Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

Need Help COnfiguring PCBE for Multi-Server Shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Need Help COnfiguring PCBE for Multi-Server Shutdown
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Mr._Chip_apc
Mr._Chip_apc
Cadet

Posted: ‎2021-06-30 08:08 AM

0 Likes
1
184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 08:08 AM

Need Help COnfiguring PCBE for Multi-Server Shutdown

This was originally posted on APC forums on 2/7/2009


Hello

I am hoping someone can help me configure my UPS and PCBE installation. I have a 6-year old Smart-UPS 1400 RMXL unit with three additional battery packs daisy chained to it. A little over a year ago I bought all new genuine APC batteries for the entire system. I am self employed so the roughly $1,500 I spent on batteries was not trivial. I used to have two W2K servers connected to the UPS. I just upgraded my entire server rack so I now have a total of 4 servers being protected. One of the four is one of the original W2K servers. So I now have:

One W2K server (old web server)
One 2003 SBS server (primary domain controller)
One 2003 Enterprise server (backup domain controller)
One 2008 Server (new web server)

Note: There will only be a 1-2 month period when the old web server (W2K) and new web server (2008) are both running. After this testing period the old web server will be unplugged and retired.

I purchased a port expansion card so my 1400 now has three serial and one USB connector. I am a lifelong APC customer and have so many PowerChute disks that I could build a sculpture out of them. Unfortunately, I cannot seem to locate the original disk that came with the 1400. I downloaded the latest version of PowerChute Business Edition from APC and tried installing it on the SBS box (which I want to act as the PowerChute Server). I want to program the UPS to do the following. In the event of a power loss, keep everything on for 15 minutes. If the power is still out, I would want it to do an orderly shutdown of the Backup Domain Controller. If I also have both web servers running, I also want it to shutdown whichever web server is not being used in production at this time. So after 15 minutes the UPS will be powering the SBS domain controller and the production web server. Then it should keep both of these online until there is only 10% battery power left. At that point it should shut them both down, probably the web server first and then the SBS.

Question #1. Can I do all of this with PCBE and my port expansion card?

Question #2: Assuming the answer to Q1 is yes, what ports does PCBE use to communicate with all of the servers. My set-up is protected by a hardware firewall that is partitioned into several zones. I may need to "punch holes" in the firewall for the PCBE to communicate with all of the servers.

Question #3. I have been told that the AP9617 network management card would be a "nicer" solution since it requires a single connection to the network and can be controlled over the LAN. If I buy one of these cards would my PCBE software work or would I also need to buy PowerChute Network Shutdown. I can swing the cost of the card, but if the card and s/w cost around $500 I would very much like to stay with my current solution.

Question #4. I have tried installing the PCBE Agent on the SBS server. It is unable to auto detect the UPS. I checked and confirmed I am using the correct APC serial cable. I also made sure the COM port is configured in the suggested way. Any suggestions on why the server can't see the UPS?

Thanks so much! I have literally spent 3+ hours Googling this trying to find an answer on my own.

Chip

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • configuration
  • network
  • PowerChute
  • shutdown
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:08 AM

0 Likes
0
184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 08:08 AM

This reply was originally posted by Angela on APC forums on 2/9/2009


hi,

hopefully I can assist here:

> Question #1. Can I do all of this with PCBE and my port expansion card?

Yes, you can do this but you can only have one server attached to the serial port on the UPS that will be able to communicate in "smart signaling" mode. Smart signaling is where the UPS and computer can essentially communicate back and forth. The rest of the ports on the serial interface expander card will only be able to comminicate in "simple signaling" mode. This means the UPS can only essentially tell the server that there is a "low battery" and that is when the devices connected to the serial interface expander will shutdown. The only thing you can do is change the low battery signaling time on the UPS via the computer attached to the serial port on the UPS which can change the value because its in "smart signaling mode." So essentially, you will only be able to customize the shutdown on the computer attached to the "smart signaling" port on the UPS. The rest will only shutdown based on the low battery signaling time. I think this may be a hassle due to what you are looking to do and the cabling required. 940-0020B cables are required for the two devices using simple signaling and then you probably have the 940-0024/940-1524 cable needed for smart signaling.

> Question #2: Assuming the answer to Q1 is yes, what ports does PCBE use to communicate with all of the servers. My set-up is protected by a hardware firewall that is partitioned into several zones. I may need to "punch holes" in the firewall for the PCBE to communicate with all of the servers.

[see this article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=2790]. and FYI, here is what all the components of business edition are if you arent sure. The free version is just a single node agent.

There are 3 components to PCBE deluxe, Agent, Server and Console. The agent runs as a background service on each server with a data connection to the UPS. Please note that only these servers will shutdown. The role of the Agent is to monitor the UPS and initiate a shutdown based upon configurable UPS events. The role of the Server is to provide centralized monitoring and control of numerous PCBE Agents. The role of the Console is to provide a remote graphical interface for any and all PCBE server modules on the network. The freeware version of PCBE can accommodate 1 Agents per UPS installation. The server and console run only on Windows platforms, but each agent has a web user interface, which can be used for non-Windows environments.










> Question #3. I have been told that the AP9617 network management card would be a "nicer" solution since it requires a single connection to the network and can be controlled over the LAN. If I buy one of these cards would my PCBE software work or would I also need to buy PowerChute Network Shutdown. I can swing the cost of the card, but if the card and s/w cost around $500 I would very much like to stay with my current solution.

I totally agree with this. It requires a lot less cabling (uses the network as you mentioned) and you can get an AP9617 NMC for around $250-$300. Powerchute network shutdown is free and is a lot more customizable than the above solution with the serial interface expander card. Also, Powerchute Business Edition, the paid version if you needed it to monitor all the UPSs from one GUI, is double the cost and I think a network management card would work a heck of a lot better for you. You then will also have a web interface to monitor everything and can set up email notifications, SNMP, SSH, etc. You can log into a network management card to test even at [http://testdrive.apc.com] so that you can see if you like it. I highly recommend doing this and would be happy to assist you in configuring it.




> Question #4. I have tried installing the PCBE Agent on the SBS server. It is unable to auto detect the UPS. I checked and confirmed I am using the correct APC serial cable. I also made sure the COM port is configured in the suggested way. Any suggestions on why the server can't see the UPS?

If this is on the interface expander, as I mentioned before, it will use simple signaling. You'd have to manually choose simple signaling mode/interface expander with a Smart UPS. If you are using the smart signaling port, I am not sure why it couldnt detect it. I'd first recommend removing the simple signaling devices/cables from the UPS and trying again.

Hope this helps!! please let me know if you have any other questions or comments.

See Answer In Context

Reply
Share
Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:08 AM

0 Likes
0
185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-30 08:08 AM

This reply was originally posted by Angela on APC forums on 2/9/2009


hi,

hopefully I can assist here:

> Question #1. Can I do all of this with PCBE and my port expansion card?

Yes, you can do this but you can only have one server attached to the serial port on the UPS that will be able to communicate in "smart signaling" mode. Smart signaling is where the UPS and computer can essentially communicate back and forth. The rest of the ports on the serial interface expander card will only be able to comminicate in "simple signaling" mode. This means the UPS can only essentially tell the server that there is a "low battery" and that is when the devices connected to the serial interface expander will shutdown. The only thing you can do is change the low battery signaling time on the UPS via the computer attached to the serial port on the UPS which can change the value because its in "smart signaling mode." So essentially, you will only be able to customize the shutdown on the computer attached to the "smart signaling" port on the UPS. The rest will only shutdown based on the low battery signaling time. I think this may be a hassle due to what you are looking to do and the cabling required. 940-0020B cables are required for the two devices using simple signaling and then you probably have the 940-0024/940-1524 cable needed for smart signaling.

> Question #2: Assuming the answer to Q1 is yes, what ports does PCBE use to communicate with all of the servers. My set-up is protected by a hardware firewall that is partitioned into several zones. I may need to "punch holes" in the firewall for the PCBE to communicate with all of the servers.

[see this article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=2790]. and FYI, here is what all the components of business edition are if you arent sure. The free version is just a single node agent.

There are 3 components to PCBE deluxe, Agent, Server and Console. The agent runs as a background service on each server with a data connection to the UPS. Please note that only these servers will shutdown. The role of the Agent is to monitor the UPS and initiate a shutdown based upon configurable UPS events. The role of the Server is to provide centralized monitoring and control of numerous PCBE Agents. The role of the Console is to provide a remote graphical interface for any and all PCBE server modules on the network. The freeware version of PCBE can accommodate 1 Agents per UPS installation. The server and console run only on Windows platforms, but each agent has a web user interface, which can be used for non-Windows environments.










> Question #3. I have been told that the AP9617 network management card would be a "nicer" solution since it requires a single connection to the network and can be controlled over the LAN. If I buy one of these cards would my PCBE software work or would I also need to buy PowerChute Network Shutdown. I can swing the cost of the card, but if the card and s/w cost around $500 I would very much like to stay with my current solution.

I totally agree with this. It requires a lot less cabling (uses the network as you mentioned) and you can get an AP9617 NMC for around $250-$300. Powerchute network shutdown is free and is a lot more customizable than the above solution with the serial interface expander card. Also, Powerchute Business Edition, the paid version if you needed it to monitor all the UPSs from one GUI, is double the cost and I think a network management card would work a heck of a lot better for you. You then will also have a web interface to monitor everything and can set up email notifications, SNMP, SSH, etc. You can log into a network management card to test even at [http://testdrive.apc.com] so that you can see if you like it. I highly recommend doing this and would be happy to assist you in configuring it.




> Question #4. I have tried installing the PCBE Agent on the SBS server. It is unable to auto detect the UPS. I checked and confirmed I am using the correct APC serial cable. I also made sure the COM port is configured in the suggested way. Any suggestions on why the server can't see the UPS?

If this is on the interface expander, as I mentioned before, it will use simple signaling. You'd have to manually choose simple signaling mode/interface expander with a Smart UPS. If you are using the smart signaling port, I am not sure why it couldnt detect it. I'd first recommend removing the simple signaling devices/cables from the UPS and trying again.

Hope this helps!! please let me know if you have any other questions or comments.

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc