Looking for input on Server shutdown configuration

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Looking for input on Server shutdown configuration
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:50 AM . Last Modified: ‎2024-03-07 10:40 PM

0 Likes
2
815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:50 AM . Last Modified: ‎2024-03-07 10:40 PM

Looking for input on Server shutdown configuration

Hello all

Thank you for taking time to read this. Here is my situtation. I have I enterprise class Mitsubishi UPS protecting my entire server room. The UPS itself is perfectly adequate and well maintained. The issue I am having is Mitsubishi's UPS to server communication is sorely lacking. What I would like to do is buy he simplest/smallest APC I can and use APC's software to signal the servers to shut down in a power event.

What model of UPS would fit the bill and which of the network software would you recommend?

Thank you in advance

Caleb

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:50 AM . Last Modified: ‎2024-03-07 10:40 PM

0 Likes
0
815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:50 AM . Last Modified: ‎2024-03-07 10:40 PM

hi caleb,

i see only one issue with what you want to do, you are most likely going to run into a difference with runtime between two UPSs. your larger UPS may have more or less runtime than the APC UPS that you wish to buy and it is possible that you'd want to let your equipment as long as it can go at which point, the APC UPS may have already turned off. most likely, if you put little or no load on the APC UPS, it can out run your larger UPS but I am not sure. this is something you will need to figure out. assuming you do, i hope the below solution is what you are looking for even though its not necessarily something the APC would recommend.

assuming you arent going to plug anything in for power to the UPS that you plan on buying from APC as noted above, I personally suggest possibly getting the smallest UPS with a Smart Slot so you can buy a network management card to put inside of it. the UPS should be able to monitor the power and act just as with your larger UPS (when it goes to battery because of a power outage but as noted above, may go to battery at different times depending on what it considers a power problem) to see when the power goes out and thus via the network, communicate with the powerchute network shutdown software to shut your servers down gracefully or send emails, etc.

This would be the SUA750 in conjunction with an AP9617.

[see SUA750 here|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SUA750]

[see AP9617 here|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP9617]

alternatively you could get an AP9619 card if you wanted environmental monitoring with it and dry contacts or an AP9618 if you require those features of the AP9619 plus out of band management.

now for the powerchute software. you would need powerchute network shutdown. you install this on the servers you want to gracefully shutdown and then give input the IP of the network management card on each client. the management card can send information over the network and based on certain events you choose on each of the certain servers, can shut down the operating system, notify users (via windows messenger service) or run command files.

[here is a link to the supported operating systems for powerchute network shutdown|http://www.apcmedia.com/salestools/SJHN-7AYQNP_R2_EN.pdf]

hope this helps!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 07:50 AM . Last Modified: ‎2024-03-07 10:40 PM

0 Likes
0
815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:50 AM . Last Modified: ‎2024-03-07 10:40 PM

I'd be a little concerned about the UPSes disagreeing on the definition of a "power event." For instance, UPSes often have "boost and trim" which adjusts the line voltage during slight over and undervoltage conditions. So when the line sags, one UPS may boost the voltage up while the other considers the line bad and goes to battery.

Another issue is how to turn the computers back on. PowerChute Network Shutdown can be set up to have the last computer that is shutting down tell the APC UPS to turn off. That turns off power to the computers. Then when the line comes back, the computers set up to turn on when power is restored will turn back on. This approach won't work if the computers are really being powered by a different UPS. I would investigate whether your Mitsubishi UPS can be set up to always turn power off and back on during after a power failure to force any shutdown computer back on.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:50 AM . Last Modified: ‎2024-03-07 10:40 PM

0 Likes
0
816
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:50 AM . Last Modified: ‎2024-03-07 10:40 PM

hi caleb,

i see only one issue with what you want to do, you are most likely going to run into a difference with runtime between two UPSs. your larger UPS may have more or less runtime than the APC UPS that you wish to buy and it is possible that you'd want to let your equipment as long as it can go at which point, the APC UPS may have already turned off. most likely, if you put little or no load on the APC UPS, it can out run your larger UPS but I am not sure. this is something you will need to figure out. assuming you do, i hope the below solution is what you are looking for even though its not necessarily something the APC would recommend.

assuming you arent going to plug anything in for power to the UPS that you plan on buying from APC as noted above, I personally suggest possibly getting the smallest UPS with a Smart Slot so you can buy a network management card to put inside of it. the UPS should be able to monitor the power and act just as with your larger UPS (when it goes to battery because of a power outage but as noted above, may go to battery at different times depending on what it considers a power problem) to see when the power goes out and thus via the network, communicate with the powerchute network shutdown software to shut your servers down gracefully or send emails, etc.

This would be the SUA750 in conjunction with an AP9617.

[see SUA750 here|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SUA750]

[see AP9617 here|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP9617]

alternatively you could get an AP9619 card if you wanted environmental monitoring with it and dry contacts or an AP9618 if you require those features of the AP9619 plus out of band management.

now for the powerchute software. you would need powerchute network shutdown. you install this on the servers you want to gracefully shutdown and then give input the IP of the network management card on each client. the management card can send information over the network and based on certain events you choose on each of the certain servers, can shut down the operating system, notify users (via windows messenger service) or run command files.

[here is a link to the supported operating systems for powerchute network shutdown|http://www.apcmedia.com/salestools/SJHN-7AYQNP_R2_EN.pdf]

hope this helps!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of