Is something wrong with my UPS Calibration or with PowerChute software?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Is something wrong with my UPS Calibration or with PowerChute software?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-14 03:57 AM

0 Likes
8
1444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-14 03:57 AM

Is something wrong with my UPS Calibration or with PowerChute software?

Hi,

Last friday I've done a calibration of a brand new SUA750XL with one SUA24XLBP attached. I used a 150 watts lamp as the only load and unplugged the UPS from the wall. The power from the batteries lasted for 8 hours 34 minutes. That's a bit longer than what can be estimated from the APC website.

Now, with the normal load attached (one 24 ports switch, 3 routers, 2 modems, 1 WIFI access point) PowerChute indicate a load of 0.8A. That's about 100 watts. PowerChute also estimate that the UPS can make this run on batteries for only 488 minutes or 7 hours 8 minutes. This seems wrong to us. The UPS powered a 150 watts lamp for 8.5 hours and is now estimating just over 7 hours for a 100 watts load.

Can there be something wrong with PowerChute estimations (by the way we declared 1 battery pack in PowerChute for our SUA24XLBP. Is this Ok?) or can there be something wrong with the calibration process.

Message was edited by: mathmoi

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • apc
  • battery
  • power
  • PowerChute
  • smart-ups
  • usb
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:52 PM . Last Modified: ‎2024-03-14 03:57 AM

0 Likes
0
1443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:52 PM . Last Modified: ‎2024-03-14 03:57 AM

Hi Techie and i picKed a winna,

Thanks you both for your help. Since I at least know that the batteries are working correctly and near the APC's estimation, i'll live with the uncertainty of the estimation and not do another discharge.

Again, thanks for your help.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-14 03:57 AM

0 Likes
0
1443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-14 03:57 AM

Hi,

Last friday I've done a calibration of a brand new SUA750XL with one SUA24XLBP attached. I used a 150 watts lamp as the only load and unplugged the UPS from the wall. The power from the batteries lasted for 8 hours 34 minutes. That's a bit longer than what can be estimated from the APC website.

Now, with the normal load attached (one 24 ports switch, 3 routers, 2 modems, 1 WIFI access point) PowerChute indicate a load of 0.8A. That's about 100 watts. PowerChute also estimate that the UPS can make this run on batteries for only 488 minutes or 7 hours 8 minutes. This seems wrong to us. The UPS powered a 150 watts lamp for 8.5 hours and is now estimating just over 7 hours for a 100 watts load.

Can there be something wrong with PowerChute estimations (by the way we declared 1 battery pack in PowerChute for our SUA24XLBP. Is this Ok?) or can there be something wrong with the calibration process.

Message was edited by: mathmoi

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-14 03:57 AM

0 Likes
0
1443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-14 03:57 AM

Mathmoi,

The External Battery Pack count which you have set is correct. The SUA750XL + (1)SUA24XLBP estimated run time is 9 hrs 45 mins if the equipment connected consumes 100 Watts of Power from the UPS outlets. Click on the below link to view the SUA750XL runtime chart:
http://www.apc.com/resource/include/ups_runtime_chart.cfm?base_sku=SUA750XL&family_id=165

I would like to gather some more information from you to understand what is going on with the unit. Could you please let me know the Power Chute version which you are using to monitor the UPS? What was the battery capacity when it showed 7 hours 8 minutes of run time? If possible, could you please post the data and event logs of the UPS on this thread?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-14 03:57 AM

0 Likes
0
1443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-14 03:57 AM

Hi Techie,

Thanks for your reply.

We are using PowerChute Business Edition Basic 7.0.5.

PowerChute is showing 8 hours 8 minutes, not 7 hours. That was my error. Still, that's less than the calibration time with less load. It's showing this with the battery capacity at 100%.

I attached the logs

Message was edited by: mathmoi

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-14 03:57 AM

0 Likes
0
1443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-14 03:57 AM

The logs are attached to my previous message.

Message was edited by: mathmoi

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-14 03:57 AM

0 Likes
0
1443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-14 03:57 AM

Hi,

The current load percentage (with netowrking equipments connected) is 18.2% VA. I can also read it as 0.8 A.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-14 03:57 AM

0 Likes
0
1443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-14 03:57 AM

If possible, please re perform a manual run time calibration and check the UPS runtime. Please follow the below K-base document instructions(Option 3) to perform the manual runtime calibration.

http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=1497

I hope that it helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-14 03:57 AM

0 Likes
0
1443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-14 03:57 AM

it should also be noted that while the UPS is online and running off of AC power, the estimated runtime is an estimate. the value should become more accurate while its running on battery and after a couple of discharges, should update accordingly. when the UPS is very new, sometimes you can see a difference in reported runtime versus actual runtime.

as you could see, the batteries worked just fine and lasted as they should when you discharged the battery. i would not waste another discharge by doing a manual calibration based on the fact that you know the batteries lasted the correct amount of time on your first discharge.

i would suggest keeping an eye on the runtime reported through the powerchute software, knowing its just an estimate, and then make sure it evens out over time with the observed runtime during your initial discharge.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:52 PM . Last Modified: ‎2024-03-14 03:57 AM

0 Likes
0
1444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:52 PM . Last Modified: ‎2024-03-14 03:57 AM

Hi Techie and i picKed a winna,

Thanks you both for your help. Since I at least know that the batteries are working correctly and near the APC's estimation, i'll live with the uncertainty of the estimation and not do another discharge.

Again, thanks for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of