Old 5000RM "Battery Discharged" Notifications...

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Old 5000RM "Battery Discharged" Notifications...
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
114
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
GDI
Crewman GDI
Crewman

Posted: ‎2024-10-18 07:08 PM

0 Likes
7
594
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-18 07:08 PM

Old 5000RM "Battery Discharged" Notifications...

We have an old 5000RM. Batteries are less than a year old.

 

For the past several weeks, at almost the exact same time each night (within seconds), we get 3-5 "Battery Discharged" notifications and then they stop until the next day. We've run a calibration and the run time seems normal. There is nothing on the UPS that does anything that requires any additional power at the same time each night.

 

In trying to track down the issue, we plugged in a Probe 100+ power monitor after the UPS. Basically, it's a power logger that plugs into a computer USB and logs any power fluctuations. Here's the weird part: we plugged in the monitor and received no alerts for 4-5 days. Power stayed steady at 120v. We thought the issue resolved itself so we removed the monitor and the alerts came back that night at the same time and reoccured for 2-3 days. We decide to plug the power monitor back in and the alerts stopped again now for 4 days.

 

So we are a bit baffled. We know this is a very old unit. But don't know why the alerts would stop with the power monitor plugged in but return as soon as remove it.

 

Any ideas?

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
Teken
Spock Teken
Spock

Posted: ‎2024-10-21 04:46 AM

0 Likes
6
591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-21 04:46 AM

Any power quality monitor should be connected to the same electrical outlet. Was this the case in this particular instance as it’s not clear by your description?!?

 

If you have the event and data logs for this system please upload the same here for review.

Reply

Link copied. Please paste this link to share this article on your social media post.

GDI
Crewman GDI
Crewman

Posted: ‎2024-10-21 12:20 PM

In response to Teken
0 Likes
5
532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-21 12:20 PM

The monitor is plugged into the UPS. With the monitor plugged into the UPS, we do not receive battery discharge events. When it is NOT plugged into the UPS, we receive battery discharge events every night at the same time.

 

See the attached log for a sample.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2024-10-22 03:39 AM

In response to GDI
0 Likes
4
524
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-22 03:39 AM

What is connected to the output of the system now?


What happens when you plug in something else like a resistive load such as a light bulb vs a reactive load?

 

Please upload the data logs for this UPS. You can also upload the logs from the power monitor to for comparisons.

Reply

Link copied. Please paste this link to share this article on your social media post.

GDI
Crewman GDI
Crewman

Posted: ‎2024-10-22 04:57 AM

In response to Teken
0 Likes
3
508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-22 04:57 AM

Right now, a few network switches and a few computers are connected to the UPS. We haven't tried any other loads as of yet (ie. resistive loads).

 

Sorry, I must not know what you mean by "data logs". All I can find are event logs, which I uploaded a snippet earlier. This is an old Web/SNMP interface.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2024-10-22 05:21 AM

In response to GDI
0 Likes
2
506
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-22 05:21 AM

The Data Logs if present would show input / output voltage, frequency, battery voltage / capacity, amp / current, load, temperature etc.

 

If APC Power Chute is installed on the two computers you may be able to screen capture the same. 👍

 

The obvious next step is to remove one appliance to see the results. I would also confirm what other loads are connected to this branch circuit.

 

If this isn’t a dedicated circuit I would confirm it’s not shared with something like a copier, fan, microwave, shredder, coffeemaker, dehumidifier, etc.

 

If it is on a dedicated circuit the data from the power quality monitor should indicate surge / sags, frequency, THD, etc.

 

The power quality monitor needs to be connected to the same outlet not the UPS. Given it’s probably a 120 VAC standard plug it won’t connect to the wall outlet. 🤦‍♂️

Reply

Link copied. Please paste this link to share this article on your social media post.

GDI
Crewman GDI
Crewman

Posted: ‎2024-10-22 05:28 AM

In response to Teken
0 Likes
1
447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-22 05:28 AM

Thank you for the info. Yeah, this old Web/SNMP interface doesn't really provide much info. I may see if I can swap it out for a AP9631 or something.

 

You are also correct, the quality monitor is 120 VAC but the 5000RM is 208V, so I can't plug it into the same outlet as the UPS. Seeing as we don't get alerts with the quality monitor plugged into the UPS, we may just leave it as it is. I know it's not a "fix" but this 5000RM is so old it may not be worth investigating. It really should be replaced.

 

Either way, I appreciate the advice!

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2024-10-23 05:03 AM . Last Modified: ‎2024-10-23 05:04 AM

In response to GDI
0 Likes
0
444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-23 05:03 AM . Last Modified: ‎2024-10-23 05:04 AM

If you can swap out the NMC that would be very helpful! 👍

 

Please ensure you set the logs to the maximum retention and if your site has a NMS / Syslog server ensure all metrics are sent to the same.

 

As they will offer historic and longer retention of the faults / metrics. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of