Hi Guys,
I have a SMART-UPS x3000, the device is fully powered and says 100% but it is not producing any output power to my servers. I had to take it out of the equation to get them powered up. I have tested with a test environment PC and nothing from that too.
Has anyone any ideas why it is not producing power? Logs below:
Data log -
"Smart-UPS X 3000 Firmware Version: UPS 07.4 (ID1003) Integrated EMU
Event log -
"
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:34 AM . Last Modified: 2024-03-18 12:21 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:34 AM . Last Modified: 2024-03-18 12:21 AM
Does it produce power when online, or the fault is only when on battery?
If it does not produce power even when online it's definitely a fault. Confirm that the circuit breaker has not tripped or check the panel (that's if you're good at fixing electronics) that the component labelled CT1 is ok.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:34 AM . Last Modified: 2024-03-18 12:21 AM
Hi,
There are a few errors. The first indicates there may be a bad battery or it is an internal fault.
On 3/6/2018 10:26 AM, Michael said:03/06/2018 08:30:48 Device UPS: A battery bus soft start fault exists. 0x015B
The second is the outlet groups are powered off.
On 3/6/2018 10:26 AM, Michael said:03/06/2018 08:30:48 Device UPS: The power for switched outlet group 3, Outlet Group 3, is off. 0x018603/06/2018 08:30:48 Device UPS: The power for switched outlet group 2, Outlet Group 2, is off. 0x018603/06/2018 08:30:48 Device UPS: The power for switched outlet group 1, Outlet Group 1, is off. 0x0186
You can try to re energize the Outlet groups from the LCD panel go to Control and select each outlet group and power them up.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:34 AM . Last Modified: 2024-03-18 12:21 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:34 AM . Last Modified: 2024-03-18 12:21 AM
Hi Bill, thank you for the reply,
Ive tried turning on the Outlets groups but they failed to start and the same error keeps coming back, per below.
Serial Number : 5A1414T13037
Device Serial Number : AS1415144401
Date : 03/08/2018
Time : 10:55:12
Code : 0x015B
Critical - UPS: A battery bus soft start fault exists.
Any other ideas?
Would it be a new battery or do you think the board itself is faulty?
Kind Regards,
Michael.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:34 AM . Last Modified: 2024-03-18 12:21 AM
Hi,
It could be a faulty battery pack or an internal fault. When measuring the battery pack what does it report. A good battery pack should give a reading of around 136v DC since it is made up of 10 12v 5.5ah batteries.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:34 AM . Last Modified: 2024-03-18 12:21 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:34 AM . Last Modified: 2024-03-18 12:21 AM
Hi Bill,
I got this > Refused via managed device due to invalid state. When trying to run any tests.
Kind regards,
Michael.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:34 AM . Last Modified: 2024-03-18 12:21 AM
Hi,
Can you test with a multimeter?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:34 AM . Last Modified: 2024-03-18 12:21 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:34 AM . Last Modified: 2024-03-18 12:21 AM
Does it produce power when online, or the fault is only when on battery?
If it does not produce power even when online it's definitely a fault. Confirm that the circuit breaker has not tripped or check the panel (that's if you're good at fixing electronics) that the component labelled CT1 is ok.