Hello,
I need to get the power from all outlets of an AP8653. I would use snmp, so I need to know the MIB OID. I find rPDUOutletStatusLoad that returns the load in Amps, but I need the power in watts. Do you know what OID I should use?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:23 AM . Last Modified: 2024-03-18 02:23 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:23 AM . Last Modified: 2024-03-18 02:23 AM
Thanks for your reply. It's the OID that I need!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:23 AM . Last Modified: 2024-03-18 02:23 AM
you should be under the rpdu2 tree to begin.
try these OIDs - you should get a reply for each outlet
.iso.org.dod.internet.private.enterprises.apc.products.hardware.rPDU2.rPDU2Outlet.rPDU2OutletMetered
under here you'll see: rPDU2OutletMeteredStatusTable, then rPDU2OutletMeteredStatusEntry. under there is the breakdown. a reply should come back for each outlet. i assume you need .1.3.6.1.4.1.318.1.1.26.9.4.3.1.7 which is
.iso.org.dod.internet.private.enterprises.apc.products.hardware.rPDU2.rPDU2Outlet.rPDU2OutletMetered.rPDU2OutletMeteredStatusTable.rPDU2OutletMeteredStatusEntry.rPDU2OutletMeteredStatusPower
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:23 AM . Last Modified: 2024-03-18 02:23 AM
you're welcome 🙂
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:23 AM . Last Modified: 2024-03-18 02:23 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:23 AM . Last Modified: 2024-03-18 02:23 AM
Thanks for your reply. It's the OID that I need!