My Symmetra UPS Clients (Windows server 2008) unexpected shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • My Symmetra UPS Clients (Windows server 2008) unexpected shutdown
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 06:05 AM . Last Modified: ‎2024-03-04 11:51 PM

0 Likes
3
773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:05 AM . Last Modified: ‎2024-03-04 11:51 PM

My Symmetra UPS Clients (Windows server 2008) unexpected shutdown

I have a APC Symmetra LX 16kVA. I installed PowerChute on Widnows server 2008 clients and configured PCNS in case of Overheating of Server room (40C) or upon low power. I noted that the shutdown was taking place even when the temperature was reached. Confused, I un-installed powerchute software from the windows clients and even disconnected the UPS from the LAN.

Still the servers keep shutting down, at unexpected times. I have also noted that some few workstations in the LAN are also shutting down upon booting, though I still do not know whether that is connected to UPS!

What will be the cause of the shutdown, colleagues?

Thanks

Andrew

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:05 AM . Last Modified: ‎2024-03-04 11:51 PM

0 Likes
0
773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:05 AM . Last Modified: ‎2024-03-04 11:51 PM

Do you have any logs from the PCNS clients?

OK, so let's start here:

[Symmetra]

VoutReporting=Auto

FreqVoltOverload=Go to Bypass

AlarmRedundancyUnder=Never

AlarmLoadOver=Never

AlarmRuntimeUnder=5

ReturnBatteryCapacity=0

LowBatteryDuration=12

ShutdownDelay=120

ReturnDelay=0

SleepTime=000

UPSName=UPS_IDEN

UPSPosition=RACK

ExternalBatteryCabinet=0000

BatteryDate=09/00/14

SimpleSignalShutdown=enabled

SelfTestSchedule=Every 14 days

You have it set to alarm you if the runtime is under 5 minutes. If I look in the event log, I see a lot of things going on. I see this telling me you're hitting this low runtime threshold (several times) that you've set: UPS: A runtime alarm threshold violation exists.    0x0227. It is possible that PowerChute Network Shutdown is reacting to this but I'd have to see that log/configuration to be sure.

How much is your total runtime? How old are the batteries? You also have the LowBatteryDuration set to 12 so that ultimately, when 12 minutes of runtime are remaining, your UPS will have a "low battery" which every PowerChute Network Shutdown client is forced to shutdown at that mark. Do you know why this is set a bit high? It likely wouldn't be a problem if you had hours and hours of runtime. But if the batteries are older, then maybe this is something that based on the frequency of input power problems/on battery events, is showing itself now.

Thus, total runtime, age of batteries, intended configuration, and comments on my comments are what I'd say we need to discuss next.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:05 AM . Last Modified: ‎2024-03-04 11:51 PM

0 Likes
0
773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:05 AM . Last Modified: ‎2024-03-04 11:51 PM

Hello,

The most helpful thing for us will be the Network Management Card (in the UPS)'s logs - event.txt, data.txt, config.ini. Instructions are here on how to download it and please just help point out the timestamps when you saw issues, if possible ->How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...

Also, PowerChute Network Shutdown software contains a log of it's own. We'd want that too along with the pcnsconfig.ini file from the PowerChute installations where you saw this issue so we have an overview of the events and any configuration. Some of this may be a moot point though now if the logs have been deleted and the configuration is different after uninstalling.

One thing that comes to mind is we'd want to see what triggered the shutdown if possible and then if the UPS is not allowed to complete it's reboot process, it could still be trying to send the shutdown command. It can be rebooted to stop this but that is just a uneducated guess.

Hope that helps get you started.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 06:05 AM . Last Modified: ‎2024-03-04 11:51 PM

0 Likes
0
773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:05 AM . Last Modified: ‎2024-03-04 11:51 PM

Config.ini text

Edit by Angela N: To make this more manageable to read, I took the text from the logs and put them back in .txt files to attach to each post to avoid scrolling. (attachments can be added if you use the "advanced editor" on your reply.)

I am deleting the other two replies and just attaching all the files here.

Attachments
event.txt.zip
data.txt.zip
config.ini.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:05 AM . Last Modified: ‎2024-03-04 11:51 PM

0 Likes
0
774
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:05 AM . Last Modified: ‎2024-03-04 11:51 PM

Do you have any logs from the PCNS clients?

OK, so let's start here:

[Symmetra]

VoutReporting=Auto

FreqVoltOverload=Go to Bypass

AlarmRedundancyUnder=Never

AlarmLoadOver=Never

AlarmRuntimeUnder=5

ReturnBatteryCapacity=0

LowBatteryDuration=12

ShutdownDelay=120

ReturnDelay=0

SleepTime=000

UPSName=UPS_IDEN

UPSPosition=RACK

ExternalBatteryCabinet=0000

BatteryDate=09/00/14

SimpleSignalShutdown=enabled

SelfTestSchedule=Every 14 days

You have it set to alarm you if the runtime is under 5 minutes. If I look in the event log, I see a lot of things going on. I see this telling me you're hitting this low runtime threshold (several times) that you've set: UPS: A runtime alarm threshold violation exists.    0x0227. It is possible that PowerChute Network Shutdown is reacting to this but I'd have to see that log/configuration to be sure.

How much is your total runtime? How old are the batteries? You also have the LowBatteryDuration set to 12 so that ultimately, when 12 minutes of runtime are remaining, your UPS will have a "low battery" which every PowerChute Network Shutdown client is forced to shutdown at that mark. Do you know why this is set a bit high? It likely wouldn't be a problem if you had hours and hours of runtime. But if the batteries are older, then maybe this is something that based on the frequency of input power problems/on battery events, is showing itself now.

Thus, total runtime, age of batteries, intended configuration, and comments on my comments are what I'd say we need to discuss next.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of