New Smart-UPS 1000 SKUSMC1000IC New firmware needed as configuration not accessible

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • New Smart-UPS 1000 SKUSMC1000IC New firmware needed as configuration not accessible
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
adriand2
adriand2
Cadet

Posted: ‎2025-07-01 05:15 AM

0 Likes
2
422
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-01 05:15 AM

New Smart-UPS 1000 SKUSMC1000IC New firmware needed as configuration not accessible

Firmware RevisionUPS 02.0 / COM 02.0 (1061 - 1)
I am reasonably tech savvy and finding this new UPS very frustrating: I am surprised that absolute basics like what the 3 buttons do on the front panel do not agree with my manual. Maybe this is me being daft /?

The buttons on the UPS do not agree with my manual, I cannot seem to enter configuration mode.
Pressing the status enquiry button doesn't do much,  I expected the LCD to illuminate.
Pressing it with the Mute for a while doesn't seem to enter configuration mode; all I get is UPd on the LCD.
Otherwise the UPS is working, except that UPS Communication is intermittent on USB to my Win 11 PC.

The info from the PowerChute software about menu doesn't explicitly state the ID value.

I downloaded and ran FUW and it confirms an update is available. I have looked in the table https://www.se.com/uk/en/faqs/FA279197/ but haven't downloaded any firmware files.
The FUW software seems to come with a set of files and the wizard is selecting SMC1061UPS_02-0.enc.
At this point I have stopped as I need some confidence I am doing this correctly.

Can someone please help.




  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Kirk Teken
Kirk

Posted: ‎2025-07-02 04:08 AM

0 Likes
1
418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-02 04:08 AM

I have appended the user manual for you here which calls out how to enter the configuration mode on page 11:

 

https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=SU_UM_990-5444E_MN0...

 

UPS Firmware: Based on the information you have provided I’m not sure if the first line in your statement indicates you’re already on v2.0 firmware?!?

 

If so, there is no reason to update the (UPS) firmware as this process is extremely dangerous if all prerequisites and instructions are not followed.

 

Firmware should only be done while (in warranty) to address bugs, security, or feature enhancements ~ live over the phone with APC Technical Support.

 

The FUW will always present you with the correct UPS firmware. There is no reason to download any individual files unless instructed to do so or you have experience and knowledge as to why.

 

The SMC is the entry level and stripped down hardware version in the Smart-UPS Series. As such there aren’t very many extra features via the LCD Menu.

 

The Configuration Mode Simply allows you to enable / disable options and features not defaulted by the manufacturer.

 

Key important features are the battery replacement, Smart Connect Remote Commands, Firmware Update, Green Mode, LCD Energy Save.

 

Questions Ask . . . 👍

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Teken
Kirk Teken
Kirk

Posted: ‎2025-07-02 04:08 AM

0 Likes
1
419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-02 04:08 AM

I have appended the user manual for you here which calls out how to enter the configuration mode on page 11:

 

https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=SU_UM_990-5444E_MN0...

 

UPS Firmware: Based on the information you have provided I’m not sure if the first line in your statement indicates you’re already on v2.0 firmware?!?

 

If so, there is no reason to update the (UPS) firmware as this process is extremely dangerous if all prerequisites and instructions are not followed.

 

Firmware should only be done while (in warranty) to address bugs, security, or feature enhancements ~ live over the phone with APC Technical Support.

 

The FUW will always present you with the correct UPS firmware. There is no reason to download any individual files unless instructed to do so or you have experience and knowledge as to why.

 

The SMC is the entry level and stripped down hardware version in the Smart-UPS Series. As such there aren’t very many extra features via the LCD Menu.

 

The Configuration Mode Simply allows you to enable / disable options and features not defaulted by the manufacturer.

 

Key important features are the battery replacement, Smart Connect Remote Commands, Firmware Update, Green Mode, LCD Energy Save.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

adriand2
adriand2
Cadet

Posted: ‎2025-07-02 11:54 PM

In response to Teken
0 Likes
0
404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-02 11:54 PM

I can confirm:

  • I have not done any firmware upgrade and the current revision, as supplied new last week, is UPS 02.0 / COM 02.0 (1061 - 1)

  • The only reason I am looking into this is because when I use the front panel buttons they clearly do  not operate as per the manual I originally found (EN 990-4493F 06/2022) and your referenced manual (EN 990-5444E 10/2023).
  • The mute button doesn't work; I can achieve this via the PowerChute software
  • I cannot enter configuration mode, all I get is 'UPd' displayed, which seems to indicate upgrade in progress.
  • The menu button does nothing, no menus and it doesnt turn the LCD backlight on.
  • I can only get the LCD backlight on by pressing the power button.


When looking into the actions required to do firmware upgrade, one of the key things is checking the ID value, however, the info from the PowerChute software about menu doesn't explicitly state the ID value.

Still looking for help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.