MGE Comet 80kVA - Internal Comms Failure
Hello,
UPS fail suddenly at midnight, obviously, all loads dropped
we checked all the fuses, are fine
we execute BACK TO NORMAL procedures in the manual and always keeps the fault:
INTERNAL COMMS FAULT
electronic boards shows no damage or burns
UPS is now in Bypass
please help to how accurately detect the problem and where to get spare parts ???
MODEL: 72-160802-42 80kVA 480-20
SERIAL: B01-10012 01/34
Thank you