Measuring individual outlet loads on AP7922

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Measuring individual outlet loads on AP7922
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
143
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 03:19 AM . Last Modified: โ€Ž2024-03-18 04:44 AM

0 Likes
8
2024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 03:19 AM . Last Modified: โ€Ž2024-03-18 04:44 AM

Measuring individual outlet loads on AP7922

Is it possible to get the individual outlet loads on AP7922 models? Getting the bank load is pretty simple via either the Web UI or SNMP:
bq. PowerNet-MIB::rPDULoadStatusLoad.1 = Gauge32: 48 \\ PowerNet-MIB::rPDULoadStatusLoad.2 = Gauge32: 29 \\ PowerNet-MIB::rPDULoadStatusLoad.3 = Gauge32: 23
However, the PowerNet-MIB::rPDUOutletStatusLoad.* OIDs on SNMP all return zero, regardless of what load is pulled on each outlet:



bq. PowerNet-MIB::rPDUOutletStatusLoad.1 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.2 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.3 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.4 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.5 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.6 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.7 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.8 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.9 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.10 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.11 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.12 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.13 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.14 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.15 = Gauge32: 0 \\ PowerNet-MIB::rPDUOutletStatusLoad.16 = Gauge32: 0

-z

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • management
  • pdu
  • snmp
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Cap1_apc
Lt. Commander Cap1_apc
Lt. Commander

Posted: โ€Ž2021-06-28 03:20 AM . Last Modified: โ€Ž2024-03-18 04:44 AM

0 Likes
0
2024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 03:20 AM . Last Modified: โ€Ž2024-03-18 04:44 AM

Hello,

Individual outlet monitoring is not possible on APC's current switched rack pdu's (AP79xx). To get this functionality it would be necessary to put a clamp meter on every outlet. Currently we clamp the bank (or phase) depending on model. So it is a physical impossibility, not a MIB or firmware issue. The MIB has these OID's for future hardware development opportunities.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 03:19 AM . Last Modified: โ€Ž2024-03-18 04:44 AM

0 Likes
0
2024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 03:19 AM . Last Modified: โ€Ž2024-03-18 04:44 AM

i hear you on the PDU thing - I am not sure. it may have been carried over from another older device that supported it, i am not sure.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 03:19 AM . Last Modified: โ€Ž2024-03-18 04:44 AM

0 Likes
0
2024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 03:19 AM . Last Modified: โ€Ž2024-03-18 04:44 AM

[check this out|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=9431]

i believe it will answer your question. let me know if you need anything else ๐Ÿ˜‰

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 03:19 AM . Last Modified: โ€Ž2024-03-18 04:44 AM

0 Likes
0
2025
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 03:19 AM . Last Modified: โ€Ž2024-03-18 04:44 AM

i believe it will answer your question. let me know if you need anything else ๐Ÿ˜‰
Doesn't really answer the question. I know what rPDULoadStatusLoad is and what it means. What I'm trying to do is measure the load on each individual outlet, not the per-bank load. Can this even be done on an AP7922. If not, what PDU models support this?

-z

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 03:19 AM . Last Modified: โ€Ž2024-03-18 04:44 AM

0 Likes
0
2025
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 03:19 AM . Last Modified: โ€Ž2024-03-18 04:44 AM

oh, sorry. basically that shows you the information you will get. i dont believe its possible to measure the load on each particular outlet, only by bank. if you were able to, i believe it'd be an option in the web/telnet interfaces as well and it is not. i dont believe we make any single phase PDUs that do that unfortunately :-(. don't think there are any three phase ones either but i am not too familar with them.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 03:19 AM . Last Modified: โ€Ž2024-03-18 04:44 AM

0 Likes
0
2025
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 03:19 AM . Last Modified: โ€Ž2024-03-18 04:44 AM

thanks for your help anyway.

-z

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 03:20 AM . Last Modified: โ€Ž2024-03-18 04:44 AM

0 Likes
0
2024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 03:20 AM . Last Modified: โ€Ž2024-03-18 04:44 AM

Unfortunately, APC does not make a rack PDU that measures the load for each individual outlet. Only per power strip.

Message was edited by: i picKed a winna - there was a violation of APC Forum Rules of Online Behavior - "Contains business solicitation of any type, including advertising a product or service, offering a product or service for sale, or directing readers to a location for more information about a product or service"

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 03:20 AM . Last Modified: โ€Ž2024-03-18 04:44 AM

0 Likes
0
2024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 03:20 AM . Last Modified: โ€Ž2024-03-18 04:44 AM

Unfortunately, APC does not make a rack PDU that measures the load for each individual
outlet. Only per power strip.
Well, that sucks, no doubt about it. Why bother having a MIB entry for individual PDU outlet loads if none of your products actually support it?
Message was edited by: i picKed a winna - there was a violation of APC Forum
Rules of Online Behavior - "Contains business solicitation of any type, including
advertising a product or service, offering a product or service for sale, or directing
readers to a location for more information about a product or service"


-z

Reply

Link copied. Please paste this link to share this article on your social media post.

Cap1_apc
Lt. Commander Cap1_apc
Lt. Commander

Posted: โ€Ž2021-06-28 03:20 AM . Last Modified: โ€Ž2024-03-18 04:44 AM

0 Likes
0
2025
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 03:20 AM . Last Modified: โ€Ž2024-03-18 04:44 AM

Hello,

Individual outlet monitoring is not possible on APC's current switched rack pdu's (AP79xx). To get this functionality it would be necessary to put a clamp meter on every outlet. Currently we clamp the bank (or phase) depending on model. So it is a physical impossibility, not a MIB or firmware issue. The MIB has these OID's for future hardware development opportunities.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore