I want to chart power usage across time, on my in-rack PDUs, and I'm having trouble finding the Object Values for the 2nd (daisy-chained) PDU.
SNMPv2-MIB::sysDescr.0 = STRING: APC Web/SNMP Management Card (MB:v4.1.0 PF:v6.4.0 PN:apc_hw05_aos_640.bin AF1:v6.4.0 AN1:apc_hw05_rpdu2g_640.bin MN:AP8841 HR:02 SN: 5A1516E01497 MD:04/14/2015)
SNMPv2-MIB::sysObjectID.0 = OID: PowerNet-MIB::masterSwitchrPDU2
I can see that I have (2) PDUs:
PowerNet-MIB::rPDU2BankTableSize.0 = INTEGER: 2
PowerNet-MIB::rPDU2BankConfigIndex.1 = INTEGER: 1
PowerNet-MIB::rPDU2BankConfigIndex.2 = INTEGER: 2
Which allows me to grab total Amp draw on each one:
PowerNet-MIB::rPDU2BankStatusCurrent.1 = INTEGER: 14
PowerNet-MIB::rPDU2BankStatusCurrent.2 = INTEGER: 0
But I do not see anything similar for Power. I was expecting to see something like:
PowerNet-MIB::rPDU2BankStatusPower.1 = INTEGER: 14
PowerNet-MIB::rPDU2BankStatusPower.2 = INTEGER: 0
But these MIB entries aren't there (and are not defined in PowerNet-MIB
I have found the following:
PowerNet-MIB::rPDUIdentDevicePowerWatts.0 = INTEGER: 240
PowerNet-MIB::rPDUIdentDevicePowerFactor.0 = INTEGER: 810
PowerNet-MIB::rPDUIdentDevicePowerVA.0 = INTEGER: 290
PowerNet-MIB::rPDU2DeviceStatusPower.1 = INTEGER: 24
Along the same vein, I also do not see how to query Voltage or even Power Supply status on the 2nd Bank.
Are these queries not supported yet? Or is there another way of getting them?
--sk
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:03 AM . Last Modified: 2024-03-13 01:50 AM
Hi Stuart,
The items you're looking for are only available at the total PDU (device) level and not at the bank level. To clarify, we don't offer a bank power value (only load value in amps) and same with PDU input voltage. You've found the OIDs I mentioned which give you the power and VA at the total device level.
Also you mentioned "power supply status" .. if you're referring to the internal DC power supplies, the PDU power supply status isn't something you look at within each bank - there is only one power supply alarm state to monitor in a metered PDU and two power supplies/states in a switched rack PDU for redundancy and maintaining outlet on/off status in case of a singular power supply failure. These OIDs for monitoring the internal power supplies are under rPDU2DeviceStatusTable. AP8841 is a metered rack PDU.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:03 AM . Last Modified: 2024-03-13 01:50 AM
Hi Stuart,
The items you're looking for are only available at the total PDU (device) level and not at the bank level. To clarify, we don't offer a bank power value (only load value in amps) and same with PDU input voltage. You've found the OIDs I mentioned which give you the power and VA at the total device level.
Also you mentioned "power supply status" .. if you're referring to the internal DC power supplies, the PDU power supply status isn't something you look at within each bank - there is only one power supply alarm state to monitor in a metered PDU and two power supplies/states in a switched rack PDU for redundancy and maintaining outlet on/off status in case of a singular power supply failure. These OIDs for monitoring the internal power supplies are under rPDU2DeviceStatusTable. AP8841 is a metered rack PDU.
Link copied. Please paste this link to share this article on your social media post.