Posted: 2021-07-01 01:05 AM . Last Modified: 2024-03-06 02:09 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 01:05 AM . Last Modified: 2024-03-06 02:09 AM
Hi,
have some questions about both cards AP9630/9631.
If I buy a AP9631 is there a Temperatur sensor within the Kit?
I want to put this sensor into the rack
Can I read the temperature values via the Management Software PCNS?
Can I set thresholds via PCNS to send an eMail and/or an SNMP-Trap?
With the old AP9617 I had the problem if sending SMTP-Mails out I can put in Username/Password for the
SMTP-Server. Do the new Cards 9630/9631 have the possibility to configure Username/Password for sending out SMTP-Mails?
Regards, Hans
Message was edited by: Magnussen
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 01:05 AM . Last Modified: 2024-03-06 02:09 AM
I have 5.1.7 installed on AP9631 and I'm not seeing the SSL \ TLS options. Is there any new information regarding this feature? Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 01:05 AM . Last Modified: 2024-03-06 02:09 AM
hello Hans:
If I buy a AP9631 is there a Temperatur sensor within the Kit? - yes, AP9335T temp only probe is included, AP9335TH temp/humidity probe is optional
I want to put this sensor into the rack
Can I read the temperature values via the Management Software PCNS? - PCNS can act upon a temperature alarm from the NMC when it is "out of range" - so it cannot read specific temperatures unfortunately just when there is any violation.
Can I set thresholds via PCNS to send an eMail and/or an SNMP-Trap? - you set the thresholds on the AP9631 itself, not PCNS. you can do email, syslog, or SNMP notifications for temperature alarms.
With the old AP9617 I had the problem if sending SMTP-Mails out I can put in Username/Password for the SMTP-Server. Do the new Cards 9630/9631 have the possibility to configure Username/Password for sending out SMTP-Mails? yes, the newer cards support basic SMTP authentication currently - meaning plain text. we will be supporting SSL/TLS in the future.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 01:05 AM . Last Modified: 2024-03-06 02:09 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 01:05 AM . Last Modified: 2024-03-06 02:09 AM
Thanks for the answer! Thats good news.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 01:05 AM . Last Modified: 2024-03-06 02:09 AM
Hi Kurt
We anticipate v6.0.6 next week for sumx and sy apps. This will contain support for authenticated SMTP using SSL/TLS. v5.1.X doesn't support this.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 01:05 AM . Last Modified: 2024-03-06 02:09 AM
I have 5.1.7 installed on AP9631 and I'm not seeing the SSL \ TLS options. Is there any new information regarding this feature? Thanks