Possible to chain multiple PDUs together?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Possible to chain multiple PDUs together?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:19 AM . Last Modified: ‎2024-03-18 04:45 AM

0 Likes
5
3156
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:19 AM . Last Modified: ‎2024-03-18 04:45 AM

Possible to chain multiple PDUs together?

We have 2 AP7953 PDUs, although only 1 is currently in use (the other is a "cold spare" if you like).

However, we need more sockets and it seems to make sense to use some of the 24 on the spare AP7953... The problem is that the DC only give us 1 32A commando which is used by the live AP7953.

So... is it possible for us to power the other AP7953 via one of the 16A sockets on the live one? I mean, does such an adapter exist that would convert the IEC C19 socket to an IEC 309 socket so that we can plug the other unit into it?

I appreciate that obviously we would need to be careful about the current draw on this as it would be limited to 16A (32A PDU) but really we're only talking about using 5/6 of the sockets on the 2nd PDU (probably with no more than around 1A on each).

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:19 AM . Last Modified: ‎2024-03-18 04:44 AM

0 Likes
0
3156
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:19 AM . Last Modified: ‎2024-03-18 04:44 AM

AP9899 looks like the closest we might be able to get to this (for some reason I hadn't managed to find that). I think the problem is that the PDU has a 32A commando on it though, so instead of "309-16A" it would need to be "309-32A" ... as far as I'm aware they're different sizes.

BUT I highly doubt that there's such a wire which takes a 16A input (male) to a 32A output (female) socket as in general it makes very little sense. Also the logic behind this was that we could save ourselves a few £ by using the existing hardware, but really the AP9899 seems a similar price to a basic unswitched PDU bar (i.e. with just a few sockets) so whatever sense it might've made at the time I asked the question, I guess the point is that it can be done cheaper / similar cost anyway - and in a much cleaner fashion.

That's aside from any electrical regulations which may (or not) apply.

Thanks for help/comments anyway though.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:19 AM . Last Modified: ‎2024-03-18 04:45 AM

0 Likes
0
3156
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:19 AM . Last Modified: ‎2024-03-18 04:45 AM

Doodle,

Wow, didn't see the cost of that cable when I found it! Guess its true, just dumping a basic PDU into the mix would be cleaner and just as cost effective as the other.

Glad we could at least provide some insight for you!

-Mike

Reply

Link copied. Please paste this link to share this article on your social media post.

Cap1_apc
Lt. Commander Cap1_apc
Lt. Commander

Posted: ‎2021-06-28 03:19 AM . Last Modified: ‎2024-03-18 04:45 AM

0 Likes
0
3156
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:19 AM . Last Modified: ‎2024-03-18 04:45 AM

I'd highly recommend against this.

What you are suggesting will most likely breach several electrical codes. Will it work? Maybe...

I'd also almost guarantee that the metering functionality wouldn't work as advertised. Basically, not such a good idea.

Best bet is to have an electrician properly pull you another 32amp circuit.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:19 AM . Last Modified: ‎2024-03-18 04:45 AM

0 Likes
0
3156
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:19 AM . Last Modified: ‎2024-03-18 04:45 AM

I would be surprised re. electrical codes since it is feeding a 16A supply to a 32A commando (not the other way around) so what can be against code about it? As for the metering... honestly I see no reason why it wouldn't work, as the voltage will remain as expected by the unit. Providing the current drawn stays within the limitations of the 16A socket the whole thing connects to I don't see anything unsafe or functionally crippling - but I'm willing for someone to point out the lack of understanding I have on these points...

Please don't misunderstand: I'm not simply stating that I'm right "it must obviously work" etc. as if I knew the answer I wouldn't have asked the question. However, I'm hoping for an answer backed by facts that I can digest and understand rather than just guesses (which I can make, right or wrong).

The extra 32A circuit is out of the question as the datacentre would want to charge another £x00/month for that. The alternative to the plan of chaining the PDUs would be to buy horizontal power bars, but it seems a bit silly spending £x00 on one of those when we already have a switched PDU spare? I'd like to take that option with unlimited funds, but unfortunately financial restrictions apply.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:19 AM . Last Modified: ‎2024-03-18 04:44 AM

0 Likes
0
3156
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:19 AM . Last Modified: ‎2024-03-18 04:44 AM

Doodlepop,

I too am not entirely sure whether this will work fully or not. I do agree with your reasoning, that theoretically you will be able to get output power via the outlets of the daisy chained PDU.

I have found some IEC C19/C20 to IEC 309 power cords which might assist you with this process. SKU's for those are AP9899 and AP9876.

You will have to keep in mind, not only can the second PDU not exceed the 16A capacity of the power cord used as well as the 16A capacity of the outlet bank that the second PDU is plugged into on the first PDU. This data will have to be carefully monitored by yourself to ensure none of the limits are exceeded.

With all this being said, this would not be a support means of using the rPDU's and if you have any problems, APC Support would in fact instruct you that this is not support and each PDU's requires it's own dedicated circuit. If you are going to do this, proceed with caution and knowing that this would void any warranties on the PDU's as it is an unsupported process. I would also recommend metering the outlets prior to plugging anything in to ensure nothing abnormal is happening to the power with the daisy chained connections you want to make.

Again, I don't forsee any huge problems, and am unaware of whether it would violate any local electical codes for you. I just want you to understand that APC doesn't test our products in this configuration, so we really can't vouch for how it would work or assist you in support if you encounter problems.

-Mike

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:19 AM . Last Modified: ‎2024-03-18 04:44 AM

0 Likes
0
3157
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:19 AM . Last Modified: ‎2024-03-18 04:44 AM

AP9899 looks like the closest we might be able to get to this (for some reason I hadn't managed to find that). I think the problem is that the PDU has a 32A commando on it though, so instead of "309-16A" it would need to be "309-32A" ... as far as I'm aware they're different sizes.

BUT I highly doubt that there's such a wire which takes a 16A input (male) to a 32A output (female) socket as in general it makes very little sense. Also the logic behind this was that we could save ourselves a few £ by using the existing hardware, but really the AP9899 seems a similar price to a basic unswitched PDU bar (i.e. with just a few sockets) so whatever sense it might've made at the time I asked the question, I guess the point is that it can be done cheaper / similar cost anyway - and in a much cleaner fashion.

That's aside from any electrical regulations which may (or not) apply.

Thanks for help/comments anyway though.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of