MGE Galaxy 3500 - Dry Contact I/O Card?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • MGE Galaxy 3500 - Dry Contact I/O Card?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-13 04:13 AM

0 Likes
5
1132
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-13 04:13 AM

MGE Galaxy 3500 - Dry Contact I/O Card?

Hi, I have UPS - MGE Galaxy 3500,

which Dry Contact I/O  Card can be installed in the UPS?

possible to use a AP9613 (Dry Contact I/O SmartSlot Card)? 

Do you need to order an additional AP9600 (SMARTSLOT EXPANSION CHASSIS)?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • 3500
  • AP9600
  • ap9613
  • galaxy
  • mge
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-13 04:12 AM

0 Likes
0
1131
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-13 04:12 AM

You'll go with the DB-9 port on the left, closest to where you have the AP9631 installed now.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-13 04:13 AM

0 Likes
0
1131
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-13 04:13 AM

Hi,

Yes, for dry contacts on the MGE Galaxy 3500 UPS, you can do one of two main options depending on how many inputs/outputs you require.

Option 1: Use included AP9631 Network Management Card with AP9810 Dry Contact I/O accessory. AP9631 can support up to (2) total AP9810 accessories. Each AP9810 gives (2) input contacts and (1) output relay.

Option 2: Use AP9613 card which has (4) inputs and (6) outputs. You can keep the AP9631 Network Management Card installed and use AP9600 and install AP9613 into the AP9600 or if you do not need the AP9631 Network Management Card, put it aside and install AP9613 dry contact card directly into the UPS. You only need the AP9600 expansion chassis if you want to use both AP9631 (pre-installed in the UPS) and AP9613.

Hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-13 04:13 AM

0 Likes
0
1131
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-13 04:13 AM

thanks for the answer,
but how to connect AP9600 expansion chassis, in which port?

and how to configure relay output?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-13 04:13 AM

0 Likes
0
1131
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-13 04:13 AM

So you're going to go with AP9613 option?

You'll connect the AP9600 to the left or top serial port. I see mixed information that tells me: "Use the computer interface / smart slot serial, g3500 - left port SUVT - top port G3500" So, SUVT and MGE 3500 are very similar but it sounds like on one, the ports are top/bottom and on the other, left/right. If you have top bottom, go with the top port.

Configuring the relay can be done with dipswitches or if you want to customize, though a USB connection to the AP9613.

Some good resources are: http://www.schneider-electric.us/en/faqs/FA175043 (available events in AP9613) and the user's guide that talks about dipswitches or using custom configurations: http://www.apc.com/shop/us/en/products/Dry-Contact-I-O-SmartSlot-Card/P-AP9613 

Hope that helps!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-13 04:13 AM

0 Likes
0
1131
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-13 04:13 AM

So you're going to go with AP9613 option?

Yes, we want to use this method.

left or top serial port

???

but we have two serial ports in one line
left or right to which need to connect

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-13 04:12 AM

0 Likes
0
1132
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:32 AM . Last Modified: ‎2024-03-13 04:12 AM

You'll go with the DB-9 port on the left, closest to where you have the AP9631 installed now.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of