One UPS and 3 server without Network Card.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • One UPS and 3 server without Network Card.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 12:13 AM . Last Modified: ‎2024-02-29 11:28 PM

0 Likes
10
2348
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:13 AM . Last Modified: ‎2024-02-29 11:28 PM

One UPS and 3 server without Network Card.

Hello, I have a SMT3000RMI UPS without the network card.
I have one server connected to the UPS with a RJ-45/Serail cable.

Can I manage the shutdown of the other 3 servers attached to the UPS without using the network card?

Thank you.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • network-management-card
  • PowerChute
  • powerchute-business-edition
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-08 12:14 AM . Last Modified: ‎2024-02-29 11:27 PM

0 Likes
0
2349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:14 AM . Last Modified: ‎2024-02-29 11:27 PM

Yes the server has a serial port.

The problem is that Windows don't recognize the UPS (I have nothing in device manager).

I've tried the USB cable in different port of ther server and I've tried the Smart Singaling cable 940-0625A (the one came with the UPS).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:13 AM . Last Modified: ‎2024-02-29 11:27 PM

0 Likes
0
2349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:13 AM . Last Modified: ‎2024-02-29 11:27 PM

We only have a solution for this UPS to support "simple signaling " shutdown of (2) serial clients with use of AP9624. For more than (1) smart client (the server connected directly to the UPS) and (2) simple clients connected to AP9624 installed in the UPS, you'll have to look at the Network Card with PowerChute Network Shutdown as a solution. Alternatively, you could look into scripting a shutdown from a connected client to something that isn't physically connected but that may not be as reliable. Not sure if anyone else has any other ideas but please feel free to share.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:13 AM . Last Modified: ‎2024-02-29 11:27 PM

0 Likes
0
2349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:13 AM . Last Modified: ‎2024-02-29 11:27 PM

Thank you Angela.

If I want to try the script solution how can I trigger the start of the script to send the shutdown command to the other servers?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:13 AM . Last Modified: ‎2024-02-29 11:27 PM

0 Likes
0
2349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:13 AM . Last Modified: ‎2024-02-29 11:27 PM

You would still install PowerChute Business Edition on your "simple" or "smart" clients directly connected to the UPS and that software has the ability to run a command file based on certain events i.e. UPS on battery or UPS has a low battery. I also would say this assumes that the one client could talk to the other over the network or somehow to be able to issue a command file to get it to shutdown.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:14 AM . Last Modified: ‎2024-02-29 11:27 PM

0 Likes
0
2349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:14 AM . Last Modified: ‎2024-02-29 11:27 PM

Thank you Angela.

What is the difference between simple and smart clients?

Based on your suggestions in an Active Directory environment I have to install PCBE on the domain controller and connect it to the UPS with a USB cable. Is it right?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:14 AM . Last Modified: ‎2024-02-29 11:27 PM

0 Likes
0
2349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:14 AM . Last Modified: ‎2024-02-29 11:27 PM

To answer about smart/simple signaling, the best description is here, PDF page 9 -> http://www.apcmedia.com/salestools/PMAR-9EYLYS/PMAR-9EYLYS_R0_EN.pdf

with some additional AP9624 info here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA176957 (Interface Expander 2 SmartSlot Card Smart Signalling Information and Explanation)

I am not sure what is best for your environment but that is a likely scenario. For your UPS model, yes, you'd want to have your smart client connected via USB or serial cable direct to the UPS and if you go with this solution, 2 out of the 3 servers connected via serial to the AP9624 accessory card. Then, have your smart client execute a script to that 3rd server that isn't physically connected.

Is there a particular reason Powerchute Network Shutdown and Management card isn't feasible?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:14 AM . Last Modified: ‎2024-02-29 11:27 PM

0 Likes
0
2349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:14 AM . Last Modified: ‎2024-02-29 11:27 PM

Thanks for the info Angela.

I have 2 problems:

  1. The first and more important: for now there's no budget to buy the additional interface expander or the network card.
  2. Only one server is in the rack while the others 3 servers are in different rooms and plugged in the UPS with an extesion of the power cables. So I can't connect these servers with the USB/Serial cables.

In thi scenario is it a really bad solutions to use PCBE installed on the server in the rack and to script the shutdown of the others?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:14 AM . Last Modified: ‎2024-02-29 11:27 PM

0 Likes
0
2349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:14 AM . Last Modified: ‎2024-02-29 11:27 PM

Gotta work with what you have tongue-out

While it may not be a perfect solution and have risks, I don't see how you can do it any other way beyond scripting. You'll just need to understand the risks and caveats as there are a few points of failure which could prevent a graceful shutdown on those scripted clients.

Even though it is not "supported," you may be able to get both USB and serial connections at the same time to work on this SMT model. (Older models wouldn't work like this at all because of how the communication bus was designed.) That would at least cover (2) of your servers. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:14 AM . Last Modified: ‎2024-02-29 11:27 PM

0 Likes
0
2349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:14 AM . Last Modified: ‎2024-02-29 11:27 PM

Thank you Angela.

I've tried to install PCBE on the server (a Dell T320) but Windows Server can't recognize the UPS.

I've tried the serial/ethernet (smart) cable and the USB cable.

What can I check to resolve this issue?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:14 AM . Last Modified: ‎2024-02-29 11:27 PM

0 Likes
0
2349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:14 AM . Last Modified: ‎2024-02-29 11:27 PM

Ok, so to confirm, your server has a serial port? Or were you using a serial to USB adapter with the "smart" cable? Does Windows server detect the device in Device Manager within the control panel?

You're installing the PowerChute Business Edition Agent component, correct? Let's focus on getting that installed.

Here is a knowledge base article I found, not sure if it applies (assuming you let the software try to auto-detect the UPS) -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA167296 

Did you try a different USB port on the server?

In addition, we have this article with several steps to verify -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA163608 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 12:14 AM . Last Modified: ‎2024-02-29 11:27 PM

0 Likes
0
2350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:14 AM . Last Modified: ‎2024-02-29 11:27 PM

Yes the server has a serial port.

The problem is that Windows don't recognize the UPS (I have nothing in device manager).

I've tried the USB cable in different port of ther server and I've tried the Smart Singaling cable 940-0625A (the one came with the UPS).

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore