Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84690members
354063posts

Monitor flickers for a second while going from back up to online power

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
7
619

Monitor flickers for a second while going from back up to online power

This question was originally posted by Abhishek on APC forums on 10/29/2016


I have a SMART ups SUA 2200i.I have just noticed an strange issue for the first time.Whenever the ups switches from battery back up to online the monitor flickers for a second.I don't think I saw this behaviour earlier or perhaps I just noticed it now.Is it a usual behaviour for the equipments such as monitors connected to smart UPS to flicker or lose power for about a second?The interesting thing is that  when the ups switches to battery back up there is no flicker or power loss for a second . So this is a case of finding out the reverse transfer time for ups.Any help appreciated.


Accepted Solutions
Brad_C_apc
Commander
Commander
0 Likes
0
619

Re: Monitor flickers for a second while going from back up to online power

This was originally posted on APC forums on 11/5/2016


Relay switching time has nothing to do with transfer time on a SmartUPS. All the relay does is *disconnect* the line input, the UPS is already generating the required sine, just not switched onto the inverter. The transfer time is really the time for the UPS to decide the mains has dropped and the inverter to start. The relay's in a Smart UPS are there to boost/trim and disconnect the incoming line only.

See Answer In Context

7 Replies 7
BillP
Administrator Administrator
Administrator
0 Likes
0
619

Re: Monitor flickers for a second while going from back up to online power

This reply was originally posted by Nicole on APC forums on 10/31/2016


Hi Abhishek, 

Our Smart UPS line of UPSs have a typical transfer time of 2-4ms when switching from online to on battery and vice versa. It seems your monitor is just reacting to the transfer time of the UPS. As long as all your equipment stays on and is not being affected by the transfer time, I believe you have nothing to worry about. 

Regards, 

Nicole 

Kiriakos_GR_apc
Ensign
Ensign
0 Likes
0
619

Re: Monitor flickers for a second while going from back up to online power

This was originally posted on APC forums on 11/2/2016


You may also consider this possibility of PC monitor internal electronics at power supply as old and in need for refurbishing. 

If monitor this is 4~6 years old.

BillP
Administrator Administrator
Administrator
0 Likes
0
619

Re: Monitor flickers for a second while going from back up to online power

This reply was originally posted by Gareth on APC forums on 11/2/2016


It does sound like deteriorated capacitors as I have never noticed any monitor flicker, only light bulbs.

BillP
Administrator Administrator
Administrator
0 Likes
0
619

Re: Monitor flickers for a second while going from back up to online power

This reply was originally posted by Abhishek on APC forums on 11/4/2016


Well the equipment is being affected  as it is not performing optimally and this is irritating to say the least.But thanks for the info about reverse transfer time.Can you point me to any APC documentation/FAQ where reverse transfer time is mentioned (not transfer time).

BillP
Administrator Administrator
Administrator
0 Likes
0
619

Re: Monitor flickers for a second while going from back up to online power

This reply was originally posted by Abhishek on APC forums on 11/4/2016


Monitor is just 3 months old.Model is xl2420g from BenQ,not exactly cheap quality stuff.

Kiriakos_GR_apc
Ensign
Ensign
0 Likes
0
619

Re: Monitor flickers for a second while going from back up to online power

This was originally posted on APC forums on 11/4/2016


Few posts above Nicole wrote: Our Smart UPS line of UPSs have a typical transfer time of 2-4ms when switching from online to on battery and vice versa ... 

Now me as electrician I am aware that mechanical electrical relay specifications are not that tight. 

Usual relay at best this is 5ms when new, and it is possible this to further deteriorate due age? or simply because something got wrong at production stage.

Either way, anything it can be measured and inspected but not for end user him self.

According my book only a freelancer electronics repair specialist with true knowledge and lots of high-End tools he would find the problem and exchange anything bad with new. 

Brad_C_apc
Commander
Commander
0 Likes
0
620

Re: Monitor flickers for a second while going from back up to online power

This was originally posted on APC forums on 11/5/2016


Relay switching time has nothing to do with transfer time on a SmartUPS. All the relay does is *disconnect* the line input, the UPS is already generating the required sine, just not switched onto the inverter. The transfer time is really the time for the UPS to decide the mains has dropped and the inverter to start. The relay's in a Smart UPS are there to boost/trim and disconnect the incoming line only.