Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Older Symmetra 16kVa + brand new AP9617 = UPS Not Supported message

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Older Symmetra 16kVa + brand new AP9617 = UPS Not Supported message
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
138
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:26 AM . Last Modified: β€Ž2024-03-08 12:08 AM

0 Likes
6
2679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:26 AM . Last Modified: β€Ž2024-03-08 12:08 AM

Older Symmetra 16kVa + brand new AP9617 = UPS Not Supported message

Hello everyone -- thanks in advance for your comments and advice.

I purchased an AP9617 Network Management Card for my single-phase Symmetra system to replace the older AP9606 model. (I've not had good reliability from the AP9606's despite several replacements and troubleshooting.)

In accordance with the install guide, I popped out the old board, and installed the new one. The APC "Configure IP" wizard found the AP9617 on my LAN and let me configure it statically. The web GUI works great and I was able to configure all kinds of things on the card successfully. It even saw the "MeasureUPS II" environmental monitor card and provided readouts, which I could never get the AP9606 to do, oddly. Things looked great until I hit the "UPS" tab, and all I get is "Lost communication to the UPS" on all UPS sections.

The card is installed exactly as described on page 3 of the "multiple management cards" [install guide|http://www.apcmedia.com/salestools/ASTE-6Z5QFC_R0_EN.pdf]. Note, I'm not using any other management card or expansion chassis. Slots 2 and 3 are empty, The AP9617 is occupying the slot where the AP9606 was living.

I decided to reboot the UPS; I put it in maintenance bypass and used System Enable to power off the unit, waited 30 seconds or so, and powered back on. No change.

Then I figured I'd read the [release notes|http://www.apcmedia.com/salestools/ASTE-6Z5QFA_R0_EN.pdf] more carefully. There are multiple firmware .BIN files listed, according to what product the management card is used with. Sounds kind of interesting.

Wanting to see more, I used telnet to log into the card. According to the manual, the line below "Environment:" should list the UPS model. Here, it says "A UPS was found that is not supported by this application." I took a snapshot. Also note the two top lines, at right, where the application doesn't read Symmetra, and firmware on both is 3.5.5. !http://lunatiq.org/images/apc_telnet_shows_unsupported_ups.jpg

I checked available firmware on APC's download page, and for AP9617 firmware for Symmetra, the app version is 3.3.1 and AOS 3.3.4, which are obviously older.

My theory is that I need to downgrade this brand new AP9617 in order to gain Symmetra support. Can anyone confirm this? I'm still waiting for a tech support callback 😞

David

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • ap9617
  • firmware
  • network_management_card
  • symmetra
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:26 AM . Last Modified: β€Ž2024-03-08 12:08 AM

0 Likes
1
2680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:26 AM . Last Modified: β€Ž2024-03-08 12:08 AM

Hello everyone -- thanks in advance for your comments and advice.

I purchased an AP9617 Network Management Card for my single-phase Symmetra system to replace the older AP9606 model. (I've not had good reliability from the AP9606's despite several replacements and troubleshooting.)

In accordance with the install guide, I popped out the old board, and installed the new one. The APC "Configure IP" wizard found the AP9617 on my LAN and let me configure it statically. The web GUI works great and I was able to configure all kinds of things on the card successfully. It even saw the "MeasureUPS II" environmental monitor card and provided readouts, which I could never get the AP9606 to do, oddly. Things looked great until I hit the "UPS" tab, and all I get is "Lost communication to the UPS" on all UPS sections.

The card is installed exactly as described on page 3 of the "multiple management cards" [install guide|http://www.apcmedia.com/salestools/ASTE-6Z5QFC_R0_EN.pdf]. Note, I'm not using any other management card or expansion chassis. Slots 2 and 3 are empty, The AP9617 is occupying the slot where the AP9606 was living.

I decided to reboot the UPS; I put it in maintenance bypass and used System Enable to power off the unit, waited 30 seconds or so, and powered back on. No change.

Then I figured I'd read the [release notes|http://www.apcmedia.com/salestools/ASTE-6Z5QFA_R0_EN.pdf] more carefully. There are multiple firmware .BIN files listed, according to what product the management card is used with. Sounds kind of interesting.

Wanting to see more, I used telnet to log into the card. According to the manual, the line below "Environment:" should list the UPS model. Here, it says "A UPS was found that is not supported by this application." I took a snapshot. Also note the two top lines, at right, where the application doesn't read Symmetra, and firmware on both is 3.5.5. !http://lunatiq.org/images/apc_telnet_shows_unsupported_ups.jpg

I checked available firmware on APC's download page, and for AP9617 firmware for Symmetra, the app version is 3.3.1 and AOS 3.3.4, which are obviously older.

My theory is that I need to downgrade this brand new AP9617 in order to gain Symmetra support. Can anyone confirm this? I'm still waiting for a tech support callback 😞

David

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:26 AM . Last Modified: β€Ž2024-03-08 12:08 AM

0 Likes
1
2680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:26 AM . Last Modified: β€Ž2024-03-08 12:08 AM

I know this is an old thread, but I wanted to post a response in case others are seeking the same answer: the older firmware was, indeed, the solution. After loading the firmware indicated in your response, the card came right up and all functions were available. It is still operating smoothly to this day.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:26 AM . Last Modified: β€Ž2024-03-08 12:08 AM

0 Likes
1
2681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:26 AM . Last Modified: β€Ž2024-03-08 12:08 AM

Hello everyone -- thanks in advance for your comments and advice.

I purchased an AP9617 Network Management Card for my single-phase Symmetra system to replace the older AP9606 model. (I've not had good reliability from the AP9606's despite several replacements and troubleshooting.)

In accordance with the install guide, I popped out the old board, and installed the new one. The APC "Configure IP" wizard found the AP9617 on my LAN and let me configure it statically. The web GUI works great and I was able to configure all kinds of things on the card successfully. It even saw the "MeasureUPS II" environmental monitor card and provided readouts, which I could never get the AP9606 to do, oddly. Things looked great until I hit the "UPS" tab, and all I get is "Lost communication to the UPS" on all UPS sections.

The card is installed exactly as described on page 3 of the "multiple management cards" [install guide|http://www.apcmedia.com/salestools/ASTE-6Z5QFC_R0_EN.pdf]. Note, I'm not using any other management card or expansion chassis. Slots 2 and 3 are empty, The AP9617 is occupying the slot where the AP9606 was living.

I decided to reboot the UPS; I put it in maintenance bypass and used System Enable to power off the unit, waited 30 seconds or so, and powered back on. No change.

Then I figured I'd read the [release notes|http://www.apcmedia.com/salestools/ASTE-6Z5QFA_R0_EN.pdf] more carefully. There are multiple firmware .BIN files listed, according to what product the management card is used with. Sounds kind of interesting.

Wanting to see more, I used telnet to log into the card. According to the manual, the line below "Environment:" should list the UPS model. Here, it says "A UPS was found that is not supported by this application." I took a snapshot. Also note the two top lines, at right, where the application doesn't read Symmetra, and firmware on both is 3.5.5. !http://lunatiq.org/images/apc_telnet_shows_unsupported_ups.jpg

I checked available firmware on APC's download page, and for AP9617 firmware for Symmetra, the app version is 3.3.1 and AOS 3.3.4, which are obviously older.

My theory is that I need to downgrade this brand new AP9617 in order to gain Symmetra support. Can anyone confirm this? I'm still waiting for a tech support callback 😞

David

Reply

Link copied. Please paste this link to share this article on your social media post.

MBCITech
MBCITech
Cadet

Posted: β€Ž2024-03-21 05:44 AM

In response to Anonymous user
0 Likes
0
2229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-03-21 05:44 AM

Thank you for your update on this. We have a very similar situation. I have searched APC Firmware through APC and the only version available for download is the 3.9.3. Where were you able to get the older version of Firmware.?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillC1
Crewman BillC1
Crewman

Posted: β€Ž2024-04-02 09:19 PM

0 Likes
0
2173
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-04-02 09:19 PM

Hello gentlemen,

I have a very similar situation, and now I will maybe LOST my job.

I have mistakenly updated my ap9617 to sumx393 while my apc ups is Symmetra PX. After that the LED showed that the nmc is not supported. Now i want get back my old firmware sy3p v331 but i could not find  it anywhere even at apc.com itself.

Any help, I will be appreciated so much, forever.

  • Tags:
  • ap9617
  • Symmetra PX
Reply

Link copied. Please paste this link to share this article on your social media post.

BillC1
Crewman BillC1
Crewman

Posted: β€Ž2024-04-08 04:14 PM

In response to Anonymous user
0 Likes
0
2121
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-04-08 04:14 PM

Hello brother

Thanks God. Where have you found this AP9617 firmware for Symmetra version 3.3.1 and AOS 3.3.4 ?

Could you please give the link, please?

I have looked for it everywhere. 

Reply

Link copied. Please paste this link to share this article on your social media post.

dpierce4776
Lieutenant dpierce4776
Lieutenant

Posted: β€Ž2024-04-10 07:01 AM

0 Likes
0
2104
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-04-10 07:01 AM

I have a question. Why are you using an AP9617? Those have been EOL for years now.

Also APC uses 2 different firmwares. One for Symmetra marked with SY in the name and one for the rest of their gear. If you do not use the right firmware then it will not work. So with all due respect when you say you upgraded did you use the right firmware?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore