NTP Update Causes E-mail Alert: System: Set Daylight Saving Time

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • NTP Update Causes E-mail Alert: System: Set Daylight Saving Time
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:33 AM . Last Modified: ‎2024-03-06 01:34 AM

0 Likes
6
3518
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:33 AM . Last Modified: ‎2024-03-06 01:34 AM

NTP Update Causes E-mail Alert: System: Set Daylight Saving Time

Hello,

I have an AP9618 UPS Management Card inside a Smart UPS RT 3000 XL UPS. The AP9618 is using Application Module sumx v3.7.2 2-2-2010 and APC OS (AOS) v3.7.3 2-2-2010. The clock is set to update via NTP every 24 hours to Central Time (-06:00 hours). Daylight Saving Time is set for Traditional US DST (Second Sunday in March, First Sunday in November). My problem is every time the UPS synchronizes with the NTP server I receive an e-mail message stating System: Set Daylight Saving Time Code: 0x003D. I don't know why because DST is set correctly and the UPS retrieves the correct time for our time zone. I've tried using Custom DST but that hasn't solved the problem. I tried using different NTP servers but that hasn't solved the problem. Does anyone know why this is happening or had the problem before? Thank you.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:33 AM . Last Modified: ‎2024-03-06 01:34 AM

0 Likes
0
3517
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:33 AM . Last Modified: ‎2024-03-06 01:34 AM

I recently updated the firmware for the management card, AP9617, to the same version, and it is doing the exact same thing.  I will have to disable the message too.

It also will not let me replace the batteries online anymore.  As soon as I disconnected the battery the UPS shutdown.  I was always able to hot-swap them before.  I usually have to replace the batteries every 2 years.  I really wish I didn't update the firmware.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:33 AM . Last Modified: ‎2024-03-06 01:34 AM

0 Likes
0
3518
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:33 AM . Last Modified: ‎2024-03-06 01:34 AM

I recently updated the firmware for the management card, AP9617, to the same version, and it is doing the exact same thing.  I will have to disable the message too.

It also will not let me replace the batteries online anymore.  As soon as I disconnected the battery the UPS shutdown.  I was always able to hot-swap them before.  I usually have to replace the batteries every 2 years.  I really wish I didn't update the firmware.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:33 AM . Last Modified: ‎2024-03-06 01:34 AM

0 Likes
0
3518
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:33 AM . Last Modified: ‎2024-03-06 01:34 AM

I had the replacement battery ready to go.  I only had the battery disconnected for a minute.  I received a "The battery is not installed properly" message in the log on the management card, and then the UPS turned off.  The next message in the management card log was "Network service started" and "Coldstart" a minute later when I connected the new battery.  In the logs on each of the servers I had connected to the UPS using PowerChute Network Shutdown software was the message "Battery has been disconnected".

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:33 AM . Last Modified: ‎2024-03-06 01:34 AM

0 Likes
0
3519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:33 AM . Last Modified: ‎2024-03-06 01:34 AM

The NMC firmware update has nothing to do with affecting the batteries being hot swappable so I suspect something else is going on with the battery situation and it is just a coincidence..perhaps the UPS tried to transfer to battery for something (sag, electrical noise, etc) and the battery was briefly disconnected.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:34 AM . Last Modified: ‎2024-03-06 01:34 AM

0 Likes
0
3519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:34 AM . Last Modified: ‎2024-03-06 01:34 AM

well we can start a new thread and look at the logs for that issue but i am 99.9% sure this has nothing to do with updating the firmware on the management card.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:34 AM . Last Modified: ‎2024-03-06 01:34 AM

0 Likes
0
3519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:34 AM . Last Modified: ‎2024-03-06 01:34 AM

yes, i have seen this before. i'd suggest you just disable this message from emailing you specifically or logging in the event log. i think it is just a firmware "bug" if you will that provides this message every time the sync is done if the time is adjusted.

let me know if you need help doing that.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:34 AM . Last Modified: ‎2024-03-06 01:34 AM

0 Likes
0
3519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:34 AM . Last Modified: ‎2024-03-06 01:34 AM

That's what I did. I disabled the e-mail notification since the time is correct anyway. Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now