Network Air ACPA4000 air filters

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Network Air ACPA4000 air filters
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:40 AM . Last Modified: ‎2024-02-14 10:53 PM

0 Likes
3
1511
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:40 AM . Last Modified: ‎2024-02-14 10:53 PM

Network Air ACPA4000 air filters

Probably just something I am missing. I have an ACPA 4000 Air conditioning unit that we installed about 2 months ago. About 3 weeks after installing it I recieved a minor alarm informing me that the filter was clogged. No problem. I ordered some replacement filters and swapped it out. The minor alarm never went away. It is still there. I can't find a way through the web interface or the menu on the unit to reset alarms. No idea what is going on. I also checked the intake tube and the mesh insude that for a clog and found nothing.

Is there a way to reset these alarms?

If it is supposed to be automatic than any idea what is causing this issue?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • acpa4000
  • filter
  • minor_alarm
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:40 AM . Last Modified: ‎2024-02-14 10:52 PM

0 Likes
0
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:40 AM . Last Modified: ‎2024-02-14 10:52 PM

The unit uses an adjustable air pressure differential switch to sense the drop in air pressure (restriction) across the air filter and the evaporator coil. Sometimes the switch setting is set too low and causes nuisance trips, which is probably the case when the unit is less than 3 months old. To check/adjust it, you need to make sure the power is OFF (disconnect the power cord); on the left side of the unit there is a small access door, remove the 2 door screws and set the door on the floor very carefully without damaging anything attached to the door; now look into the unit (a flashlight will help) and you will see a small square (about 3" square) box with a blue adjustable dial, that's the pressure switch. Next to the dial is a setpoint indicator, check what setting is at the indicator, adjust the dial to NO MORE THAN 0.8. See attached picture. That should take care of your problem.

If you have a unit older than 3 months, you should make sure that the evaporator coil is clean and the filter is new before making adjustments. You can clean the coil using a soft brush and vacuum cleaner if necessary.

Remember the air pressure switch senses air restriction across the air filter and coil and, once properly adjusted, is meant to advise the customer that the filter (and coil) needs maintenance. How often maintenance is required depends on site conditions.

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:40 AM . Last Modified: ‎2024-02-14 10:53 PM

0 Likes
0
1511
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:40 AM . Last Modified: ‎2024-02-14 10:53 PM

Probably just something I am missing. I have an ACPA 4000 Air conditioning unit that we installed about 2 months ago. About 3 weeks after installing it I recieved a minor alarm informing me that the filter was clogged. No problem. I ordered some replacement filters and swapped it out. The minor alarm never went away. It is still there. I can't find a way through the web interface or the menu on the unit to reset alarms. No idea what is going on. I also checked the intake tube and the mesh insude that for a clog and found nothing.

Is there a way to reset these alarms?

If it is supposed to be automatic than any idea what is causing this issue?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:40 AM . Last Modified: ‎2024-02-14 10:52 PM

0 Likes
0
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:40 AM . Last Modified: ‎2024-02-14 10:52 PM

It doesn't seem like anyone has any advise to offer. I know cooling units are certainly not my expertise. I would recommend calling the APC Cooling product support at 800-890-4272 if you have not already.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:40 AM . Last Modified: ‎2024-02-14 10:52 PM

0 Likes
0
1510
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:40 AM . Last Modified: ‎2024-02-14 10:52 PM

The unit uses an adjustable air pressure differential switch to sense the drop in air pressure (restriction) across the air filter and the evaporator coil. Sometimes the switch setting is set too low and causes nuisance trips, which is probably the case when the unit is less than 3 months old. To check/adjust it, you need to make sure the power is OFF (disconnect the power cord); on the left side of the unit there is a small access door, remove the 2 door screws and set the door on the floor very carefully without damaging anything attached to the door; now look into the unit (a flashlight will help) and you will see a small square (about 3" square) box with a blue adjustable dial, that's the pressure switch. Next to the dial is a setpoint indicator, check what setting is at the indicator, adjust the dial to NO MORE THAN 0.8. See attached picture. That should take care of your problem.

If you have a unit older than 3 months, you should make sure that the evaporator coil is clean and the filter is new before making adjustments. You can clean the coil using a soft brush and vacuum cleaner if necessary.

Remember the air pressure switch senses air restriction across the air filter and coil and, once properly adjusted, is meant to advise the customer that the filter (and coil) needs maintenance. How often maintenance is required depends on site conditions.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore