NMC2 not responding to HTTP

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • NMC2 not responding to HTTP
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:15 PM . Last Modified: ‎2024-03-14 03:00 AM

0 Likes
4
2788
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:15 PM . Last Modified: ‎2024-03-14 03:00 AM

NMC2 not responding to HTTP

Just setup our SURTA3000RMXL3U last night with one add'l battery pack.
Put a 9630 NMC2 in it as well.
I can, without issue, Telnet into it and do anything I want in Telnet. It can ping anything within Telnet.
APC Firmware Upgrade Tool can see it.
I can configure it via ARP as well.

But nomatter what, nomatter which free IP I assign to it, I cannot access the UPS via HTTP and it is driving me out of my mind. I can ping it just fine but when it comes to the web admin page - nothing.

I flashed its FW from 5.0.1 to 5.0.3 which made no behavioral difference.

I ONCE - on the very first attempt - logged in via HTTP and was using it just great, but after I ran a Self Test I have yet to see a single response on HTTP at all.

I've thrice fully powered=off the UPS, I've tried using the NMC2's Reset button (which AFAIK is only for Password resetting, not a full factory default restoration?), I've reseated the NMC2 into the unit twice and nothing I'm doing is making any difference to the behavior.

With all that said I feel very unknowledgeable about UPS's so please assume nothing if you're so king to respond.
...but what am I overlooking in my shooting-in-the-dark troubleshooting process? Is this a UPS issue and not a NMC2 issue somehow?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 2
  • 9630
  • card
  • connect
  • http
  • management
  • network
  • nmc2
  • problem
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 11:15 PM . Last Modified: ‎2024-03-14 03:00 AM

0 Likes
0
2786
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:15 PM . Last Modified: ‎2024-03-14 03:00 AM

As a first step for troubleshooting, I would use FTP to download the config.ini file and the event log and then post them here.

What error message does your browser give when attempting to access the NMC? What happens if you try a different browser?

Additionally, using the CLI you may want to check to make sure the NMC's HTTP server is not disabled or set to HTTPS, and that it is set to use port 80.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 11:15 PM . Last Modified: ‎2024-03-14 03:00 AM

0 Likes
0
2787
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:15 PM . Last Modified: ‎2024-03-14 03:00 AM

As a first step for troubleshooting, I would use FTP to download the config.ini file and the event log and then post them here.

What error message does your browser give when attempting to access the NMC? What happens if you try a different browser?

Additionally, using the CLI you may want to check to make sure the NMC's HTTP server is not disabled or set to HTTPS, and that it is set to use port 80.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:15 PM . Last Modified: ‎2024-03-14 03:00 AM

0 Likes
0
2786
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:15 PM . Last Modified: ‎2024-03-14 03:00 AM

Thanks for the fast reply. Now I can try something new. I'm standing in a grocery store right now but when I get him I'll VPN in and try this out. The only thing I can say immediately is that FF/IE simply give a page cannot be displayed style error-and quickly too. No timing out, it spits that out fairly quickly.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:15 PM . Last Modified: ‎2024-03-14 03:00 AM

0 Likes
0
2785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:15 PM . Last Modified: ‎2024-03-14 03:00 AM

Awesome stuff Voidstar:
Telnet's web command showed that I had changed the HTTP port to 8080. Working late in the night helped me misunderstand exactly what I was doing: seems pretty dumb of me in hindsight but I was thinking the admin page was asking me what port to use to GET TO the web. Never did I wonder WHY a UPS would need to get to the web (maybe for firmware update notifications?) but I immediately plugged-in my proxy's port 8080 and went along my way.

What a relief - this was really irritating me!

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 11:15 PM . Last Modified: ‎2024-03-14 03:00 AM

0 Likes
0
2785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:15 PM . Last Modified: ‎2024-03-14 03:00 AM

I'm glad we could get it working.

Not so dumb, eventually we may need to have proxy settings on the NMC.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore