My ups show totally wrong "UPS Load" value.
  • My ups show totally wrong "UPS Load" value.
5060
139
Erasmus_apc
Sisko Erasmus_apc
112
oddman_apc
oddman_apc
Cadet
Posted: ‎2021-06-30 10:51 PM . Last Modified: ‎2024-03-06 10:36 PM
1514
I use the PowerChute Bussiness Edititon 9.1.1 software. So for the “UPS Load” in this program show me 0.0% value when I attached to this ups a device which consumption about 400 Watt. The 5 led of the ups left site does not lit this time. The bottommost led of the ups left side just lit when I load the ups with about 500 Watt. So I think this leds indicator and the PCBE software show me totally wrong ups load value. The front panel leds work fine certainly because I tested them from the PowerChute software. I used the “Test Alarm” option.
So is it a hardware malfunction? Or can I calibrate the ups load display indicator somehow?
Thank you for your helps in advance.
Sorry for my bad English. 🙂
My UPS type: APC Smart-UPS 1000 (SU1000INET)
My UPS cable type: RS232 940-0024C
  • fault
  • problem
  • smart-ups
Janeway
Just a guess, but perhaps:
Your device is only using 100 watts (squelched to 0% in PCBE) at the moment and later goes up to 200 causing the first light on the load indicator to light up.
Janeway