Most Common Matrix 5000 Failures

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Most Common Matrix 5000 Failures
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:33 PM

0 Likes
4
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:33 PM

Most Common Matrix 5000 Failures

I get the impression that these Matrix 5000 UPS units are very reliable. Even so, nothing lasts forever. Just curious for those of you that have experience with the Matrix 5000 units, what is the most common mode of failure (apart from batteries)? What part of the unit usually fails first (upper control unit or lower transformer unit), and what components usualy fail?

Thanks.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:02 AM . Last Modified: ‎2024-03-13 11:33 PM

0 Likes
0
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:02 AM . Last Modified: ‎2024-03-13 11:33 PM

I concur that the MX5000 is one of the most reliable ups around - here at the University of B.C. there are units that were some of the very first off the assembly line that are still in service - we are talking 1993/94 vintage - 17 years old now! I have done all sorts of repairs on these, mostly common repair is rebuilding the smartcells with fresh panasonic batteries, (Tip: be watchful of the smartcells, as the built in fault light system does not always work properly. If you ever hear your matrix emitting continuosu chirping sounds this means the battery charger is working overtime as it is forcing current thru a faulty battery - and the Matrix's battery charging circuits are so powerful that a failed (resistive) smartcell can quickly melt down (cells overheat and swell badly and will crack open and leak acid). The second most common fault is the need to replace the EU and IU cooling fans which are rated at 80,000 hours. Another point of failure is the interconnectivity between the EU and IU. Its a good idea to put the UPS in bypass every 2 - 3 years , remove the EU and clean the contact busses on the bottom of the EU (circuit board edge connection and metal power/ground bus fingers)...oxidation of the contacts can lead to problems. Only once did I experience a dropped load becasue of this; the EU shut down (blank display). When I have the two halves apart I also take this one step further and clean the inside of the EU and vacuum off the air intakes on the IU (blow the dust out) as these can get plugged with dust easily as the vent holes are skinny.

...Dave

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:33 PM

0 Likes
0
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:33 PM

I get the impression that these Matrix 5000 UPS units are very reliable. Even so, nothing lasts forever. Just curious for those of you that have experience with the Matrix 5000 units, what is the most common mode of failure (apart from batteries)? What part of the unit usually fails first (upper control unit or lower transformer unit), and what components usualy fail?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:33 PM

0 Likes
0
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:33 PM

Hello!

I have Matrix 5000 and Matrix 3000 with the same trouble. Both pass self test after powering them on, but during 5 minutes after that, indicate "Bypass relay fault". Can you advice what could be the reason.
Another question - may be anyone does have schematic or service manual for Matrix UPS. Could you please share with me. Thanks in advance.
Regards,
Sergey

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:33 PM

0 Likes
0
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:33 PM

The Matrix units are definitely very reliable (we see units from "98-"99 all the time still kicking along. I would say the The Electronics Unit is more like to go first just due to the nature of the electronic components in it. The Isolation unit is a fairly simple isolation step down transformer that will most likely outlast the Electronics unit. That being said 90% of the interactions I deal with the matrix are always battery issues, even with these units form "98-"99. Hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:02 AM . Last Modified: ‎2024-03-13 11:33 PM

0 Likes
0
1510
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:02 AM . Last Modified: ‎2024-03-13 11:33 PM

I concur that the MX5000 is one of the most reliable ups around - here at the University of B.C. there are units that were some of the very first off the assembly line that are still in service - we are talking 1993/94 vintage - 17 years old now! I have done all sorts of repairs on these, mostly common repair is rebuilding the smartcells with fresh panasonic batteries, (Tip: be watchful of the smartcells, as the built in fault light system does not always work properly. If you ever hear your matrix emitting continuosu chirping sounds this means the battery charger is working overtime as it is forcing current thru a faulty battery - and the Matrix's battery charging circuits are so powerful that a failed (resistive) smartcell can quickly melt down (cells overheat and swell badly and will crack open and leak acid). The second most common fault is the need to replace the EU and IU cooling fans which are rated at 80,000 hours. Another point of failure is the interconnectivity between the EU and IU. Its a good idea to put the UPS in bypass every 2 - 3 years , remove the EU and clean the contact busses on the bottom of the EU (circuit board edge connection and metal power/ground bus fingers)...oxidation of the contacts can lead to problems. Only once did I experience a dropped load becasue of this; the EU shut down (blank display). When I have the two halves apart I also take this one step further and clean the inside of the EU and vacuum off the air intakes on the IU (blow the dust out) as these can get plugged with dust easily as the vent holes are skinny.

...Dave

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore