LED on left side of UPS blinking

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • LED on left side of UPS blinking
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 02:18 AM . Last Modified: β€Ž2024-03-18 11:23 PM

0 Likes
6
1615
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:18 AM . Last Modified: β€Ž2024-03-18 11:23 PM

LED on left side of UPS blinking

Hi,

I have just bought a used unit and was going to do manual new battery calibration. 30.5% load

Of corse i bought 2 new battery packs πŸ˜‰

the unit is a SUA3000, everything was looking fine and i added equipment (lights fans,...) to reach the 30% load. I noted all the specs like temp 22C, runtime 47min,...

than i flicked the bracker in my electric panel and i hear the UPS went on battery with some kind of heavy humming noise for about 5 seconds and than all the LED to the left started blinking. I tried to restart the unit with the following outcome:

unit will turn on and on line LED will blick for few seconds

than it will go on battery with a havy humming noise for a second

than all the LED to the left will blink (5*load, 1*AVR trim, 1* On Line, 1*AVR Boost)

now it seams i even cant get back in to the networkcard to see the logs and so, no current on outlets. is it dead?

Best

Andy

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • blinking
  • dead
  • humming
  • led
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 02:19 AM . Last Modified: β€Ž2024-03-18 11:23 PM

0 Likes
0
1614
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:19 AM . Last Modified: β€Ž2024-03-18 11:23 PM

Hi,

The description provided indicates a DC imbalance. You wrote that you had replaced the batteries. If you are using none APC batteries you should verify the batteries are wired correctly. Wiring incorrectly could cause a DC imbalance. If they are wired properly and the reset does not resolve the issue then the issue is most likely a component failure and the unit will need to be replaced.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 02:18 AM . Last Modified: β€Ž2024-03-18 11:23 PM

0 Likes
0
1614
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:18 AM . Last Modified: β€Ž2024-03-18 11:23 PM

Hi,

Reset / bran dead the unit to see if it will come back on line.

Instruction on how to brain dead the UPS can be found in Kbase FA156611

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 02:18 AM . Last Modified: β€Ž2024-03-18 11:23 PM

0 Likes
0
1614
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:18 AM . Last Modified: β€Ž2024-03-18 11:23 PM

Hi Bill,

Thanks for the quick awnser:)

Ok i have tried both solution i can see in the FA, but still the same outcome 😞

  • I made sure no load
  • braker to off in my electic panel (unit is hardwired)
  • hold I button till long beep (2 sec) and release
  • it tries to do selftest or so 
  • back on to the blinking LED

for the second test

  • no load
  • braker off
  • hold O button till click
  • braker ON
  • I button and unit turns on with selftest
  • back to blinking lights

Crap, is there anything else you can point me to? 

I did see some post where they will conect via serial cable and thgis way the get access and do some changes to the battery constant.

Thanks so much

Andy

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 02:19 AM . Last Modified: β€Ž2024-03-18 11:23 PM

0 Likes
0
1615
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:19 AM . Last Modified: β€Ž2024-03-18 11:23 PM

Hi,

The description provided indicates a DC imbalance. You wrote that you had replaced the batteries. If you are using none APC batteries you should verify the batteries are wired correctly. Wiring incorrectly could cause a DC imbalance. If they are wired properly and the reset does not resolve the issue then the issue is most likely a component failure and the unit will need to be replaced.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 02:19 AM . Last Modified: β€Ž2024-03-18 11:23 PM

0 Likes
0
1614
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:19 AM . Last Modified: β€Ž2024-03-18 11:23 PM

Hi,

Batteries been bought by local supplier sine I needed them quick so I can get the unit up and running. 

The voltage of the bats are 27. On each pack. They are brand new and wiring should be ok. 

Fuesed 100amp see picture below 

So u say it needs to be replaced ?  Can it be repaierd?  What would be wrong with it?

whats the closest APC authorized repair shop for me?

I live in 

Cookshire QC Canada

J0B 1M0

thanks

VsQQl7y1r64N1e0rjYfioQ%3D%3D.jpegVsQQl7y1r64N1e0rjYfioQ%3D%3D.jpeg

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 02:19 AM . Last Modified: β€Ž2024-03-18 11:23 PM

0 Likes
0
1614
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:19 AM . Last Modified: β€Ž2024-03-18 11:23 PM

Hi,

Sorry but I am not aware of a company in Canada that does UPS repairs but maybe another forum member is.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 02:19 AM . Last Modified: β€Ž2024-03-18 11:22 PM

0 Likes
0
1614
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 02:19 AM . Last Modified: β€Ž2024-03-18 11:22 PM

OK 😞

Thanks a lot for your help Bill

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of