Hey guys,
I am new to this whole power thing but am slowly learning. We have a rack at a Colo and they are bringing the A Side power down for an entire week. This leaves each rack running on B side power only. One of our racks (the SAN and blade server rack) is now at 22.7 amps. My question is this: This PDU is on a 32 AMP circuit but the threshold of the PDU itself is 24 amps. What does or should that mean to me? Am I too close to tripping a breaker for comfort or am I okay?
The other issue is if we spin up more VM's (20 more to be exact) it will push the amps up closer to 24 amps.
Looking for someone to educate me on the risk of being this close. The model PDU we are using is: AP8841
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:56 AM . Last Modified: 2024-03-18 01:06 AM
AP8841 PDU is a 30A PDU. Per National Electrical Code here in the US, a circuit is not supposed to use more than 80% of its rating meaning this PDU is de-rated to 24A which is 80% of 30A.
So, your overload threshold is at 24A for the entire PDU because of that 80% rating.
Then each PDU bank (or groups of outlets) is 16A (de-rated 80% from a 20A circuit cause they have 20A breakers) on there I believe so between the two banks, you shouldn't go over 24A and each bank or group of outlets you shouldn't go over 16A.
The breakers actually trip at either 30A (at your panel) or 20A for each bank. It should technically have a 30A breaker and not 32A.
Am I making sense?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:56 AM . Last Modified: 2024-03-18 01:06 AM
AP8841 PDU is a 30A PDU. Per National Electrical Code here in the US, a circuit is not supposed to use more than 80% of its rating meaning this PDU is de-rated to 24A which is 80% of 30A.
So, your overload threshold is at 24A for the entire PDU because of that 80% rating.
Then each PDU bank (or groups of outlets) is 16A (de-rated 80% from a 20A circuit cause they have 20A breakers) on there I believe so between the two banks, you shouldn't go over 24A and each bank or group of outlets you shouldn't go over 16A.
The breakers actually trip at either 30A (at your panel) or 20A for each bank. It should technically have a 30A breaker and not 32A.
Am I making sense?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:56 AM . Last Modified: 2024-03-18 01:06 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:56 AM . Last Modified: 2024-03-18 01:06 AM
Hey guys,
I am new to this whole power thing but am slowly learning. We have a rack at a Colo and they are bringing the A Side power down for an entire week. This leaves each rack running on B side power only. One of our racks (the SAN and blade server rack) is now at 22.7 amps. My question is this: This PDU is on a 32 AMP circuit but the threshold of the PDU itself is 24 amps. What does or should that mean to me? Am I too close to tripping a breaker for comfort or am I okay?
The other issue is if we spin up more VM's (20 more to be exact) it will push the amps up closer to 24 amps.
Looking for someone to educate me on the risk of being this close. The model PDU we are using is: AP8841
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:56 AM . Last Modified: 2024-03-18 01:06 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:56 AM . Last Modified: 2024-03-18 01:06 AM
yes. you are correct on the 30 amp. My mistake . I am also managing each bank as you stated above keeping each below 16 Amps.
So if I am understanding you correctly: Right now I am at 21.6amps total balanced across the two 16 amp banks. In theory, If I were to run at, let's say .... 25 amps total for a short period (less than 8 hours), (16 amps on one bank and 9 amps on the other) .. how much risk am a I looking at in tripping a breaker?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:56 AM . Last Modified: 2024-03-18 01:06 AM
You're within 5 amps of tripping your upstream breaker which brings the whole PDU down
So I would make sure there is no fluctuation and expect the PDU to constantly be alarming you (so you might want to tone down your notification settings during this period).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:56 AM . Last Modified: 2024-03-18 01:06 AM
Glad to hear!