Need constant values for APC Smart-UPS 900XLI (old unit)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Need constant values for APC Smart-UPS 900XLI (old unit)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:37 AM . Last Modified: ‎2024-03-17 11:56 PM

0 Likes
2
889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:37 AM . Last Modified: ‎2024-03-17 11:56 PM

Need constant values for APC Smart-UPS 900XLI (old unit)

Hello,

I have an old Smart-UPS 900XLI unit (the one which may be extended with up to 10 external battery packs), serial beginning with S9403, firmware revision is 7TI, circuit board REV7. I'd really appreciate if you could share the factory default constant values for EEPROM registers 0,5,6. Low battery is detected too early, battery constant value probably drifted off far from the original value. Registers 5,6 may be fine, but I'd like to compare against my unit's registers. Interesting experience: this is not the first UPS of this generation that I find with drifted constant values. On this generation of units however, drifting seems to happen only if the DIP switches have been all transferred to the 1 position (and left there for years), and when a calibration tool or management software has been used to alter EEPROM values.

Thanks in advance!

hUqeXYdoGjcqwFCHCESfMw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeghUqeXYdoGjcqwFCHCESfMw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:37 AM . Last Modified: ‎2024-03-17 11:56 PM

0 Likes
0
889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:37 AM . Last Modified: ‎2024-03-17 11:56 PM

Here is the whole procedure I did:

-soldered a jumper wire to R178 resistor, so it measured 0.0 ohms across its leads

-transferred all of the DIP switches to position 1

-using a terminal emulation program over RS232, I asked for the values of registers 5,6,0 by sending the ASCII values 5,6,0 respectively. 

-I kept adjusting register 5 by sending ASCII character 2 as many times as it was needed to cycle to the proper value. (register 0 is adjusted via character 4)

-after reaching the desired value, I confirmed the functionality of the UPS

-turned off the unit, retransferred DIP switches to position 0

-removed the jumper wire from R178

I hope this may be useful to someone. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:37 AM . Last Modified: ‎2024-03-17 11:56 PM

0 Likes
0
889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:37 AM . Last Modified: ‎2024-03-17 11:56 PM

I have successfully reset the constants to their good (or close to good) values. I happened to have a Smart-UPS 900I (non XL version) around with roughly the same manufacture date and same firmware (7TI). This UPS unit used as a reference had the following values:

5 - F3
6 - FC
0 - 9F

My 900XLI had these:

5 - 9D
6 - FC
0 - A0


I already knew that register 0 is used to determine the available runtime versus battery charge level (ASCII 'f') & load (ASCII 'P'). I had no idea about the other two values. The only difference was register 5, and after correcting it, low battery is no longer detected too early, and battery leds are correctly lit all the way up & lowering slowly as the load depletes the batteries. This makes me believe that register 5 probably determines the battery capacity which is likely calculated somehow using the detected battery voltage.

I did a manual runtime test so that I could accurately set register 0 to display remaining runtime correctly. With new batteries, the 900XLI ran for 88 minutes under ~390W load using 1 external battery pack. The stock '9F' / 'A0' setting was no good for this, it only shows 17 minutes for the given load. I pushed the register 0 value up to 'FE', increasing runtime to 34 minutes, which is still far from the 88 minutes measured manually. Value 'FF' is maximum, but it translates to infinite runtime (>>>> minutes). Concluding all of the above, my final settings are:

5 - F3
6 - FC
0 - FE

I am also inclined to think now (as opposed to my previous post) that these register values do not drift by themselves, at least not in these very old units. Likely the previous owner or a service center attempted to do software calibration and messed up things while doing so.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:37 AM . Last Modified: ‎2024-03-17 11:56 PM

0 Likes
0
890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:37 AM . Last Modified: ‎2024-03-17 11:56 PM

Here is the whole procedure I did:

-soldered a jumper wire to R178 resistor, so it measured 0.0 ohms across its leads

-transferred all of the DIP switches to position 1

-using a terminal emulation program over RS232, I asked for the values of registers 5,6,0 by sending the ASCII values 5,6,0 respectively. 

-I kept adjusting register 5 by sending ASCII character 2 as many times as it was needed to cycle to the proper value. (register 0 is adjusted via character 4)

-after reaching the desired value, I confirmed the functionality of the UPS

-turned off the unit, retransferred DIP switches to position 0

-removed the jumper wire from R178

I hope this may be useful to someone. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore