I bought a new RBC7 battery replacement (17Ah, 24V) pack for a Smart-UPS SMT1500I (1500AV, 1050W) with a AP9631 Network Management Card 2. The NMC2 allows me to collect and plot data provided by the UPS.
So I ran tests: the load is a laptop charger and a traditional light bulb and the powerstrip with power monitor says together they peak at 150W.
1) disconnect the input power from the UPS (see attached picture SMT1500i-RBC7-batt)
2) built-in calibration test (see attached picture SMT1500i-RBC7-cal)
Both diagrams clearly show a 20% battery charge drop right when the UPS switches to battery output. After that drop the battery charge decreases linearly.
Is this normal behaviour of a new and freshly charged RBC7 model battery? If that is normal how is the initial charge drop explained?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:31 AM . Last Modified: 2024-03-15 05:35 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:31 AM . Last Modified: 2024-03-15 05:35 AM
The battery charge reported by the UPS actually dropped as follows:
in test (1): 20%
in test (2): 40%
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:31 AM . Last Modified: 2024-03-15 05:35 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:31 AM . Last Modified: 2024-03-15 05:35 AM
The battery charge reported by the UPS actually dropped as follows:
in test (1): 20%
in test (2): 40%
Link copied. Please paste this link to share this article on your social media post.