I have downloaded the config.ini file from several of my NMCs trying to put together a comprehensive list of settings to push out to several dozen UPSs, but none of them seem to be complete, they tend to end mid-setting in many cases. I've made changes and when the new config.ini is created, it still ends in the same place.
Example:
; Environment: A fault no longer exists for external Environmental Monitor input contact 2 ({name} at {location}).
E0304=ES,E[-:-:-:],T[:::::],P[:::]
; Environ
That's it. it ends there.
Any ideas? I need a full list of all of the settings to make sure my notifications are are setup comprehensively. How many settings are there? Is there a full list somewhere? Will I be able to upload everything or is there a limit to the file size (or length) you can upload?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:44 PM . Last Modified: 2024-02-29 11:46 PM
Mostly (possibly all) AP9631 NMC are being used.
I have been using ftp to download the config.ini file directly. That's the file that was ending.
In the web interface, I couldn't find the "generate logs" on most of my devices (Old Firmware). So ... updating a whole bunch of Management Card firmwares I guess.
But ... Yes that was very helpful, downloading the logs that way did give me the whole file it seems.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:44 PM . Last Modified: 2024-02-29 11:46 PM
Hi Steve,
What model NMC do you have? AP9630/31/35, embedded NMC in a PDU, etc?
What method are you using to download the config.ini file? Have you tried the "generate logs" method through the web interface? Under About --> Support, then click "generate logs" and "download".
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:44 PM . Last Modified: 2024-02-29 11:46 PM
Mostly (possibly all) AP9631 NMC are being used.
I have been using ftp to download the config.ini file directly. That's the file that was ending.
In the web interface, I couldn't find the "generate logs" on most of my devices (Old Firmware). So ... updating a whole bunch of Management Card firmwares I guess.
But ... Yes that was very helpful, downloading the logs that way did give me the whole file it seems.
Thanks!