On Battery Event Log Question for Smart-UPS 1500 XLM

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • On Battery Event Log Question for Smart-UPS 1500 XLM
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:05 AM . Last Modified: ‎2024-03-12 01:15 AM

0 Likes
5
2591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:05 AM . Last Modified: ‎2024-03-12 01:15 AM

On Battery Event Log Question for Smart-UPS 1500 XLM

Hello,

I have a Smart-UPS 1500 XLM with an  AP9631 NMC FW v5.1.1. We received numerous alerts for this device due to a power issue at the site. The Last Battery Transfer indicates that the UPS went on battery due to unacceptable utility voltage rate of change. There is a lot going on in the logs, most of the entries showing that the 3 outlet groups were being turned on and off. This doesn't look to be normal behavior. Can someone take a look at the attached log file and see if you can make something of it?

Also, at the same site we had another UPS that went on battery. We received an alert for low battery and it eventually drained completely. Right before the ups shut down the outputs, we saw an event stating that a low battery condition no longer exists. I've seen this before on other UPSs during our testing. Is this normal behavior? It doesn't seem correct to me. Here are the logs for this UPS.

12/11/2014 05:18:02 UPS: The power for the outlet group 3, Outlet Group, is now turned off due to UPS turn off.
12/11/2014 05:18:02 UPS: The power for the outlet group 2, Outlet Group, is now turned off due to UPS turn off.
12/11/2014 05:18:02 UPS: The power for the outlet group 1, Outlet Group, is now turned off due to UPS turn off.
12/11/2014 05:18:01 UPS: The output power is turned off.
12/11/2014 05:18:01 UPS: A low battery condition no longer exists.
12/11/2014 04:58:41 UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
12/11/2014 04:58:30 UPS: On battery power in response to an input power problem.

Attachments
Logs for HNL UPS.txt.zip
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:06 AM . Last Modified: ‎2024-03-12 01:15 AM

0 Likes
0
2591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:06 AM . Last Modified: ‎2024-03-12 01:15 AM

Thanks!

Yes, you can go to 6.2.0 but I don't like to force people to it if they don't like it because of the major changes and having to explain the major changes to just validate checking something like this in the log. From your other post, I understand you're familiar with it so I would try that.

If anything for what I saw in the log, I'll blame the UPS but we'll see! As far as reliable method, I know that I haven't seen this issue with the Network Management Card with any types of UPS models and I'll do my best to determine where the issue is - NMC firmware or UPS.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:06 AM . Last Modified: ‎2024-03-12 01:15 AM

0 Likes
0
2591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:06 AM . Last Modified: ‎2024-03-12 01:15 AM

Hi Ryan,

I am confused a little bit on the timestamps in this log file attachment?

What I see in the log you posted in your question looks normal to me. How much runtime on battery does this UPS typically have? somewhere around 20 minutes?

What I see on the blurb you posted is at 4:58, the UPS goes to battery power, it seems to be in a low battery condition at that time (so it sounds like the low battery duration is at a higher value than the default 2 minutes), and then 20 minutes later it (entire UPS and its outlet groups) turns off because it ran out of battery power. The low battery condition now longer exists I think is normal right before it turns off because it is going to turn off right after (or rebooted to finish its cycle if the AC power returned). You'd also see that event if the UPS came back online I think too and AC power returned.

Let me know where I am not making sense but the series of events looks normal to me and you could double check my theory on the Low Battery Duration setting being raised.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:06 AM . Last Modified: ‎2024-03-12 01:15 AM

0 Likes
0
2591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:06 AM . Last Modified: ‎2024-03-12 01:15 AM

Angela,

Thank you for the clarification on the 2nd question. As for the first question; sorry, I forgot to mention that the time and date were a bit off in the attached log file. The log dates should be for this morning, but the times were correct. The attached log is for a separate UPS, but experienced the same power outage as the other UPS. I am confused as to why the other UPS (with logs attached) acted differently. The logs were flooded with events for the outlet groups and turning on and off and for the environmental sensors being connected/disconnected.

Sorry if I am confusing you with two questions, probably should have split these into two different posts. Let me know if you need more clarification.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:06 AM . Last Modified: ‎2024-03-12 01:15 AM

0 Likes
0
2591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:06 AM . Last Modified: ‎2024-03-12 01:15 AM

Hi Ryan,

Thanks for clarifying. Yes, that one does not look right. Do you have the serial number on that UPS itself? Do you know, was the attached equipment actually turning on and off or were these messages erroneous? In my gut, I think something is wrong with the actual UPS and the frequent on/off of the relay and the UPS going to battery is causing communication problems with the Network Management Card to the UPS/Universal I/O ports - some type of electrical interference.

Though, v5.1.1 is very old firmware and I would at least want to try v5.1.7, though I don't really think it will change anything. I just was thinking if it was me, that is what I'd try and see if the logging changes at all or any faults are able to be reported in the UPS. If you want to try that, let me know, and I'll get you v5.1.7 to try.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:06 AM . Last Modified: ‎2024-03-12 01:15 AM

0 Likes
0
2591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:06 AM . Last Modified: ‎2024-03-12 01:15 AM

Here is the info on the UPS:

Model:Smart-UPS 1500 XLM
Serial Number:QS0834230108
Firmware Revision:716.3.D
Manufacture Date:08/22/08

We lost connectivity to the equipment, but I am unsure if it was actually turning on and off. The UPS is located at one of our airports, so I do not have physical access to it. Is there any reliable way of determining if it is a UPS issue or an NMC issue?

As far as the firmware goes, could we upgrade it to v6.2.0? Or are there issues with upgrading that far?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:06 AM . Last Modified: ‎2024-03-12 01:15 AM

0 Likes
0
2592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:06 AM . Last Modified: ‎2024-03-12 01:15 AM

Thanks!

Yes, you can go to 6.2.0 but I don't like to force people to it if they don't like it because of the major changes and having to explain the major changes to just validate checking something like this in the log. From your other post, I understand you're familiar with it so I would try that.

If anything for what I saw in the log, I'll blame the UPS but we'll see! As far as reliable method, I know that I haven't seen this issue with the Network Management Card with any types of UPS models and I'll do my best to determine where the issue is - NMC firmware or UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore