Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

NTP Update Causes E-mail Alert: System: Set Daylight Saving Time

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • NTP Update Causes E-mail Alert: System: Set Daylight Saving Time
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:33 AM

0 Likes
6
903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:33 AM

NTP Update Causes E-mail Alert: System: Set Daylight Saving Time

This question was originally posted by Michael on APC forums on 9/24/2012


Hello,

I have an AP9618 UPS Management Card inside a Smart UPS RT 3000 XL UPS. The AP9618 is using Application Module sumx v3.7.2 2-2-2010 and APC OS (AOS) v3.7.3 2-2-2010. The clock is set to update via NTP every 24 hours to Central Time (-06:00 hours). Daylight Saving Time is set for Traditional US DST (Second Sunday in March, First Sunday in November). My problem is every time the UPS synchronizes with the NTP server I receive an e-mail message stating System: Set Daylight Saving Time Code: 0x003D. I don't know why because DST is set correctly and the UPS retrieves the correct time for our time zone. I've tried using Custom DST but that hasn't solved the problem. I tried using different NTP servers but that hasn't solved the problem. Does anyone know why this is happening or had the problem before? Thank you.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
jgonya_apc
Crewman jgonya_apc
Crewman

Posted: ‎2021-07-01 01:33 AM

0 Likes
0
902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:33 AM

This was originally posted on APC forums on 6/7/2013


I recently updated the firmware for the management card, AP9617, to the same version, and it is doing the exact same thing.  I will have to disable the message too.

It also will not let me replace the batteries online anymore.  As soon as I disconnected the battery the UPS shutdown.  I was always able to hot-swap them before.  I usually have to replace the batteries every 2 years.  I really wish I didn't update the firmware.

See Answer In Context

Reply
Share
Replies 6
jgonya_apc
Crewman jgonya_apc
Crewman

Posted: ‎2021-07-01 01:33 AM

0 Likes
0
903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:33 AM

This was originally posted on APC forums on 6/7/2013


I recently updated the firmware for the management card, AP9617, to the same version, and it is doing the exact same thing.  I will have to disable the message too.

It also will not let me replace the batteries online anymore.  As soon as I disconnected the battery the UPS shutdown.  I was always able to hot-swap them before.  I usually have to replace the batteries every 2 years.  I really wish I didn't update the firmware.

Reply
Share
jgonya_apc
Crewman jgonya_apc
Crewman

Posted: ‎2021-07-01 01:33 AM

0 Likes
0
903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:33 AM

This was originally posted on APC forums on 6/7/2013


I had the replacement battery ready to go.  I only had the battery disconnected for a minute.  I received a "The battery is not installed properly" message in the log on the management card, and then the UPS turned off.  The next message in the management card log was "Network service started" and "Coldstart" a minute later when I connected the new battery.  In the logs on each of the servers I had connected to the UPS using PowerChute Network Shutdown software was the message "Battery has been disconnected".

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:33 AM

0 Likes
0
904
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:33 AM

This reply was originally posted by Angela on APC forums on 6/7/2013


The NMC firmware update has nothing to do with affecting the batteries being hot swappable so I suspect something else is going on with the battery situation and it is just a coincidence..perhaps the UPS tried to transfer to battery for something (sag, electrical noise, etc) and the battery was briefly disconnected.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:34 AM

0 Likes
0
904
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:34 AM

This reply was originally posted by Angela on APC forums on 6/7/2013


well we can start a new thread and look at the logs for that issue but i am 99.9% sure this has nothing to do with updating the firmware on the management card.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:34 AM

0 Likes
0
904
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:34 AM

This reply was originally posted by Angela on APC forums on 9/25/2012


yes, i have seen this before. i'd suggest you just disable this message from emailing you specifically or logging in the event log. i think it is just a firmware "bug" if you will that provides this message every time the sync is done if the time is adjusted.

let me know if you need help doing that.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:34 AM

0 Likes
0
904
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:34 AM

This reply was originally posted by Michael on APC forums on 10/30/2012


That's what I did. I disabled the e-mail notification since the time is correct anyway. Thank you.

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc