Hi,
I have just bought a used unit and was going to do manual new battery calibration. 30.5% load
Of corse i bought 2 new battery packs π
the unit is a SUA3000, everything was looking fine and i added equipment (lights fans,...) to reach the 30% load. I noted all the specs like temp 22C, runtime 47min,...
than i flicked the bracker in my electric panel and i hear the UPS went on battery with some kind of heavy humming noise for about 5 seconds and than all the LED to the left started blinking. I tried to restart the unit with the following outcome:
unit will turn on and on line LED will blick for few seconds
than it will go on battery with a havy humming noise for a second
than all the LED to the left will blink (5*load, 1*AVR trim, 1* On Line, 1*AVR Boost)
now it seams i even cant get back in to the networkcard to see the logs and so, no current on outlets. is it dead?
Best
Andy
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-28 02:19 AM . Last Modified: β2024-03-18 11:23 PM
Hi,
The description provided indicates a DC imbalance. You wrote that you had replaced the batteries. If you are using none APC batteries you should verify the batteries are wired correctly. Wiring incorrectly could cause a DC imbalance. If they are wired properly and the reset does not resolve the issue then the issue is most likely a component failure and the unit will need to be replaced.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-28 02:18 AM . Last Modified: β2024-03-18 11:23 PM
Hi,
Reset / bran dead the unit to see if it will come back on line.
Instruction on how to brain dead the UPS can be found in Kbase FA156611
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-28 02:18 AM . Last Modified: β2024-03-18 11:23 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-28 02:18 AM . Last Modified: β2024-03-18 11:23 PM
Hi Bill,
Thanks for the quick awnser:)
Ok i have tried both solution i can see in the FA, but still the same outcome π
for the second test
Crap, is there anything else you can point me to?
I did see some post where they will conect via serial cable and thgis way the get access and do some changes to the battery constant.
Thanks so much
Andy
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-28 02:19 AM . Last Modified: β2024-03-18 11:23 PM
Hi,
The description provided indicates a DC imbalance. You wrote that you had replaced the batteries. If you are using none APC batteries you should verify the batteries are wired correctly. Wiring incorrectly could cause a DC imbalance. If they are wired properly and the reset does not resolve the issue then the issue is most likely a component failure and the unit will need to be replaced.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-28 02:19 AM . Last Modified: β2024-03-18 11:23 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-28 02:19 AM . Last Modified: β2024-03-18 11:23 PM
Hi,
Batteries been bought by local supplier sine I needed them quick so I can get the unit up and running.
The voltage of the bats are 27. On each pack. They are brand new and wiring should be ok.
Fuesed 100amp see picture below
So u say it needs to be replaced ? Can it be repaierd? What would be wrong with it?
whats the closest APC authorized repair shop for me?
I live in
Cookshire QC Canada
J0B 1M0
thanks
VsQQl7y1r64N1e0rjYfioQ%3D%3D.jpeg
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-28 02:19 AM . Last Modified: β2024-03-18 11:23 PM
Hi,
Sorry but I am not aware of a company in Canada that does UPS repairs but maybe another forum member is.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-28 02:19 AM . Last Modified: β2024-03-18 11:22 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-28 02:19 AM . Last Modified: β2024-03-18 11:22 PM
OK π
Thanks a lot for your help Bill