Is it possible to get the individual outlet loads on AP7922 models? Getting the bank load is pretty simple via either the Web UI or SNMP:
bq. PowerNet-MIB::rPDULoadStatusLoad.1 = Gauge32: 48 \\ PowerNet-MIB::rPDULoadStatusLoad.2 = Gauge32: 29 \\ PowerNet-MIB::rPDULoadStatusLoad.3 = Gauge32: 23
However, the PowerNet-MIB::rPDUOutletStatusLoad.* OIDs on SNMP all return zero, regardless of what load is pulled on each outlet:
bq. PowerNet-MIB::rPDUOutletStatusLoad.1 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.2 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.3 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.4 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.5 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.6 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.7 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.8 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.9 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.10 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.11 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.12 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.13 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.14 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.15 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.16 = Gauge32: 0
-z
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:20 AM . Last Modified: 2024-03-18 04:44 AM
Hello,
Individual outlet monitoring is not possible on APC's current switched rack pdu's (AP79xx). To get this functionality it would be necessary to put a clamp meter on every outlet. Currently we clamp the bank (or phase) depending on model. So it is a physical impossibility, not a MIB or firmware issue. The MIB has these OID's for future hardware development opportunities.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:19 AM . Last Modified: 2024-03-18 04:44 AM
i hear you on the PDU thing - I am not sure. it may have been carried over from another older device that supported it, i am not sure.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:19 AM . Last Modified: 2024-03-18 04:44 AM
[check this out|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=9431]
i believe it will answer your question. let me know if you need anything else 😉
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:19 AM . Last Modified: 2024-03-18 04:44 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:19 AM . Last Modified: 2024-03-18 04:44 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:19 AM . Last Modified: 2024-03-18 04:44 AM
oh, sorry. basically that shows you the information you will get. i dont believe its possible to measure the load on each particular outlet, only by bank. if you were able to, i believe it'd be an option in the web/telnet interfaces as well and it is not. i dont believe we make any single phase PDUs that do that unfortunately :-(. don't think there are any three phase ones either but i am not too familar with them.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:19 AM . Last Modified: 2024-03-18 04:44 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:19 AM . Last Modified: 2024-03-18 04:44 AM
thanks for your help anyway.
-z
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:20 AM . Last Modified: 2024-03-18 04:44 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:20 AM . Last Modified: 2024-03-18 04:44 AM
Unfortunately, APC does not make a rack PDU that measures the load for each individual outlet. Only per power strip.
Message was edited by: i picKed a winna - there was a violation of APC Forum Rules of Online Behavior - "Contains business solicitation of any type, including advertising a product or service, offering a product or service for sale, or directing readers to a location for more information about a product or service"
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:20 AM . Last Modified: 2024-03-18 04:44 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:20 AM . Last Modified: 2024-03-18 04:44 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:20 AM . Last Modified: 2024-03-18 04:44 AM
Hello,
Individual outlet monitoring is not possible on APC's current switched rack pdu's (AP79xx). To get this functionality it would be necessary to put a clamp meter on every outlet. Currently we clamp the bank (or phase) depending on model. So it is a physical impossibility, not a MIB or firmware issue. The MIB has these OID's for future hardware development opportunities.
Link copied. Please paste this link to share this article on your social media post.