OID clarification for controlling outlets via SNMP on guest/linked rPDU's?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • OID clarification for controlling outlets via SNMP on guest/linked rPDU's?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:14 AM . Last Modified: ‎2024-03-18 11:33 PM

0 Likes
3
1668
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:14 AM . Last Modified: ‎2024-03-18 11:33 PM

OID clarification for controlling outlets via SNMP on guest/linked rPDU's?

I am looking to clarify my understanding of the OID(s) used for controlling outlets on linked/guest rPDUs.

We all know the base OID for controlling a single rPDU:

rPDUOutletControlIndex 1.3.6.1.4.1.318.1.1.12.3.3.1.1.1
rPDUOutletControlOutletName rPDUOutletControlOutletName 1.3.6.1.4.1.318.1.1.12.3.3.1.1.2
rPDUOutletControlOutletPhase rPDUOutletControlOutletPhase 1.3.6.1.4.1.318.1.1.12.3.3.1.1.3
rPDUOutletControlOutletCommand rPDUOutletControlOutletCommand 1.3.6.1.4.1.318.1.1.12.3.3.1.1.4
rPDUOutletControlOutletBank rPDUOutletControlOutletBank 1.3.6.1.4.1.318.1.1.12.3.3.1.1.5

I have found what I think is the correct OID path for controlling outlets in rPDU2 at: enterprises.318.1.1.26.9.2.4 however I wasn't able to find anything concrete to shore up my assumption:

rPDU2OutletSwitchedControlTable rPDU2OutletSwitchedControlTable 1.3.6.1.4.1.318.1.1.26.9.2.4
rPDU2OutletSwitchedControlEntry rPDU2OutletSwitchedControlEntry 1.3.6.1.4.1.318.1.1.26.9.2.4.1
rPDU2OutletSwitchedControlIndex rPDU2OutletSwitchedControlIndex 1.3.6.1.4.1.318.1.1.26.9.2.4.1.1
rPDU2OutletSwitchedControlModule rPDU2OutletSwitchedControlModule 1.3.6.1.4.1.318.1.1.26.9.2.4.1.2
rPDU2OutletSwitchedControlName rPDU2OutletSwitchedControlName 1.3.6.1.4.1.318.1.1.26.9.2.4.1.3
rPDU2OutletSwitchedControlNumber rPDU2OutletSwitchedControlNumber 1.3.6.1.4.1.318.1.1.26.9.2.4.1.4
rPDU2OutletSwitchedControlCommand rPDU2OutletSwitchedControlCommand 1.3.6.1.4.1.318.1.1.26.9.2.4.1.5

When I walk that it appears to be what I want but before I made assumptions I wanted to ask.

I've attached a txt file with the output from snmpwalk on 1.3.6.1.4.1.318.1.1.26.9.2.4 if that helps.

Thank you 😃

Attachments
Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:14 AM . Last Modified: ‎2024-03-18 11:33 PM

0 Likes
0
1667
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:14 AM . Last Modified: ‎2024-03-18 11:33 PM

Hi Brian,

That looks right. I'd then guess you probably have two, switched 24 outlet PDUs so instance 48 on that OID would indeed be outlet #24 on your second PDU.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:14 AM . Last Modified: ‎2024-03-18 11:33 PM

0 Likes
0
1668
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:14 AM . Last Modified: ‎2024-03-18 11:33 PM

Hi Brian,

Any OID that begins with rPDU is intended to be used with our older style PDUs with model numbers in the AP7XXX range - AP79XX specifically for switched outlet models.

Any OID that begins with rPDU2 is intended to be used with or 2G or 2nd generation PDUs that have model numbers beginning with AP8XXX. The switched models are AP89XX and AP86XX.

If you are using the AP8XXX series and are using the Network Port Sharing feature - which means you'd have host and guest PDUs, then I suggest to read here and refer to the SNMP section to understand how SNMP changes when you have more than one PDU at a single IP address -> http://www.apc.com/us/en/faqsFA164436 

Essentially, you'll need to pay attention to the index numbers for each rPDU2 OID and know which PDU is at which SNMP index, especially if you have more than two PDUs where it can be a little complex. And it gets even more complex if you have a mix and match of PDUs that are switched and those that are metered because certain OIDs are only intended for Switched PDUs.

Anyway, please review what I shared here and let us know if you need any further clarification afterwards.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:14 AM . Last Modified: ‎2024-03-18 11:33 PM

0 Likes
0
1669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:14 AM . Last Modified: ‎2024-03-18 11:33 PM

Angela,

Thanks, I've gone through and ensured outlet# => index => index device owner.

To simplify (please correct me if I'm wrong), to reboot outlet 24 on a PDU-B in a shared gen2 PDU implementation via SNMP I'd send "3" to:

enterprises.318.1.1.26.9.2.4.1.5.48

...where 48 is the index assigned to port 24 on PDU-B.

http://oidref.com/1.3.6.1.4.1.318.1.1.26.9.2.4.1.5

...seems to confirm this - just crossing my T's and dotting my I's. Thanks 😃

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:14 AM . Last Modified: ‎2024-03-18 11:33 PM

0 Likes
0
1668
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:14 AM . Last Modified: ‎2024-03-18 11:33 PM

Hi Brian,

That looks right. I'd then guess you probably have two, switched 24 outlet PDUs so instance 48 on that OID would indeed be outlet #24 on your second PDU.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of