New to racks, need help making decision

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • New to racks, need help making decision
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 02:32 AM . Last Modified: β€Ž2024-03-18 11:10 PM

0 Likes
4
858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:32 AM . Last Modified: β€Ž2024-03-18 11:10 PM

New to racks, need help making decision

Hello,

I need to make the move to racks for my businesses data center, aka my office for the next few months.

I will be mounting an:
IBM ISeries 525
Several Proliant DL series
Several new Dell rackmounts (not sure on model, a software vendor is providing them to me, bu they are new models)
Watchguard x750 firewall
24p switch
shelf for an older non RM server I will phase out.
UPS

Need to know:
1. What racks would work best? 42u is as high as I can go but if there are any shorter racks I don't see myself using much more than 20u soon.
2. Will the IBM and others fit together in the same rack well?
3. What do I need for power distribution in the rack?
4. ?? What else am I forgetting? New to this!

Thanks!

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 02:33 AM . Last Modified: β€Ž2024-03-18 11:10 PM

0 Likes
0
858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:33 AM . Last Modified: β€Ž2024-03-18 11:10 PM

Hello,

I need to make the move to racks for my businesses data center, aka my office for the next few months.

I will be mounting an:
IBM ISeries 525
Several Proliant DL series
Several new Dell rackmounts (not sure on model, a software vendor is providing them to me, bu they are new models)
Watchguard x750 firewall
24p switch
shelf for an older non RM server I will phase out.
UPS

Need to know:
1. What racks would work best? 42u is as high as I can go but if there are any shorter racks I don't see myself using much more than 20u soon.
2. Will the IBM and others fit together in the same rack well?
3. What do I need for power distribution in the rack?
4. ?? What else am I forgetting? New to this!

Thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 02:32 AM . Last Modified: β€Ž2024-03-18 11:10 PM

0 Likes
0
858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:32 AM . Last Modified: β€Ž2024-03-18 11:10 PM

Hello,

I would recommend using the Rack Configurator tool located on the APC website to help determine how to setup and configure your rack. You can even Configure To Order with our AR3100 42U standard SX rack, or the AR2105BLK 25U VX rack. The configurator has an expanse list of Non-APC devices and will be able to determine if they can be mounted in the rack. All standard EIA-310-D compliant pieces of equipment will fit into our Netshelter line of Racks. The configurator will also help you figure out which APC devices can be used, including Rackmount Power Distribution Units.

http://configurator.apcc.com/products/powerstruxure/configurator/PSX_ChooseRackTool.cfm?cc=US&startC...

If all the pieces of equipment are standard EIA-310-D compliant and compatible with 19" wide mounting, there should not be a problem installing the devices into our racks. In terms of Power Distribution, we have 0U PDU's that will fit into a channel in the rear of the rack, and will not take any U space. Something you may be forgetting is keeping the rack cool. We have a variety of fan units that promote proper air flow and can keep your IT equipment safe and cool.

http://www.apc.com/products/category.cfm?id=9&subid=47

Please let us know if there is anything else we can help with. Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 02:33 AM . Last Modified: β€Ž2024-03-18 11:10 PM

0 Likes
0
858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:33 AM . Last Modified: β€Ž2024-03-18 11:10 PM

I have tried the configuration tool. For some reason it shows nothing fitting under the Validations section?

Andy

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 02:33 AM . Last Modified: β€Ž2024-03-18 11:10 PM

0 Likes
0
858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:33 AM . Last Modified: β€Ž2024-03-18 11:10 PM

Use 42U. Never fails πŸ™‚ If you opt for shorter -- it's not that cheap, takes the same space from your floor, you'll have to kneel before it for any maintenance, you wouldn't be able to use any proper cooling systems. 42U -- great investment (especially AR3100) -- it will be suitable for any computer hardware for any foreseeable future.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 02:33 AM . Last Modified: β€Ž2024-03-18 11:10 PM

0 Likes
0
859
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:33 AM . Last Modified: β€Ž2024-03-18 11:10 PM

Hello,

I need to make the move to racks for my businesses data center, aka my office for the next few months.

I will be mounting an:
IBM ISeries 525
Several Proliant DL series
Several new Dell rackmounts (not sure on model, a software vendor is providing them to me, bu they are new models)
Watchguard x750 firewall
24p switch
shelf for an older non RM server I will phase out.
UPS

Need to know:
1. What racks would work best? 42u is as high as I can go but if there are any shorter racks I don't see myself using much more than 20u soon.
2. Will the IBM and others fit together in the same rack well?
3. What do I need for power distribution in the rack?
4. ?? What else am I forgetting? New to this!

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.