Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Load Shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Load Shutdown
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Anonymous user
Not applicable

Posted: ‎2021-06-26 02:29 AM . Last Modified: ‎2024-03-19 01:55 AM

0 Likes
0
874
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:29 AM . Last Modified: ‎2024-03-19 01:55 AM

Load Shutdown

 

We have a 2 Symmentra 40K, a few days ago we had a quickly power outage and both UPS disconnect the load and didnt come up until we put to bypass manualy and then to online.

Thats the events

0100A11E IM    A TIM running                             16/08/25 20:36:41 922
0100D11E IM    D TIM running                             16/08/25 20:36:41 922
0A00A07E USER  A UPS transferred to inverter             16/08/25 15:20:22 980
0900A05E IM    A IM oper. mode: Shift to ON LINE         16/08/25 15:20:22 976
0100D13E IM    D TIM has SSW on                          16/08/25 15:20:22 976
0100A12E IM    A TIM has Inverter on                     16/08/25 15:20:22 976
0203D24E PM 03 D Output RMS voltage fail                 16/08/25 15:19:59 134
0203D23E PM 03 D Inverter RMS voltage fail               16/08/25 15:19:59 134
0500A32E SSW   A Backfeed Contactor closed               16/08/25 15:19:59 078
0205D24E PM 05 D Output RMS voltage fail                 16/08/25 15:19:58 982
0205D23E PM 05 D Inverter RMS voltage fail               16/08/25 15:19:58 982
0100D04E IM    D Output voltage error                    16/08/25 15:19:58 947
0204D24E PM 04 D Output RMS voltage fail                 16/08/25 15:19:58 938
0204D23E PM 04 D Inverter RMS voltage fail               16/08/25 15:19:58 938
0600D06F EXSG  D Operate Q002 ok                         16/08/25 15:19:58 865
0A00A06E USER  A UPS transferred to bypass               16/08/25 15:19:58 783
0900A08E IM    A IM oper. mode: Shift to REQUEST. BYPASS 16/08/25 15:19:58 779
0100A13E IM    A TIM has SSW on                          16/08/25 15:19:58 779
0205A07E PM 05 A CHG oper. mode: Shift to HIGH           16/08/25 15:13:51 741
0204A07E PM 04 A CHG oper. mode: Shift to HIGH           16/08/25 15:13:51 251
0203A07E PM 03 A CHG oper. mode: Shift to HIGH           16/08/25 15:13:50 758
0205A04E PM 05 A PFC oper. mode: Shift to MAINS          16/08/25 15:13:35 443
0204A04E PM 04 A PFC oper. mode: Shift to MAINS          16/08/25 15:13:34 974
0203A04E PM 03 A PFC oper. mode: Shift to MAINS          16/08/25 15:13:34 509
0100D57E IM    D Inverter sync. error                    16/08/25 15:13:30 652
0205D20E PM 05 D Mains synch fail                        16/08/25 15:13:28 786
0204D20E PM 04 D Mains synch fail                        16/08/25 15:13:28 747
0203D20E PM 03 D Mains synch fail                        16/08/25 15:13:28 707
0205D16E PM 05 D Mains RMS voltage fail                  16/08/25 15:13:27 708
0204D16E PM 04 D Mains RMS voltage fail                  16/08/25 15:13:27 669
0100D02E IM    D Bypass voltage error                    16/08/25 15:13:27 645
0203D16E PM 03 D Mains RMS voltage fail                  16/08/25 15:13:27 630
0100D01E IM    D Mains voltage error                     16/08/25 15:13:27 552
0100D06E IM    D PLL disabled due to bypass RMS error    16/08/25 15:13:27 528
0205A20E PM 05 A Mains synch fail                        16/08/25 15:13:27 285
0203A24E PM 03 A Output RMS voltage fail                 16/08/25 15:13:27 204
0203A23E PM 03 A Inverter RMS voltage fail               16/08/25 15:13:27 204
0203A20E PM 03 A Mains synch fail                        16/08/25 15:13:27 200
0600A06F EXSG  A Operate Q002 ok                         16/08/25 15:13:27 174
0900A02E IM    A IM oper. mode: Shift to LOAD DISCONNECT 16/08/25 15:13:27 153
0100D13E IM    D TIM has SSW on                          16/08/25 15:13:27 153
0500D32E SSW   D Backfeed Contactor closed               16/08/25 15:13:27 149
0205A05E PM 05 A CHG oper. mode: Shift to OFF            16/08/25 15:13:27 060
0205A03E PM 05 A PFC oper. mode: Shift to BATTERY        16/08/25 15:13:27 060
0205A24E PM 05 A Output RMS voltage fail                 16/08/25 15:13:27 056
0205A23E PM 05 A Inverter RMS voltage fail               16/08/25 15:13:27 056
0205A16E PM 05 A Mains RMS voltage fail                  16/08/25 15:13:27 051
0204A05E PM 04 A CHG oper. mode: Shift to OFF            16/08/25 15:13:27 017
0204A03E PM 04 A PFC oper. mode: Shift to BATTERY        16/08/25 15:13:27 017
0204A24E PM 04 A Output RMS voltage fail                 16/08/25 15:13:27 013
0204A23E PM 04 A Inverter RMS voltage fail               16/08/25 15:13:27 013
0100A06E IM    A PLL disabled due to bypass RMS error    16/08/25 15:13:27 013
0204A20E PM 04 A Mains synch fail                        16/08/25 15:13:27 009
0204A16E PM 04 A Mains RMS voltage fail                  16/08/25 15:13:27 009
0203A05E PM 03 A CHG oper. mode: Shift to OFF            16/08/25 15:13:26 977
0203A03E PM 03 A PFC oper. mode: Shift to BATTERY        16/08/25 15:13:26 977
0203A16E PM 03 A Mains RMS voltage fail                  16/08/25 15:13:26 968
0100A01E IM    A Mains voltage error                     16/08/25 15:13:26 951
0900A07E IM    A IM oper. mode: Shift to TEMP BYPASS     16/08/25 15:13:26 930
0100A13E IM    A TIM has SSW on                          16/08/25 15:13:26 930
0100D12E IM    D TIM has Inverter on                     16/08/25 15:13:26 930
0100A04E IM    A Output voltage error                    16/08/25 15:13:26 930

0100A02E IM    A Bypass voltage error                    16/08/25 15:13:26 831
0100A57E IM    A Inverter sync. error                    16/08/25 15:13:26 808
0100D02E IM    D Bypass voltage error                    16/08/25 15:13:26 808
0100A02E IM    A Bypass voltage error                    16/08/25 15:13:26 794

Attachments
Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
  • Tags:
  • bypass
  • load
  • shutdown
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore