Offsite Control of cooling units

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Offsite Control of cooling units
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-09 03:48 AM . Last Modified: ‎2024-02-14 11:18 PM

0 Likes
3
1752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 03:48 AM . Last Modified: ‎2024-02-14 11:18 PM

Offsite Control of cooling units

We have 2 cooling units in my company , which are working in 12hour rotation cycles, one at a time.
 

Is it possible to turn on, one of the standby cooling units, manually, using some software, from PC?

Currently, physically someone has to come to the Datacenter to switch on the standby unit, if the temperature goes up.

Products used

APC Symmetra PX Frame 160kW 400V SYCF160KH
Uniflair CW 27 to 56 kw Cooling Unit UFCW2756

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 03:48 AM . Last Modified: ‎2024-02-14 11:18 PM

0 Likes
0
1751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 03:48 AM . Last Modified: ‎2024-02-14 11:18 PM

The information was pulled straight from the Operations and Maintenance Manual for the Uniflair. This can be found on our website www.apc.com. I have attached an manual for the US units below.

Thank you

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 03:48 AM . Last Modified: ‎2024-02-14 11:18 PM

0 Likes
0
1751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 03:48 AM . Last Modified: ‎2024-02-14 11:18 PM

Hello Steffin. The Uniflair units come with a sleep mode that can be set up to turn on the standby unit if the temperature or humidity rises above a setpoint. This can be set up through the front screen or through BMS. If you call your local tech support, they can walk you through setting this up on your units. Thank you

Sleep mode
This screen displays the setback function, which can be either
activated or deactivated by using the control panel or BMS. This
function consists of an automatic start-up of the standby unit if the
unit exceeds the following programmable limits for at least 30
seconds:
• Minimum temperature
• Maximum temperature
• Minimum relative humidity (only with optional humidity sensor)
• Maximum relative humidity (only with optional humidity sensor)
The setback function intervenes to control the room conditions—although with larger tolerances— even
if the whole system is in stand-by. Its intervention is independent and not influenced by signals from
remote systems. The intervention of the setback function is not considered an alarm situation.
Fan Cyclical Start: If set to Y, the fan runs in cycles, defined by the cycle time, to allow air from the room
to be drawn across the sensor.
When in setback mode, in the STATUS screen the symbol is displayed. Normal operating conditions
are reset automatically when the temperature values return to values set for [temp. min. + 2°C] + 3.6°F
and for [max. temp. - 2°C] - 3.6°F. A minimum of 15 minutes must pass before the unit exits the setback
mode. This enables stable conditions to be reached and avoids continuous switching on and off of the
fans.
When normal conditions return, the icon is displayed, alternating with other icons depending
on the previous status.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-09 03:48 AM . Last Modified: ‎2024-02-14 11:18 PM

0 Likes
0
1750
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 03:48 AM . Last Modified: ‎2024-02-14 11:18 PM

Thanks for the reply..

Is there any guide, which describes all this , which I can go through?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 03:48 AM . Last Modified: ‎2024-02-14 11:18 PM

0 Likes
0
1752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 03:48 AM . Last Modified: ‎2024-02-14 11:18 PM

The information was pulled straight from the Operations and Maintenance Manual for the Uniflair. This can be found on our website www.apc.com. I have attached an manual for the US units below.

Thank you

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore