My KVM2132P unit drops configuration additions & reboots when I make config changes. This problem has been present ever since I've deployed it.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • My KVM2132P unit drops configuration additions & reboots when I make config changes. This problem has been present ever sinc...
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
wojciech.galuszka_apc
Crewman wojciech.galuszka_apc
Crewman

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-12 01:15 AM

0 Likes
1
614
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-12 01:15 AM

My KVM2132P unit drops configuration additions & reboots when I make config changes. This problem has been present ever since I've deployed it.

Hi Everyone,

I am dealing with a bizarre problem with a KVM2132P unit ('APC KVM 2G, Enterprise Digital/IP, 2 Remote Users, 1 Local User, 32 ports with Virtual Media').

Ever since I deployed this IP KVM in early January 2014, I've been noticing that the KVM would sometimes kick me out of the web GUI when I was making configuration changes such as creating new local users or assigning host or PDU outlet access to users.

This is still happening.   I'd like to determine what is causing it and how I could correct it.   Here are the relevant architecture & configuration details.

The single KVM2132P is connected to 7 KVM0216A units ('APC KVM 2G, Enterprise Analog, 2 Local Users, 16 ports with Virtual Media') in a two-bus tiered configuration.

The KVM2132P is running v1.0.083 firmware.   The KVM0216A are running v1.0.077 firmware.

To five KVM0216A units, I've connected 2 x AP8941 ('Rack PDU 2G, Switched, ZeroU, 30A, 200/208V, (21) C13 & (3) C19').   To 2 KVM0216A units, I've connected 1 x AP8941.

The IP KVM uses a RADIUS server to authenticate its end users.   To create new local users, I connect to the KVM over HTTPS and use the web GUI.   At this time, I have 38 local users.

There are 68 servers that connect to KVM0216A units via KVM-USB ('APC KVM 2G, Server Module, USB').   Power is provided by 12 APC UPS units ('SUA5000RMT5U').

We allow users to power-on,power-off,reboot outlets on AP8941 PDUs that are assigned to them.

I feel that I've already submitted a flood of information that might or might not be required to troubleshoot this problem.   I've opened an APC Case in September & techs have been trying to find the reason for this weirdness but so far without success.

They've analyzed my configuration file and concluded that it did not look abnormal.    They sent me a new KVM2132P hardware to which I uploaded my configuration file, but the issues persist.

They sent me a newer (not yet released to general public) firmware for the KVM2132P ('KVM2132P1_0_086CC_001.CSF'), but that didn't solve the problem.

My current best guess is that there is no problem with the hardware, but that buggy firmware (from ATEN) somehow passed Quality Assurance and made it into the KVM2132P hardware sold to customers.

If you have any thoughts or suggestions about the above, I'd really like to hear from you.   I've been debugging this problem for over 2 months & I am running out of ideas & things to try.

Wojciech Galuszka / UNIX Systems Administrator / ENCS IT

//    ing. jr member of l'Ordre des ingenieurs du Quebec

//    B.Eng //


Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • buggy_firmware
  • digital_kvm
  • ip
  • kvm
  • kvm2132p
  • rebooting
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-12 01:14 AM

0 Likes
0
613
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-12 01:14 AM

Hi,

Sorry - I was on vacation so I apologize for the lack of reply. Though, my colleague was working with you I think and now he is on vacation for a few weeks. I know this has been annoying and I thank you for your patience while helping us debug it. I will check in on this today as I know we made a few suggestions to try and identify what criteria must be true for this to happen and on what firmwares. This was escalated internally and will continue to be until we are able to provide you with a suitable resolution.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-12 01:14 AM

0 Likes
0
614
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-12 01:14 AM

Hi,

Sorry - I was on vacation so I apologize for the lack of reply. Though, my colleague was working with you I think and now he is on vacation for a few weeks. I know this has been annoying and I thank you for your patience while helping us debug it. I will check in on this today as I know we made a few suggestions to try and identify what criteria must be true for this to happen and on what firmwares. This was escalated internally and will continue to be until we are able to provide you with a suitable resolution.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of