KVM IP Solutions Questions

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • KVM IP Solutions Questions
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:46 AM . Last Modified: ‎2024-02-14 10:46 PM

0 Likes
5
1959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:46 AM . Last Modified: ‎2024-02-14 10:46 PM

KVM IP Solutions Questions

I searched these forums for KVM info, but I didn't find any topics related to it.

I looked at the APC KVM units that are available on the APC website at
http://www.apc.com/products/family/index.cfm?id=319

I'm looking for a KVM IP device that provides remote access where I would either A). install software or go to the B). web interface by using my browser from a computer (from a different location from where the KVM device is).

Here's what I need. I device that will connect to 15 servers (or thereabouts). And users can login with their username/password to connect to their own server. I want to have 15 username/password users, 15 servers it is connected to, and all 15 of those users be able to connect concurrently (all at the same time).

But from what I've seen, KVM devices only usually support 2 to 4 concurrent users at one time. But they do allow 15 user/pass accounts and be connected to 15 servers. I'm not sure about APC though.

I also have no need for a local console. Since all I am needing are remote KVM (by web browser or software on a user computer).

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:47 AM . Last Modified: ‎2024-02-14 10:46 PM

0 Likes
0
1959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:47 AM . Last Modified: ‎2024-02-14 10:46 PM

I searched these forums for KVM info, but I didn't find any topics related to it.

I looked at the APC KVM units that are available on the APC website at
http://www.apc.com/products/family/index.cfm?id=319

I'm looking for a KVM IP device that provides remote access where I would either A). install software or go to the B). web interface by using my browser from a computer (from a different location from where the KVM device is).

Here's what I need. I device that will connect to 15 servers (or thereabouts). And users can login with their username/password to connect to their own server. I want to have 15 username/password users, 15 servers it is connected to, and all 15 of those users be able to connect concurrently (all at the same time).

But from what I've seen, KVM devices only usually support 2 to 4 concurrent users at one time. But they do allow 15 user/pass accounts and be connected to 15 servers. I'm not sure about APC though.

I also have no need for a local console. Since all I am needing are remote KVM (by web browser or software on a user computer).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:47 AM . Last Modified: ‎2024-02-14 10:46 PM

0 Likes
0
1959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:47 AM . Last Modified: ‎2024-02-14 10:46 PM

Hello,

The AP5405 provides web access to your KVM and allows you to connect to servers over IP.

Here are the number of concurrent users:

2 Analog + 4 RDP (In-Band)
or:
1 Analog + 1 IP + 4 RDP
or:
2 IP + 4 RDP

You can either set the 15 users' username/passwords on the KVM itself, or you can set the KVM for RADIUS, LDAP, or any other of the supported authentication protocols.

The APC IP KVM's can also be daisychained if you ever add more servers (you can still access all servers from one IP). You can also connect the Switched Rack PDU's (AP79xx only) to the IP KVMs via the AP9317 cable and have the ability to reboot PDU outlets, through the KVM.

Hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:47 AM . Last Modified: ‎2024-02-14 10:46 PM

0 Likes
0
1958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:47 AM . Last Modified: ‎2024-02-14 10:46 PM

Please explain more about what is meant by these terms given below such as "analog" and "RDP" and "In-Band". Thanks.

2 Analog + 4 RDP (In-Band)
1 Analog + 1 IP + 4 RDP
2 IP + 4 RDP

Also, will analog KVM devices such as the
AP5401
AP5202
AP5206
AP5456
work also for what I am wanting (IP KVM)?

What is the real differences between analog KVM and digital KVM?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:47 AM . Last Modified: ‎2024-02-14 10:46 PM

0 Likes
0
1959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:47 AM . Last Modified: ‎2024-02-14 10:46 PM

Analog would be a local user , someone who connects to the KVM through the local osd, not the web interface. IP users are users who connect to the KVM over IP (web browser) and then connect to the servers direct. RDP is a user who connects to the KVM over IP, and then connect to the servers through an RDP connection.

Also, will analog KVM devices such as the
AP5401 web access to the KVM but no connection to the servers
AP5202 analog only, no ip
AP5206 web access, this sku is basically an ap5202 plus ap5456
AP5456 this product is an add on, you connect this to an analog kvm to make it accessible over IP
work also for what I am wanting (IP KVM)?

What is the real differences between analog KVM and digital KVM? Difference is analog is local access through a local keyboard/monitor/mouse, digital is the kvm is accessible over IP, as well as the servers that are connected to the KVM

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:47 AM . Last Modified: ‎2024-02-14 10:46 PM

0 Likes
0
1959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:47 AM . Last Modified: ‎2024-02-14 10:46 PM

I am looking at putting my PC in one room, and my monitor (1920x1200), Keyboard, Mouse, Speakers, (maybe USB 2.0) in another room.

I have 3 cat5e cables from my back room to PC monitor location.

Most of the KVM switches I see do a local PC and a remote PC. I do not need it to do a local PC location, just the above mentioned connections to 1 monitor location

Any suggestions?

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:47 AM . Last Modified: ‎2024-02-14 10:46 PM

0 Likes
0
1960
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:47 AM . Last Modified: ‎2024-02-14 10:46 PM

I searched these forums for KVM info, but I didn't find any topics related to it.

I looked at the APC KVM units that are available on the APC website at
http://www.apc.com/products/family/index.cfm?id=319

I'm looking for a KVM IP device that provides remote access where I would either A). install software or go to the B). web interface by using my browser from a computer (from a different location from where the KVM device is).

Here's what I need. I device that will connect to 15 servers (or thereabouts). And users can login with their username/password to connect to their own server. I want to have 15 username/password users, 15 servers it is connected to, and all 15 of those users be able to connect concurrently (all at the same time).

But from what I've seen, KVM devices only usually support 2 to 4 concurrent users at one time. But they do allow 15 user/pass accounts and be connected to 15 servers. I'm not sure about APC though.

I also have no need for a local console. Since all I am needing are remote KVM (by web browser or software on a user computer).

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore