Needing more power for new rack

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Needing more power for new rack
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:52 PM . Last Modified: ‎2024-03-15 02:54 AM

0 Likes
8
1271
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:52 PM . Last Modified: ‎2024-03-15 02:54 AM

Needing more power for new rack

I'm looking to power a new rack, right now we have 3 servers powered off of a SmartUPS 700 rackmount. We have pretty beefy servers on there now 2 of them are Dell PowerEdge 2950's with 2 quad core processors in each and the other one PowerEdge 1850 is just has 2 dual core 3ghz. It can't handle the power right now and according to Dell each server is taking around 2.3amps or around 450-500w each. We are planning on adding two more of the 2950's in the future so I'm wondering what you would suggest that is rack-mountable that could support the power load of all 5 of these servers?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:52 PM . Last Modified: ‎2024-03-15 02:53 AM

0 Likes
0
1265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:52 PM . Last Modified: ‎2024-03-15 02:53 AM

Problem is I am looking for something that has a standard 120v plug input and several 120v plug outputs.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:52 PM . Last Modified: ‎2024-03-15 02:54 AM

0 Likes
0
1266
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:52 PM . Last Modified: ‎2024-03-15 02:54 AM

Infact now I hear I must plan for 2 of them and we want to run a total of 10 servers (plan on running in the near future) so we need something to support 6 servers right now and 4 more in the future. I was also told to allow it to support some other devices but I don't think they make UPS's that large to run all our phone switches, kvm switches, firewalls along with those servers allowing only 2 ups's, I don't think thats possible. Again, if it supports the regular 3 prong plugs input and output 120v that's what I'm looking for. After doing the automatic system configuration tool for selecting a UPS it chose something with 220v input and outputs

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:52 PM . Last Modified: ‎2024-03-15 02:54 AM

0 Likes
0
1266
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:52 PM . Last Modified: ‎2024-03-15 02:54 AM

I'm running about 7 Dell 2950 servers each with dual power supply units, a couple switches, kvm switch monitor combo. We only have NEMA 5P-15 plugs 120v and I would like several of the UPS units to cover protection for them. Anyone got any suggestions please??

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:52 PM . Last Modified: ‎2024-03-15 02:54 AM

0 Likes
0
1270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:52 PM . Last Modified: ‎2024-03-15 02:54 AM

Not that I want to divert income from APC but have you considered vitualization instead of adding more servers?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 06:52 PM . Last Modified: ‎2024-03-15 02:53 AM

0 Likes
0
1270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:52 PM . Last Modified: ‎2024-03-15 02:53 AM

The largest UPS you can utilize that has NEMA 5-15P input plugs is the SUA1500RM2U. The problem therein lies that if you put 2 or 3 servers with redundant PS's on there, and they all transfer over to the same 1500 at the same time, the inrush current may overload the UPS, and if this is during an on battery state, will cause everything to power down. For proper graceful shutdown, you are also looking at 1 AP9617 Network Management Card for each UPS, and doing a custom install of PowerChute Network Shutdown.

If the electrical requirements can be changed to a hardwire, 4 wire system from the service panel, I would recommend a Symmetra LX as your main UPS, with one NMC controlling shutdown on all servers, and then either hardwire out to receptacles to power each rack, or install backplates onto the LX that would feed 120V PDU's in the rear of each rack.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:52 PM . Last Modified: ‎2024-03-15 02:53 AM

0 Likes
0
1269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:52 PM . Last Modified: ‎2024-03-15 02:53 AM

Okay, What I was thinking of is placing one ps from a server on one UPS and one on the other UPS. I don't think they would redo the electrical connections for me so that's where I'm stuck, the building just got built and they just spent a ton of money on it. Now the servers can run on only a single ps so I wouldn't see a problem when your running on battery mode just running on a single power supply.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 06:52 PM . Last Modified: ‎2024-03-15 02:53 AM

0 Likes
0
1269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:52 PM . Last Modified: ‎2024-03-15 02:53 AM

Hello,

If you're looking at 1 or two servers to two UPS (1 PS from each server to each UPS), that should not be a problem. However, you might want to inquire as to why the building was facilitated with only NEMA 5-15R's. Usually the commercial standard at the MINIMUM is NEMA 5-20R. They should have also given you capabilities for 208V input as well, especially if this is within a designed data center, or server room.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:52 PM . Last Modified: ‎2024-03-15 02:53 AM

0 Likes
0
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:52 PM . Last Modified: ‎2024-03-15 02:53 AM

I'm looking to power a new rack, right now we have 3 servers powered off of a SmartUPS 700 rackmount. We have pretty beefy servers on there now 2 of them are Dell PowerEdge 2950's with 2 quad core processors in each and the other one PowerEdge 1850 is just has 2 dual core 3ghz. It can't handle the power right now and according to Dell each server is taking around 2.3amps or around 450-500w each. We are planning on adding two more of the 2950's in the future so I'm wondering what you would suggest that is rack-mountable that could support the power load of all 5 of these servers?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:52 PM . Last Modified: ‎2024-03-15 02:53 AM

0 Likes
0
1266
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:52 PM . Last Modified: ‎2024-03-15 02:53 AM

Problem is I am looking for something that has a standard 120v plug input and several 120v plug outputs.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore