Posted: 2023-04-01 12:39 PM . Last Modified: 2023-04-01 12:40 PM
Accidentally flashed an AP9631 with 7.0.8 RPDU firmware (apc_hw05_aos708_rpdu2g708_bootmon109), now NMC thinks it's connected to a PDU. Attempted to reflash with correct NMC firmware (apc_hw05_aos708_sumx708_bootmon109) but NMC firmware utility says firmware doesn't match target device platform.
Is the card toast? Or is there a way to force updating even with the mismatch?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-01 01:06 PM
Resolved. In case anyone else makes the same mistake, workaround was to flash to an older version of bootmon (apc_hw05_aos621_sumx621_bootmon108.exe in our case) to restore NMC functionality, then upgrade to 7.x. Apparently the older upgrade utilities don't perform the platform check.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-01 01:06 PM
Resolved. In case anyone else makes the same mistake, workaround was to flash to an older version of bootmon (apc_hw05_aos621_sumx621_bootmon108.exe in our case) to restore NMC functionality, then upgrade to 7.x. Apparently the older upgrade utilities don't perform the platform check.