, then 180 second delay for OS shutdown. Total before outlet group powers off = 510 seconds.