Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

MIBS for an APC 10000 RT needed.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • MIBS for an APC 10000 RT needed.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:27 PM . Last Modified: ‎2024-03-14 04:30 AM

0 Likes
5
2801
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:27 PM . Last Modified: ‎2024-03-14 04:30 AM

MIBS for an APC 10000 RT needed.

I just installed an APC 10000 RT under an Intel Modular Server (6 computete modules, "SAN") that has NO SERIAL PORTS!
I am running CLI mode Linux (No gui) and would like to use SNMP to monitor the UPS status and perform shutdowns, etc..

I've configured both SNMP V1 and V3 on the APC Web/SNMP Management Card (MB:v3.8.6 PF:v3.5.5 PN:apc_hw02_aos_355.bin AF1:v3.5.5 AN1:apc_hw02_sumx_355.bin...

But it does not seem to have a MIB for battery status and such as others do. For example, when I run "snmpwalk" I get a full set of MIBS, but not anything I (or snmp-ups using apcc) can recognize as the battery status, etc..

I'm not a hard core APC fan, and I am very confused by the amount of variants of APC UPS's and their variations of SNMP MIBS. and am going nuts trying to figure out how to communicate with this unit.

Does anyone know which MIBS are what or where I can get the right definition file?

Oh, side note: It's installed in S. America, I am now in the USA. I can access it via VPN and Telnet, barely, not enough bandwidth for a web session.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:27 PM . Last Modified: ‎2024-03-14 04:30 AM

0 Likes
0
2800
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:27 PM . Last Modified: ‎2024-03-14 04:30 AM

Side note: The powerchute software requires Java/JRE. - Which is what keeps me from using it.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 10:27 PM . Last Modified: ‎2024-03-14 04:30 AM

0 Likes
0
2800
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:27 PM . Last Modified: ‎2024-03-14 04:30 AM

You only need the PowerNet MIB for all APC branded products. Here's the latest version:

[PowerNet MIB 3.9.5|http://www.apcc.com/tools/download/software_comp.cfm?sw_sku=SFPMIB395]

For the basic battery status, you might try:

snmpget -c public -v 1 IP_GOES_HERE .1.3.6.1.4.1.318.1.1.1.2.1.1.0

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:27 PM . Last Modified: ‎2024-03-14 04:30 AM

0 Likes
0
2800
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:27 PM . Last Modified: ‎2024-03-14 04:30 AM

Thats nice, got the MIB, any clues on what to do with it? When I run that command, I get a value of "2".

And no, I'm not normally a sysadmin/network admin doing this kind of thing, but for this special case, I am relearning.
And yes, I'll be figuring this out today as I relearn things I forgot on purpose 10 years ago.

Note to all the sales-droids that e-mailed me from my post: If you aren't able to answer the questions, don't offer to sell me product.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 10:27 PM . Last Modified: ‎2024-03-14 04:30 AM

0 Likes
0
2800
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:27 PM . Last Modified: ‎2024-03-14 04:30 AM

>
Thats nice, got the MIB, any clues on what to do with it? When I run that command, I get a value of "2".
>

For that OID, "2" is batteryNormal. [This web page|http://www.karlkatzke.com/using-snmpwalk-and-a-vendor-mib-file/] seems to describe how to install and use the MIB on linux-type systems so you can get more descriptive names. I used the GetIF utility in windows to browse the MIB and give you the OID for basic battery status.

There is open source software on the internet for driving shutdowns using SNMP monitoring, however the APC solution is to use the free PowerChute Network Shutdown which works with your network management card to perform a safe shutdown of your computers. You can download it [from here|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SFPCNS223].

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:27 PM . Last Modified: ‎2024-03-14 04:30 AM

0 Likes
0
2800
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:27 PM . Last Modified: ‎2024-03-14 04:30 AM

Excellent kickstart for an old geek to get caught up, thank you!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:27 PM . Last Modified: ‎2024-03-14 04:30 AM

0 Likes
0
2801
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:27 PM . Last Modified: ‎2024-03-14 04:30 AM

Side note: The powerchute software requires Java/JRE. - Which is what keeps me from using it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore