Need help in configuring 2x ACRD201 in small server room
Hi
We have 2 CRAC units Model number CRD201 they were set up as a group but one originally failed due to an error message of high discharge pressure alarm and most recently persistent low suction pressure alarm.
Will need help to configuring it properly and identify the root cause of the unit (CRAC1) failing. I have attached the current configs and status of each unit. Any help will be appreciated.
Server room size 3.6 metres wide x 5.6m length
jgUhtIaNLMGDQXp6vfSUMA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png
CRAC1 configs
WzhZJhdaKXETLNG4GMxg8A%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png
X9qziEJVjUei%2BLfXKIuEwg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png
uBd06gP64jNmfajROnuU5g%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png
CRAC2 configs
EBjO78mhIuPMzb3fwoCLEA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png
6qg6ruH4dDc%2FS8V6oOSGqw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png
9azNMuqBVUH3JxXNYZ8K2Q%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png
GROUP configs
9GjQoj6tw5PWkZo72qzAjA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png
cZYdkvyYvNrUuJWUFbwBHg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png
FuDUGjImEF43W%2Blh7X4n6Q%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png
Unit Type
InRow RD 10KW Water/Glycol Cooled 50Hz
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:19 AM . Last Modified: 2024-02-14 11:04 PM
Hello. The last warranty I see on this unit went out in June 2015. This unit is out of warranty.
Thank you
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:19 AM . Last Modified: 2024-02-14 11:04 PM
Hello Kent. From the information provided it looks like there is a refrigerant leak somewhere in system one. It is low on pressure and has a very high superheat. An HVAC tech will need to go through the unit and look for leaks. You can also call into your local apc technical support with the serial numbers on the units to check on if they are in warranty.
Thank you
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-07-09 04:19 AM . Last Modified: 2024-02-14 11:04 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:19 AM . Last Modified: 2024-02-14 11:04 PM
Thanks Support Services, can we find out the warranty status of this unit?
Serial Number: JK1402331150
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:19 AM . Last Modified: 2024-02-14 11:04 PM
Hello. The last warranty I see on this unit went out in June 2015. This unit is out of warranty.
Thank you