OID for Temp
I am looking for the OID for the Temperature on Port 1 Temp 1. I got the battery temp = 1.3.6.1.4.1.318.1.1.1.2.2.2.0 but I really need the one for the Sensor.
- Labels:
-
Getting Started
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 11:06 PM . Last Modified: 2024-03-19 03:22 AM
Hi Clayton,
The OID's for the temp probes can be found in the "environmentalMonitor" subtree - probes are considered "integrated".
The OID for current temp from a probe would be .1.3.6.1.4.1.318.1.1.10.2.3.2.1.4
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 11:06 PM . Last Modified: 2024-03-19 03:22 AM
Hi Clayton,
The OID's for the temp probes can be found in the "environmentalMonitor" subtree - probes are considered "integrated".
The OID for current temp from a probe would be .1.3.6.1.4.1.318.1.1.10.2.3.2.1.4